Notifications
Clear all

Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Heat loss calculations and how they work in conjunction with heat pump sizing

64 Posts
12 Users
19 Reactions
20.3 K Views
GrahamF
(@grahamf)
Estimable Member Member
Joined: 2 years ago
Posts: 137
Your energy: 0 kWh
 

Posted by: @jamespa
↑

That depends on the circumstance and your assertion is not necessarily true.  If for example if oversizing leads you to going from one heat pump to 2, the change is enormous. If it leads to you requiring a 2 fan pump rather than a one fan, and there is no good space for a 2 fan, then the impact is equally enormous.  Likewise its an enormous impact if oversizing results in floorboards being lifted (or worse still solid flooring) to upgrade pipework unnecessarily.  In general terms the difference is bigger the larger the loss.

Yes that is a very fair point.  I was thinking of the situation where you really need a 10kW heat pump, but install a 12kW or 16kW.  Other items could indeed be expensive for the customer - which of course also means more revenue for the installer.

On reflection your point applies to us.  One installer told us we needed 2 x 10kW heat pumps, which probably implied a buffer tank and less efficiency.  He also suggested that we would need to upgrade to a 3 phase power supply for the two heat pumps.  That would have cost us £an additional 20k.


Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation


   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3163
Your energy: 9 kWh
 

Posted by: @majordennisbloodnok
↑

@batpred, English does not seem to be your first language

I too had exactly the same thought, and agree 100% (note I did not write 110%...) with the Major, in such cases, the simpler the language the better. If you must use technical terms, define them the first time you use them, so that we are all clear what a word or a phrase means.  


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@agentgeorge)
Reputable Member Member
Joined: 2 years ago
Posts: 194
Your energy: 0 kWh
 

 

IMG 6438
IMG 6439

@cathoderay I read your response through twice, it was very informative if a tad long 🙂

I monitor my system every day and have tweaked the settings to get as high a COP as feasible. I have weather comp on, and have adjusted the flow temps as low as the Octopus App allows

If you turn WC off, default is 50C but can set Flow Temp to 70C which is disastrous for the COP, but you could set the system up that way

I have UFH so don't want a flow temps over 40C as I have no mixer valve

My settings are in the photo above, Couldn't figure out how to move photo to here, ill be monitoring the comfort level of the house against COP through my first full winter period to see if my strategy works

I have the room stat set at 20.5 all day and night, so the HP is just ticking over at a very good COP of 4.6-5.2 this past month.

ive also set the DHW heating to midday when the HP wont have to work so hard to heat the tank

 



   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5740
Your energy: 75 kWh
 

Posted by: @batpred
↑

I reported details of a case where some friends of mine had constant temperature for the house, they were focused on efficiency and had this idea that to maximise it, the pump had to be working at all times...

Then we had an installer over was also very much insisting that the system should be running continuously. For efficiency. 

With a well designed system with a tolerably well insulated house that is true, or thereabouts.  Not only for efficiency but also for cost.  There are of course exceptions.  A modest setback (or set forward if you have a cheap tarrif period) may save a little money, or it may not.  

Thats not the same, however, as saying that it has to be operating at the same temperature 24x7, nor that all rooms must be at the same temperature.

Posted by: @batpred
↑

Not what I could call evidence but a pattern that I have to admit I assumed could be influenced by the way the systems were designed - but it could be things further down the pipeline

Its not related directly to design, even the most basic controls are quite flexible.  But it is nevertheless excellent advice as a starting point and ignoring this is a mistake that is frequently made, unfortunately.

I am not an installer but will always advise householders, unless there is a very specific reason to the contrary, to start off operating 24*7 at constant temp (constant over time, different temps allowed between rooms), with all thermostats/TRVs set at least a couple of degrees above the target, and adjust the weather compensation curve to the lowest possible consistent with heating the house.  This establishes a sound baseline which is close to the most efficient and cost effective operation in most cases.  Some minor tweaks from this baseline might improve either comfort or cost a bit depending on house, occupancy and tarrif. 

There are good reasons for this rooted in basic thermodynamics, but its a long topic to understand in full.  Two key concepts to get over are (a) that heat pumps have different operating characteristics than boilers so much of what you have learned should be forgotten and (b) that houses continue to lose heat (initially at the same rate) even if the heating is switched off, and that heat still has to be replaced.   If you want to understand it better I suggest you read around here, on the heat geek site, on protons for breakfast and elsewhere.

