Adjusting 6kW Daikin's Weather Compensation Curve
How best to fine tuning the weather compensation curve to reduce the buildings indoor temperature?
I'm familiar with accessing the adjustments of the weather curve on my Daikin 6kW hydrobox and have gradually trimmed the settings on the x-axis down from 40°C to 35°C but would like to reduce the indoor temperature slightly further.
Does the y-axis setting ever need attention?
Is it wise to make adjustments during the shoulder months?
Thanks
Posted by: @ubert767Does the y-axis setting ever need attention?
If you get outdoor temperatures outside the range where the curve has a slope then yes. So if your oat goes below -2 with any frequency I would adjust the x and y at this point to extend the line.
Posted by: @ubert767Is it wise to make adjustments during the shoulder months
It's easier to do it in the coldest months but sometimes you don't have a choice. You can always revert next season
Hope that helps
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 193 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@morgan Perfect, well received.
By HCas , 6 minutes ago
-
RE: Our journey through Octopus tariffs 2020-2025
Now that would be a really interesting point to get cla...
By Majordennisbloodnok , 15 minutes ago
-
RE: Are Water Companies Delivering Bricks?!
That's an excellent name for an audible newspaper for t...
By Transparent , 16 minutes ago
-
RE: Jokes and fun posts about heat pumps and renewables
By Morgan , 40 minutes ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@jamespa Looking at setting up the weather compensat...
By JamesPa , 59 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — thank you, that is useful information you hav...
By cathodeRay , 3 hours ago
-
RE: Grant Aerona circulation/system pump staying on
My parameters are: 42 00 = 0 (so the next three value...
By MikeFl , 3 hours ago
-
RE: Electricity price predictions
My apologies. I should've written "The number and dep...
By Transparent , 3 hours ago
-
RE: Solar panels on side of house to heat water
I wouldn’t try a direct linked system of DC at all sinc...
By Judith , 4 hours ago
-
RE: Flow rate discrepancy between ASHP and manifold
@ashrolls Air circulating in the system will confuse fl...
By bornagain , 4 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
If it happens only when it gets cold then it maybe that...
By JamesPa , 4 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
Has anyone got past this screen to set up the integrati...
By AlanW1212 , 4 hours ago
-
RE: Heat Pump Training vs. Real-World Installation
@lucia have you discoveredfor how green each of our ene...
By Judith , 5 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
You seem to be on the right track... Installers are rec...
By Batpred , 13 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
there's a detect cycle setting (4200) on the old grant ...
By damonc , 15 hours ago
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman It's also worth highlighting that th...
By Lucia , 16 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
. It does but, unless there has been a firmware updat...
By JamesPa , 19 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Yesterday it was chilly and the cosy6 had a Cop of 4.3 ...
By AgentGeorge , 21 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Same here! This month 187kw.
By Andris , 21 hours ago