Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
EV charger installation question – I don't want to bury the cable
I'm planning to install EV charger to front of garage.
Main supply is at the other corner of the house and garage is built on the other corner, after the garden.
I'd like to have an EV charger connected back to existing house supply, but not have to bury the cable.
Please help me with your expertise.
Hello @hem. And I see that @editor has very quickly found a suitable spot for this topic! 🙂
An outside cable like this would normally be Steel Wire Armoured (SWA).
For a standard domestic EV charger, it would need to be able to deliver 32A (assuming a charger rated at 7.5kW).
There will be voltage drop along the cable route. The distance matters.
But you can quickly assess the required cable size by using an online cable cable calculator, such as this one from TLC.
There is no requirement for an SWA cable to be buried underground.
You could run it above ground, clipped at low level to a wall or a fence, for example.
The important issue is that it must be protected from mechanical damage.
Save energy... recycle electrons!
Thank you Transparent.
in on of the forum you had suggest SWA - 4 CORE ( Can't remember where). is that you suggest for EV charger installation.
I have no knowledge of electrics , please ignore my stupidity.
I can't remember where either 😖
Can I check if you are intending to use a recognised EV Charger installer in order to take advantage of a grant?
Or are you simply buying a charger and getting a local electrician to fit it?
It's possible that the grant-aided schemes only work if they supply the cable.
That needs checking first.
However, the approved installer might still offer a discount if you were offering to run such a long cable yourself!
If the choice of cable is entirely up to you, then I'd usually expect it to be a 3-core SWA type.
That means both the armoured sheath and one of the cores is earth.
If it was simply a run to provide power in the garage, then an electrician might've been happy with 2-core cable.
But earthing on EV chargers is a 'hot topic' and I'd be surprised if an installer would be prepared to use an earth connection which operates only through the steel armour. It's not a great conductor if a fault should occur.
Having said all that, some EV charger installations require a local earth rod, rather than depending on a connection back to the house.
To assess that, can you say whether your house currently has its own earth rod?
Or is the earth provided by the Electricity Distribution company?
A photo of your 100A service fuse and meter would be helpful.
Save energy... recycle electrons!
Depending on the charger you install, an option may be to use an SWA cable with an integral cat5 cable. This may be used either for an internet connection if it is a 'Smart' device, to avoid using WiFi, or to connect remote current transformers to facilitate load management features in the charger (so as not to draw too much power from your home supply. Your electrician should be able to advise.
@hem that's a good observation from @ianmk13
Here's a link to that SWA with integral CAT5e data cable, also from TLC Direct.
Note that they sell it per metre, which is very helpful.
If you zoom back out to the wider selection of products sold by TLC for use with EV chargers, you'll notice that the combined power and data cable is only available with 3-cores. That's a pretty strong indication of what the market is using!
Save energy... recycle electrons!
Just a reminder @hem - we do need to know whether your house has its own earth stake, or if earth is provided via the 100A service fuse.
You should either have an earth wire coming from your service fuse, or you have an earth stake. Not both!
Which do you have?
I want to post the relevant wiring diagram for you to see.
Save energy... recycle electrons!
I'm planning and paid Podpoint .
They washed their hands advising me to get the cable from power source via garden ( ground work) to garage by myself.
Attached power source photo and a site sketch
Thanks🙏
- 26 Forums
- 2,670 Topics
- 62.5 K Posts
- 157 Online
- 7,080 Members
Join Us!
Directory
Degrees of Separation
Latest Posts
-
-
RE: MCS 2.0 - Changes in January 2025
It strike's me that there's various improvements which ...
By Temperature_Gradient , 2 hours ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@majordennisbloodnok The M5StickC turned up...
By Bash , 2 hours ago
-
Hi Everyone, I wanted to share something with you all...
By ASHP-BOBBA , 3 hours ago
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
Great journey @allyfish. Totally relate to your experie...
By ChandyKris , 5 hours ago
-
-
Many messages back and forth later… GOV UK One Login ...
By Toodles , 5 hours ago
-
RE: Say hello and introduce yourself
@will-h, this isn't a dig but we would prefer if anyone...
By Majordennisbloodnok , 7 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Thanks Tim. That SolarEdge data also shows voltages a...
By Transparent , 11 hours ago
-
RE: Configuring third party dongle for Ecodan local control
A few notable developments: I'm working through addin...
By F1p , 1 day ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
Vehicle to Grid is the further step and here is the IEA...
By Judith , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Where the grid is heading? Input from Kraken.
By Jeff , 1 day ago
-
RE: Plug and play solar. Thoughts?
@jamespa Yes, unfortunately our policymakers learned...
By Batpred , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
@l8again It seems you did very well. With our HG h...
By Batpred , 2 days ago