Posted by: @batpred
↑

I would guess that as a principle and since the system can accumulate heat in the cylinder, most customers would  want the external unit running considering when their electricity is cheaper and generally whenever the external temperature is warmer but there will surely be many other other factors that in some cases may even be more important to them. 

The cylinder is for DHW only, not for space heating, and will typically only be actively heated for 2-3 hours per day.  Its generally well insulated so will retain heat for 48hrs or more unless drained off.

Posted by: @batpred
↑

There are also various people posting in this forum talking about running the external unit continuously. Perhaps I misunderstood and they meant just the external unit to not run for short periods

Your understanding was correct the ASHP will normally be run continuously or for long periods.  Thats how low temperature heating, whether from a boiler or heat pump, works.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3163
Your energy: 9 kWh
 

Posted by: @agentgeorge
↑

I read your response through twice, it was very informative if a tad long

Thank you. Better long and informative than short and impenetrable, in my way of thinking...

Posted by: @agentgeorge
↑

If you turn WC off, default is 50C but can set Flow Temp to 70C which is disastrous for the COP, but you could set the system up that way

Exactly, just because you can doesn't mean you should.

Posted by: @agentgeorge
↑

My settings are in the photo above

Photos - you should be able to drag and drop them onto your post while you are writing it. The right hand photo shows your weather compensation curve settings, but the manufacturer just has warm weather and cold weather as the defining points for each end of the curve. Do you know what counts as warm weather and cold weather in degrees C?

Posted by: @agentgeorge
↑

I have the room stat set at 20.5 all day and night, so the HP is just ticking over at a very good COP of 4.6-5.2 this past month.

If that is so, and you are comfortable, then you have a well set up system!

Posted by: @agentgeorge
↑

ive also set the DHW heating to midday when the HP wont have to work so hard to heat the tank

I apply the same logic, make hay, or rather heat the hot water, when the sun is out, so to speak. 


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3163
Your energy: 9 kWh
 

Posted by: @jamespa
↑

The cylinder is for DHW only, not for space heating

This is an important point which I forgot to emphasise. It is a 'heat store' but only for the DHW (have a look at piping diagrams). 


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@agentgeorge)
Reputable Member Member
Joined: 2 years ago
Posts: 194
Your energy: 0 kWh
 

Posted by: @toodles
↑

There will be times when the 8 kW heat pump starts up with a surge much higher than 2 kW and also when adverse weather drags the COP down, there may well be periods where that same pump could draw far more than that 2 kW for an extended period of time. Regards, Toodles.

The max power I've recorded on my Home Power Monitor from my cosy6 is 1.56kW, at todays grid of 237.7V thats 6.56A; the HP has its own 16A mcb.

You're right there’s a startup surge, typical 6-10x running current; more when the motor is cold. There’s also a shutdown collapsing field voltage spike that needs suppressing too.

 



   
ReplyQuote
Toodles
(@toodles)
Daikin
Famed Member Contributor
Joined: 4 years ago
Posts: 3097
Your energy: 27 kWh
 

@agentgeorge Similarly, in this mild weather, our Daikin is just ticking over (even though we have temperature set for comfort at 22.5 C.). Of course the graph is only a report based on information provided by Mr. Daikin 😉 and will not display true peaks, or even necessarily be accurate in its’ reported values! The plot is for the last 32 hours approx. taken from the Homely installer app. Regards, Toodles.

IMG 1365

Toodles, heats his home with cold draughts and cooks food with magnets.


   
ReplyQuote

Batpred
(@batpred)
Vaillant
Noble Member Member
Joined: 2 years ago
Posts: 1252
Your energy: 20 kWh
 

Posted by: @cathoderay
↑

Posted by: @majordennisbloodnok
↑

@batpred, English does not seem to be your first language

I too had exactly the same thought, and agree 100% (note I did not write 110%...) with the Major, in such cases, the simpler the language the better. If you must use technical terms, define them the first time you use them, so that we are all clear what a word or a phrase means.  

😂😂

I suffer from communicating in too many languages! One of the early ones was IT Infra language. I appreciate this is not common here. Also when people use heating engineer language it is not always understood. That does not really explain most of the "misunderstanding" in that exchange. 

