Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecdon Third party Thermostat Issues
- @derek-m yeah its since the cooler weather has arrived, the controller is located in airing cupboard upstairs. The door is closed and there is no radiator in the cupboard.
Posted by: @derek-mPosted by: @adam_colwellIf the thermostat have been wired incorrectly, is a hard job to fix?
It is quite some time since I explored the delights of the Ecodan manual, but I think that Kev is correct that there may be DIP switch settings that need to be made or that equipment may need to be enabled. I would suggest that you have a look through the 'installer settings' to see if any changes need to be made.
@Derek-m, if you look at the dip switch settings in 5.4 of the FTC6 manual, it says how to set the logic for the 3rd party thermostats. If these were set wrong it could possibly cause issues like @adam_colwell is having. Another thing to look for is a 3 way valve stuck or not set up properly.
Currently viewing this topic 2 guests.
- 27 Forums
- 2,815 Topics
- 66.7 K Posts
- 1,783 Online
- 7,230 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: DIY powerflushing tutorial
Ah! So it's the electrochemical series which drives the...
By Transparent , 12 minutes ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
We've had an influx of new members joining the forums o...
By Mars , 36 minutes ago
-
@editor thank you that's a very useful reply. We've man...
By Brazilguy67 , 1 hour ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
Got excepted for the grant now so thanks for the replie...
By Chilli304 , 2 hours ago
-
Daikin Altherma 3 R F+W, room thermostat control, weath...
By JanHarley , 3 hours ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
Pretty much as I had guessed in my crude scaling from m...
By JamesPa , 6 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Well you have a vibration generator running at some fre...
By bobflux , 19 hours ago
-
RE: Why don't people choose heat pumps?
@susannasaunders The link I have found may provide a li...
By Toodles , 22 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@downfield Thats a decent rate, I’m shocked they hadn...
By Papahuhu , 2 days ago
-
RE: Should Households Who Can Afford It Pay More for Energy to Help Those Who Can't?
@batpred I mentioned earlier that targeting the payment...
By Toodles , 2 days ago
-
RE: Adventures in heat loss calculations
@toodles thanks! So as suspected, around a doubling of ...
By SusannaSaunders , 2 days ago
-
Six books in three years and I think I’ve now covered j...
By Mars , 2 days ago
-
RE: Grant Aerona3 13kw - Buffer Tank - Heating Journey
@heymikey Well done in achieving as nearer a match acro...
By Toodles , 2 days ago
-
Grant Aerona - Weather Compensation and Schedules
Im trying to set up a friends Grant Aerona. The WC curv...
By bontwoody , 3 days ago