Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @craig1980
- @derek-m I didn't set them back to 21 straight away and left them for a day. At night it was longer between but by the next day it was back to the same.Â
Had the indoor temperature changed? A further test would be to watch closely the operation of the wireless receivers for the thermostats when the system performs its short off - on cycle.
Also check that all the plug and socket connections on the circuit board are making good contact.
Â
Posted by: @craig1980@derek-m no change in the indoor temperature. The lights on the receivers do not change when it cycles on and off.
Did you close the airing cupboard door overnight? The reason I ask is that sometimes equipment, and circuit boards, can suffer intermittent faults due to thermal expansion.
What water law settings are applied at the moment?
Â
@derek-m the airing cupboard door is always shut. It doesn't get that warm in there.Â
Pics of the screen set up of water law.Â
Not sure if the set up with "floor" is correct. Whether it should be FCU instead?
Also running -2 on the home screen which I'm led to believe is a short cut to adjusting a water law setting. Assuming the 31?Â
Â
Posted by: @derek-mYes, I've seen all the different diagrams in the manuals, but it doesn't tell one which is correct. Also I don't see the point in having two pumps to do the job that one pump should be able to do.
I’d go with the one from the Jule installation manual, as it’s a Jule cylinder/heatpump package. Now that we’ve seen some more photo’s you can clearly see that the hydraulics match what is shown I their manual exactly.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @derek-mHi Hugh,
Do you know if the Samsung controller will still use WC when operating with the indoor temperature located within the controller?
I have a lot of time for Glyn Hudson over on YouTube who has just DIYd his 5kW Samsung install and has documented it with a decent video. From the comments I’ve been having with his, he says that the Samsung will still use WC when the wired controller is used as for measuring room temperature. I’ve asked him if the controller will also support load compensation and reduce the flow temperature when the room is approaching the target temp. Inversely, increasing the flow temp to recover quickly from a nighttime or away/holiday mode setback temperature.
He uses a single pump (with PWM control) on his setup but his primary pipe work is short.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Let me have a read through the manual and decipher what some of the descriptions mean. I'll get back to you tomorrow.
Glyn has his 5kW Samsung wired/plumbed up with full monitoring, the data can be viewed at:
https://emoncms.org/samsung5kw
Single grundfos PWM pump, a heatpump cylinder with a 1m2 coil (the same cylinder I’ve got - they were cheap on eBay back in the summer), and radiators throughout.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 621 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
OOch thats leaking quite a lot! it looks like...
By JamesPa , 2 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-uk Keen to know more about the pricing and wh...
By ChandyKris , 15 minutes ago
-
RE: Our 10 year old Grant heat pump failed
Since my last post on this topic we've reached a conclu...
By Mike Patrick , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 5 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 13 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 17 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 17 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 18 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 19 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 22 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 22 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago