Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Hi,
I'm helping someone who has a big 18KW Heliotherm heat pump with a DHW heating issue. I don't fully understand all the tech myself (it's two massive cylinders (like 6ft)) in a plant room.
After a couple of showers the water is has dropped 10 degrees so is down to around 39C and so he's having to reheat the water again as without this the warm but not hot. When he spoke with his heatpump installer, they said this is how it just is. I think the point they were making is that this heatpump can't heat DHW higher than 50C and so after two showers this is normal. Whereas in my house with gas and a boiler half the size, we can get 3 showers no problem.
So is this the norm for heatpumps that can only heat DHW to 50. I know others with heatpumps who heat DHW once, presumably that system can heat to 55C and so even after two showers the water is acceptable?
Grateful for any of your thoughts,
Mike
Posted by: @errmmSo is this the norm for heatpumps that can only heat DHW to 50. I know others with heatpumps who heat DHW once, presumably that system can heat to 55C and so even after two showers the water is acceptable?
It is the norm that heatpumps are set to heat DHW only to 50C, or even less. Depending on the refrigerant (R410 vs R32 vs R290) they may be capable of going higher (up to 70 in the case of R290) but for efficiency they are usually set lower.
It is not the norm, assuming that the water tank is correctly sized, that the DHW is exhausted after 2 showers unless the individuals take very long showers.
Another thing to consider is the location fo the sensor in the tank. If its low down it will see the cold water at the bottom whilst there is still plenty of hot water at the top.
To get to the bottom of this more info is needed
- How long are the showers, roughly how much water is used in each one?
- How big is the tank? (you mention tanks). Is one tank DHW and the other a buffer tank, photos may clear that up.
This is a matter of correct design not the fact its a heat pump.
If you provide more info then some more precise comments can be made.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Just to add some numbers to my comments above, a 6ft high tank sounds like 300l at least. 300l at 50C will yield 400l at 40C when diluted with incoming water at 10C. 40C is a typical showering temperature. At 20l/min. which is a very generously fast shower, this will last 20mins, which is 2 very generously long showers. At a more reasonable 10l/min and say a 5 min shower thats 8 showers. Of course I do know that some people insist on showering for 10mins at 20l/min although I have no idea why!
Hopefully that gives some context, if you provide the additional info perhaps it can be rationalised.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa, I can add a bit of real-world context from our own setup, which might help frame this a bit. We have a single 300L cylinder and we only heat ours to 45C. After my wife and I have our morning showers (roughly 10 minutes each) the reported cylinder temperature will often drop to around 35C. With a 10C hysteresis, that’s enough to trigger a reheat, even though subjectively the showers themselves have been perfectly fine. We eventually set our hysteresis to 15C, because there was still plenty of hot water.
Our shower head is around 10 L/min, so nothing particularly excessive.
That experience broadly aligns with your maths, but it also highlights how much the reported 'tank temperature' depends on sensor position and stratification rather than usable hot water at the outlet. A sensor lower down the cylinder will see the cold slug very quickly, even when there’s still plenty of hotter water sitting above it. Ours is slap bang in the middle.
So I’d be very reluctant to accept 'that’s just how heat pumps are' as an explanation here. Limiting DHW to 45-50C for efficiency reasons is normal. Rapid apparent temperature collapse after modest use is not. This definitely feels much more like a system design, configuration or control problem than a fundamental limitation of the heat pump itself.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Hi
Attached is picture of the tanks. It's a heliotherm.
I've spoken with the installer and they mentioned flow rates on showers as well.
Mike
@errmm, wow, since it's a Heliotherm there should be zero issues with hitting target temperatures.
Images didn't insert. Please try again.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@errmm Difficult to tell from the photo what's going on, but those are at least 300l possibly 400. Need a photo where you can see the pipework and whole tank to be sure if one is dhw and the other a buffer.
The most likely, but by no means the only, explanations are
1 The individual really is taking 10 min showers at 20l/min - need to ask the question
2 The sensor is half or even 2/3rds of the way down the tank so shows it cooling well before the hot water in the tank is exhausted.- need to ask if you can continue running off hot water even though it says it needs a reheat.
Before we look any further we need to rule these two obvious ones out imho.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi,
The left is the buffer tank, the right is DHW. It's right is one of these https://www.heliotherm.com/en/fresh-hot-water-system/fresh-hot-water-system.html It says it's fresh pure hot water on demand. So I don't don't understand that description along with a well two showers and it's luke warm....
Regarding sensor position, the person themselves is the one who said the water was lukewarm after the showers. It's not the case that they're looking at this data. It's me looking at it and going ok, that seems to be correctly reflecting what they are saying. I will ask about shower habits just in case though, just to rule it out.
Mike
@errmm is your friend’s house that you’re helping a large property?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @errmmHi,
The left is the buffer tank, the right is DHW. It's right is one of these https://www.heliotherm.com/en/fresh-hot-water-system/fresh-hot-water-system.html It says it's fresh pure hot water on demand. So I don't don't understand that description along with a well two showers and it's luke warm....
Regarding sensor position, the person themselves is the one who said the water was lukewarm after the showers. It's not the case that they're looking at this data. It's me looking at it and going ok, that seems to be correctly reflecting what they are saying. I will ask about shower habits just in case though, just to rule it out.
Mike
From the website I think it's a heat store not a conventional dhw tank. Not a good idea with an ashp and could very likely explain what is happening.
PS. I read it a second time, it is a heat store. Interesting though that they sell it to work with an ashp. Would need to examine the specs and operating instructions to understand how they think it should work.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,586 Topics
- 60.2 K Posts
- 385 Online
- 6,908 Members
Join Us!
Worth Watching
Latest Posts
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 4 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
A2A pipe refrigerant around, A2W pipe water, so I dont ...
By JamesPa , 7 minutes ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Great. In that case I would definitely cancel the over...
By JamesPa , 1 hour ago
-
RE: Plug and play solar. Thoughts?
Thats incorrect. The protection devices (fuses or MCBs...
By JamesPa , 2 hours ago
-
RE: Anyone concerned about GivEnergy?
@johndwyer Just to mention something that helped me whe...
By 1066 , 4 hours ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 15 hours ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 15 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Unfortunately Mr Smith may need to adjust his expectat...
By JamesPa , 19 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 20 hours ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 22 hours ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 1 day ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 1 day ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 2 days ago
-
RE: Forum updates, announcements & issues
A quick heads-up. We’ll be carrying out a major forum...
By Mars , 2 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 3 days ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
I read this thread from the beginning to its end.And th...
By LeJamaisContent , 3 days ago
-
RE: Water law settings... A year on
Yes it does Apart from the abbreviations! We're in ...
By Profzarkov , 3 days ago
-
My Immersun power diverter problems now they have ceased trading
I have had an Immersun unit for 15 years that happily w...
By pjcwood , 4 days ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
Hello @Penval unfortunately, now the winter is gone and...
By LeJamaisContent , 4 days ago
-
RE: Grant Aerona R32 – Summer, Winter mode & Setbacks
What are you envisaging doing throughout the day? Pers...
By JamesPa , 4 days ago