Column radiators for heat pump
I have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Posted by: @encI have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Radiator manufacturers generally provide either outputs at lower temperatures, an equation, or the 'exponent'. For radiators other than fan radiators (and possibly radiators with a very high 'aspect ratio') the equation is invariably "output is proportional to deltaT^n" where deltaT is the average temp difference radiator to room and ^n means raised to the power of n (n is 'the exponent'). Furthermore n is almost invariably 1.3 or very close, so output is proportional to deltaT^1.3.
Thus (for example) a radiator that outputs 1kW at 50C deltaT will output (25/50)^1.3x1kW at 25C deltaT = 406W.
I don't know of any reason why fancy column radiators should perform particularly badly or particularly well with a heat pump, however others might,
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a couple of tall (1.8m) column radiators im my kitchen diner. I presently have a boiler and have assumed the usual downrating for ASHPs. One problem I have experienced with my boiler setup is that it takes an age for the radiator to heat up. Flow and return are both at the bottom of the radiator and the installer did not fit the baffle - available seperately - to divert the flow up the first column to the top of the radiator. Conequently, the flow much refers to go straight across the bottom of the radiator from inlet to outlet. I don't know what would happen with the lower flow temperatures and higher flow rate with an ASHP in this situation, but I would definitely recommend ensuring flow across diagonal corners one way or another.
We have an 1800x500x100 mm. radiator in our dining area (insufficient wall space for conventional shape. This one works with our heat pump and provides a very even radiant heat over the whole panel space and I assume the convection is equally good - but it is well above our heads! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 22 Forums
- 2,082 Topics
- 45.7 K Posts
- 36 Online
- 3,370 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: RDSAP10 effect on existing heat pump EPC rating?
RdSAP 10 represents a significant shift in how EPCs are...
By Aaron , 4 minutes ago
-
RE: I don't need any heating in the summer. How do I turn my Samsung heat pump off?
Thank you
By Alfapat , 24 minutes ago
-
@bart Which county are you in? Kent by any chance? S...
By ASHP-BOBBA , 2 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
@jamespa Hi James, I never mind these questions as its ...
By ASHP-BOBBA , 2 hours ago
-
RE: I worry I've messed my Samsung settings up somehow
@ecobaker I missed this, sorry So 3031 was set to...
By Joshua , 2 hours ago
-
RE: Flow Rate & Low Loss Headers
It sounds like you have thought about this a lot and ev...
By JamesPa , 3 hours ago
-
RE: Remaining hot water/hot water flow meter
I think you first sentence is spot on, stored DHW is ju...
By JamesPa , 4 hours ago
-
RE: Forum updates, announcements & issues
@old_scientist thank you, and thank you to @Morgan for ...
By Mars , 4 hours ago
-
RE: Say hello and introduce yourself
I am a UK based product manager for an energy storage s...
By shawnlee , 9 hours ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
That's great and in principle I wouldn't disagree, but ...
By JamesPa , 20 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Mitsubishi 8.5 kW Ecodan Standalone (PUZ-WM85VAA)
By Nell , 1 day ago
-
-
RE: Jokes and fun posts about heat pumps and renewables
This is the plan to get our next heat pump installed an...
By Mars , 2 days ago
-
Thanks! That is most useful. I've had a look at the Mid...
By benson , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I found that Homely blog a few days ago and was tempted...
By cathodeRay , 2 days ago
-
RE: Home energy storage & battery register
I love that! Unfortunately there doesn't appear curr...
By JamesPa , 3 days ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi Melon, I would just concentrate on bala...
By ASHP-BOBBA , 4 days ago
-
-
RE: All your heat pump problems solved by -- a plate heat exchanger in a plinth!
@allyfish As you say, all the ‘plus points’ and ‘advant...
By Toodles , 6 days ago