As someone deepening knowledge about another domain based on a broad scientific base, I may assume X is the norm whereas it is the exception at the moment. Like I remember going over youtube videos that include buffer tanks. And by that I mean a tank used to keep heat that is used later to warm the space. 🙂 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Mitsubishi Electric
Famed Member Moderator
Joined: 5 years ago
Posts: 2262
Your energy: 37 kWh
 

Posted by: @batpred
↑

Posted by: @cathoderay
↑

Posted by: @majordennisbloodnok
↑

@batpred, English does not seem to be your first language

I too had exactly the same thought, and agree 100% (note I did not write 110%...) with the Major, in such cases, the simpler the language the better. If you must use technical terms, define them the first time you use them, so that we are all clear what a word or a phrase means.  

...

I suffer from communicating in too many languages! One of the early ones was IT Infra language. I appreciate this is not common here. Also when people use heating engineer language it is not always understood. That does not really explain most of the "misunderstanding" in that exchange. 

....

No, that is not what we mean. "IT Infra" is not a language; it's not even clear what you actually mean by this. If you mean "IT Infrastructure jargon", I can understand your sentence better, but that underlines that you're missing the point.

Your sentence structure and grammar, to pick just two examples, clearly tell me that whatever language you spoke in childhood it was not English. If communicating effectively in English is already a challenge for you, complicating what you're saying with technical jargon of any kind makes it immeasurably harder to actually understand what you mean. Your post just above suggests you think your English is fine and that it's just a matter of me not being familiar with IT terminology, but that unfortunately is incorrect in every sense.

I have no wish to criticise your language skills, but for effective communication you really need to move towards using much more basic English, construct simpler and shorter sentences and avoid technical terms where possible.

 


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Home Assistant to make it all play nicely together
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
Batpred
(@batpred)
Vaillant
Noble Member Member
Joined: 2 years ago
Posts: 1252
Your energy: 20 kWh
 

Posted by: @cathoderay
↑

@batpred - I think it might help somewhat if you could set down what you want from your heat pump discussion here on the forum. As I currently understand it, these are hypothetical, insofar as you don't have plans to install a heat pump any time soon, and it is always a little difficult when discussing hyotheticals because, well, they are hypothetical. That said, establishing some heat pump basics, and generally making sure anything you do now in another context (eg batteries etc) wont conflict with any future heat pump installation is certainly sensible.

Thanks, none of us posting much on this forum are typical users. I doubt many would have embarked in these HP upgrades without having first understood the key aspects to consider. We all seem to have systems thinking and most agree that each householder will expect to look after their own interests. 

My objective discussing heatpumps is just that when we will discuss ours, we will want to have an appreciation of what to balance and consider. One angle I was focusing on is the fact that much more space is required than with a combi boiler. Systems could work without a hot water tank. At the moment it would seem to me that buffer tanks could be a sensible choice for ROI. 

My perspective is that, given the wide range of considerations involved in the choices for these energy systems for each house (electricity tariffs, battery, PV, heat loss, lifestyle, disruption accepted, etc), it is not fair to expect the installer to be able to advise anyone to reach some optimal choice. I am someone that believes in standardisation, but the housing stock and all these factors differ too much. So it is probably a space where at best we have relatively standard system designs that need to be customised and sized.. If we ever get close to that 600k a year, the installers will be more specialised. So are our neighbouring heat pump installers going to be able to supply it?   

Posted by: @cathoderay
↑

And last but not least, much the same applies to DHW heating, We have to ditch the fossil fuel thinking, and instead go low with Steady Eddie, ie abandon the idea of instant hot water

Steady Eddie it will be. 😀

 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5740
Your energy: 75 kWh
 

Posted by: @batpred
↑

And by that I mean a tank used to keep heat that is used later to warm the space. 🙂 

Buffer tanks can best be thought of as part of a 'production line' for the heat, ie the heat passes through them but is not stored in them for any length of time.  If you want to store in a tank for later space heating you would need a much bigger tank and different pipework.  Its possible in principle but the scale of storage needed makes it difficult or impossible in practice.

The way to store energy for space heating is either in a battery or in the fabric of the house itself.  In particular houses with ufh buried in slab concrete flooring over insulation can be sometimes be heated quite effectively this way.  You 'batch heat' the floor when leccy is cheap, and it slowly releases over the next few hours.  Essentially is the old idea of a storage radiator.

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

Page 5 / 6

Share:
Click to access the login or register cheese