Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
DHW temp Samsung AE120RXYDEG 12kw ASHP with Gen 6 controller
Had my Samsung ASHP installed start November. They left the DHW temp at 50C and set to go on and off all the time to keep the water at 50C. The tank is huge, I live alone and only use hot water for a shower in the evening so this seemed uneconomical to me.
Following excellent advice on here I've now set a schedule for the DHW to come on for 2 hours in the afternoon and reduced the water temp to 43C. But the DHW still seemed to be way too hot.
I had a look when the DWH was on today and as you can see the set temp is for 43C but the actual temp is over 47C. It still seems to be wanting to heat to 50C it seems to me.
I've looked in the field values and can see no way to set the DHW temp from there (unless I'm missing something).
Any Samsung owners have an idea why the DHW is heating hotter than the set temperature?
@bami it may be to do with the position of the temperature sensor in the tank. If it’s half way down the top of the tank will be hotter than the set temperature due to stratification.
If so do you can drop the temperature further and still have plenty of hot water
although I’ve just noticed the image but it could still be a sensor position issue as hot water will rise even after the heat pump has stopped heating for a time especially if the coil is low down in the tank.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami lol. I could be wrong 😆
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami I feel pretty safe then 😁. As a matter of interest where abouts is the coil and the sensor ?
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bami is there a cylinder schematic? Failing that a make and model might be enough to look up.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody The tank is a Kodiak Joule Smart Pre Plumb. Can find no mention of temp sensor anywhere online or in the installation manual. I did find this photo of the coil placement on the Joule.ie website.
@bami check the field setting values #3031 to 3033 for the booster heater (immersion) operation.
#3031 turns it on/off (I have mine set to NOT USE), #3032 sets the delay before it becomes active on a DHW cycle (if you do use it, set this high so the ASHP has sufficient time to try to reach the DHW set point temperature alone), and #3033 sets the overshoot temp (max 4C). This last setting (assuming #3031 is set to use) will allow the DHW tank set point temperature to overshoot by 4C which is what could be happening in your case?
So if #3031 is set to USE, and the delay time in #3032 is short, the immersion will kick in and help the ASHP to achieve the DHW set point temp, and then allow an overshoot of up to 4C as set in #3033.
If this is the issue, setting #3031 to NOT USE should fix it.
Posted by: @bamiFollowing excellent advice on here I've now set a schedule for the DHW to come on for 2 hours in the afternoon and reduced the water temp to 43C. But the DHW still seemed to be way too hot.
2 hours is far too long, and again could be contributing to this issue. It only needs to be long enough to reheat the DHW tank to the set point. Mine typically does this in around 30mins, so I schedule my DHW reheat to start every day at 2pm and schedule it to turn off again after 45mins, as once it's done, I know it's done until tomorrow. Keep an eye on it for a couple days to get a feel for how long it may reasonably take, and then add a bit for good measure just in case the tank is colder than usual.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@bami old scientist has a good call there. I don’t use my Samsung to heat DHW as I have a Mixergy tank so aren’t familiar with the settings.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@old_scientist Thank you so much for this info 🙏🏻 I'm still in the very early stages of getting to grips with it all.
The booster is set to Use and the delay time is 75 mins. Overshoot is 0C.
I've decreased the time the tank heats on the schedule down to 60 mins and will see how that goes. This time is below the delay time of 75 mins for the booster anyway, so the booster even while on shouldn't affect anything. As the overshoot is set to 0C that can't be responsible for heating the water higher than the set point.
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,077 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 4 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 18 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago