Search with Wattson
If a heat pump can ...
 
Notifications
Clear all

Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump

32 Posts
5 Users
19 Reactions
6,642 Views
(@errmm)
Active Member Member
Joined: 10 months ago
Posts: 12
Topic starter   [#2787]

Hi,

I'm helping someone who has a big 18KW Heliotherm heat pump with a DHW heating issue.  I don't fully understand all the tech myself (it's two massive cylinders (like 6ft)) in a plant room.

After a couple of showers the water is has dropped 10 degrees so is down to around 39C and so he's having to reheat the water again as without this the warm but not hot.  When he spoke with his heatpump installer, they said this is how it just is.  I think the point they were making is that this heatpump can't heat DHW higher than 50C and so after two showers this is normal.  Whereas in my house with gas and a boiler half the size, we can get 3 showers no problem.  

So is this the norm for heatpumps that can only heat DHW to 50.  I know others with heatpumps who heat DHW once, presumably that system can heat to 55C and so even after two showers the water is acceptable?

Grateful for any of your thoughts,

 

Mike

 

image

This topic was modified 10 months ago 3 times by Mars

   
Like
1
Quote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5710
 

Posted by: @errmm
↑

So is this the norm for heatpumps that can only heat DHW to 50.  I know others with heatpumps who heat DHW once, presumably that system can heat to 55C and so even after two showers the water is acceptable?

It is the norm that heatpumps are set to heat DHW only to 50C, or even less.  Depending on the refrigerant (R410 vs R32 vs R290) they may be capable of going higher (up to 70 in the case of R290) but for efficiency they are usually set lower.

It is not the norm, assuming that the water tank is correctly sized, that the DHW is exhausted after 2 showers unless the individuals take very long showers.

Another thing to consider is the location fo the sensor in the tank.  If its low down it will see the cold water at the bottom whilst there is still plenty of hot water at the top.

To get to the bottom of this more info is needed

  • How long are the showers, roughly how much water is used in each one?
  • How big is the tank? (you mention tanks).  Is one tank DHW and the other a buffer tank, photos may clear that up.

This is a matter of correct design not the fact its a heat pump.  

 

If you provide more info then some more precise comments can be made.

 

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5016
 

Fully agree with @jamespa.

Just for context @errmm, what brand is the heat pump?


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5710
 

Just to add some numbers to my comments above, a 6ft high tank sounds like 300l at least.  300l at 50C will yield 400l at 40C when diluted with incoming water at 10C.   40C is a typical showering temperature.  At 20l/min. which is a very generously fast shower, this will last 20mins, which is 2 very generously long showers.  At a more reasonable 10l/min and say a 5 min shower thats 8 showers.  Of course I do know that some people insist on showering for 10mins at 20l/min although I have no idea why!

Hopefully that gives some context, if you provide the additional info perhaps it can be rationalised.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote

Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5016
 

@jamespa, I can add a bit of real-world context from our own setup, which might help frame this a bit. We have a single 300L cylinder and we only heat ours to 45C. After my wife and I have our morning showers (roughly 10 minutes each) the reported cylinder temperature will often drop to around 35C. With a 10C hysteresis, that’s enough to trigger a reheat, even though subjectively the showers themselves have been perfectly fine. We eventually set our hysteresis to 15C, because there was still plenty of hot water.

Our shower head is around 10 L/min, so nothing particularly excessive.

That experience broadly aligns with your maths, but it also highlights how much the reported 'tank temperature' depends on sensor position and stratification rather than usable hot water at the outlet. A sensor lower down the cylinder will see the cold slug very quickly, even when there’s still plenty of hotter water sitting above it. Ours is slap bang in the middle.

So I’d be very reluctant to accept 'that’s just how heat pumps are' as an explanation here. Limiting DHW to 45-50C for efficiency reasons is normal. Rapid apparent temperature collapse after modest use is not. This definitely feels much more like a system design, configuration or control problem than a fundamental limitation of the heat pump itself.


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
Like
1
ReplyQuote
(@errmm)
Active Member Member
Joined: 10 months ago
Posts: 12
Topic starter  

Hi 

Attached is picture of the tanks.  It's a heliotherm. 

I've spoken with the installer and they mentioned flow rates on showers as well. 

Mike 



   
Like
1
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5016
 

@errmm, wow, since it's a Heliotherm there should be zero issues with hitting target temperatures.

Images didn't insert. Please try again.


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
(@errmm)
Active Member Member
Joined: 10 months ago
Posts: 12
Topic starter  
PXL 20250806 145431018


   
ReplyQuote

JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5710
 

@errmm Difficult to tell from the photo what's going on, but those are at least 300l possibly 400.  Need a photo where you can see the pipework and whole tank to be sure if one is dhw and the other a buffer.

 

The most likely, but by no means the only, explanations are

1 The individual really is taking 10 min showers at 20l/min - need to ask the question 

2 The sensor is half or even 2/3rds of the way down the tank so shows it cooling well before the hot water in the tank is exhausted.- need to ask if you can continue running off hot water even though it says it needs a reheat.

Before we look any further we need to rule these two obvious ones out imho.


This post was modified 10 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@errmm)
Active Member Member
Joined: 10 months ago
Posts: 12
Topic starter  

Hi,

The left is the buffer tank, the right is DHW.  It's right is one of these https://www.heliotherm.com/en/fresh-hot-water-system/fresh-hot-water-system.html   It says it's fresh pure hot water on demand.  So I don't don't understand that description along with a well two showers and it's luke warm....

Regarding sensor position, the person themselves is the one who said the water was lukewarm after the showers.  It's not the case that they're looking at this data.  It's me looking at it and going ok, that seems to be correctly reflecting what they are saying.  I will ask about shower habits just in case though, just to rule it out.

 

Mike

 

 

 



   
Like
1
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5016
 

@errmm is your friend’s house that you’re helping a large property?


This post was modified 10 months ago by Mars

Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5710
 

Posted by: @errmm
↑

Hi,

The left is the buffer tank, the right is DHW.  It's right is one of these https://www.heliotherm.com/en/fresh-hot-water-system/fresh-hot-water-system.html   It says it's fresh pure hot water on demand.  So I don't don't understand that description along with a well two showers and it's luke warm....

Regarding sensor position, the person themselves is the one who said the water was lukewarm after the showers.  It's not the case that they're looking at this data.  It's me looking at it and going ok, that seems to be correctly reflecting what they are saying.  I will ask about shower habits just in case though, just to rule it out.

 

Mike

 

 

 

From the website I think it's a heat store not a conventional dhw tank.  Not a good idea with an ashp and could very likely explain what is happening.

PS. I read it a second time, it is a heat store.  Interesting though that they sell it to work with an ashp.  Would need to examine the specs and operating instructions to understand how they think it should work.  


This post was modified 10 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote

Page 1 / 3

Share:
Click to access the login or register cheese