Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Thanks @hem
That looks like a SMETS1 meter with an Elster (Honeywell) Communications Hub operating at 900/1800MHz for connection to the National Smart Meter Network operated in the southern and central territories by Telefonica.
I like the inclusion of a separate 100A 2-pole isolation switch.
That allows an electrician to work safely within your consumer unit, without needing to break the seal on the Service Fuse.
I dislike what looks like a whole-house residual current detector (RCD) in that location.
Any earth-leakage fault within the house electrics will cause that trip to open, thereby plunging everyone into darkness. Ugh!
You then need to correct the fault, before going outside with a meter-box key to reset the trip. That's unfriendly.
Since your house is supplied from a PME substation, your EV charger must have its own earth stake rather than being connected back to the house earth-block.
The house earth is being provided by a link to the Neutral incomer to the property.
Cars have metal bodies.
In the event of a broken neutral wire between your house and the substation transformer, it's essential that the metalwork can't 'float' upwards.
That would present a shock hazard to anyone touching the car.
There are 550,000 substations in Britain.
Each year about 300 of these have a neutral fault which requires the DNO to repair it.
So you need to check with PodPoint whether they'd accept a 2-core SWA cable.
The armour would still be connected to earth at the house end to protect against cable damage.
But it wouldn't connect to anything at the garage end.
Save energy... recycle electrons!
Thank you once again.
Message from podpoint
"For areas where the cable crosses a path or a garden, we require the cable to be laid underground in ducting..
When organising the works, please ensure they follow the full specifications below:
- The trench needs to be a minimum depth of 450mm except for driveways where depth should be at least 600mm.
- There needs to be continuous twin walled flexi-duct with a minimum diameter of 50mm for the entirety of the underground run.
- A 6mm - 9mm nylon rope (draw cable) for cable pulling is expected to be installed in all ductwork for current cabling AND future use/capacity.
- Yellow warning tape to be placed in trench before being filled in.
@transparent If it's a Podpoint Solo EV charger, a quick look at the installation guide suggests it has has a form of PEN fault detection and can be connected to a TN-C-S supply without need of a separate earth electrode.
@hem Again, if it's a Podpoint Solo EV charger, there doesn't appear to be a wired network option so you will need good WiFi coverage at the front of the garage. A low voltage two-wire connection back to a current transformer on the incoming grid live supply will also be required, so a cable with integral cat5 core will be useful. At that distance, I would choose the 6sq mm version. Your electrician will need to register the installation with your DNO and building control.
Posted by: @hemFor areas where the cable crosses a path or a garden,
It's not 'crossing' a path or garden except for one point near the back door.
The intended cable-run is mainly along a fence...
which we don't yet know whether you own.
We only have a plan view to go on, and a photo of the pathway near your back door might help.
I can't see why a cable can't cross between the house and the fence at high level (say 2.5m above the path).
The fence may require a post to be extended upwards. But that could be done using a piece of aluminium angle.
I'd be paying more attention to how the SWA cable gets attached as it crosses that back path.
A thin stainless-steel wire rope could provide the required support.
Go to Amazon and type in Steel Wire Kit; there's loads of possibilities.
Save energy... recycle electrons!
I found this on outer wall of garage..looks from main power supply.
Can EV charger can be installed via this?
thanks
Hmmm...
That raises a lot of questions in my mind!
1: The Steel Wire Armoured (SWA) cable size needs to be known.
What does the white writing say on the outer black sheath below the junction box?
2: Have you located the other end of that SWA cable within the house?
It may not be derived from the main consumer unit.
It could equally be a spur from a ring main.... which should have a fuse, but may not.
3: What do the brown and blue wires supply inside the garage?
4: We don't like screwed terminal strips any more(!). But that 3-way could readily be replaced by three 2-pole WAGO connectors.
You're not going to be able to run a 7.5kW charger from that SWA cable anyway.
It would need to be around 6mm² for that.
But you might still be able to draw 16A, depending on the conductor size and where the house-end connects.
I have a 32A 3-pin round blue connector for my EV, with no actual charger at all.
There is a 16A equivalent which you could consider.
Save energy... recycle electrons!
@transparent Thank you for your reply. It's going to be difficult to find the other end. That unit on the garage wall is in neighbours garden 🙄
So whose electricity is passing through that junction box?
What socket (or light) does it feed within your garage?
Which of the trips in your consumer unit render that socket 'dead'?
Any of them?
Save energy... recycle electrons!
@transparent I checked, Electricity is going through our power supply and the fuse pic attached.
In garage it is connected to plug socket and to a bulb. I have checked the trip too. Pic attached.
Thanks,
Hem
The fact that the MCB is rated 16A tells us what we need to know.
If you were sure to use no garage light or socket at the same time, then you'd be able to draw 16A for the EV.
Unless you have any other evidence that the SW cable is larger than 1.5mm² then you shouldn't increase the rating of the MCB.
There's a cable-size calculator here on the TLC Direct website which can 'play' with to see what's possible.
Save energy... recycle electrons!
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 716 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
@david999 Thanks, I have read that some detergents are ...
By colinc , 18 minutes ago
-
RE: Our 10 year old Grant heat pump failed
Glad you got a resolution but £11k to £14.5k to replace...
By JamesPa , 1 hour ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
OOch thats leaking quite a lot! it looks like...
By JamesPa , 1 hour ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-uk Keen to know more about the pricing and wh...
By ChandyKris , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 6 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 15 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 18 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 19 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 20 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 20 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 23 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 23 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago