Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hi All My installer has just put up a 6 KW Solar PV array and is about to connect a Solis S6-GR1P5K inverter to it. This is rated at a max input of 7.5KW DC but a max output of only 5KW AC even though efficiency is stated at 97%. Does this make sense? Shouldn't they fit an inverter with an output of 6KW?
Rapid response appreciated because the electrician is due this afternoon to fit it!
Many thanks Tom
@trbob i’ll reply in more deteil when I get home but basically, this is a restriction placed on the grid by your DNO. Regards Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @tommclHi All My installer has just put up a 6 KW Solar PV array and is about to connect a Solis S6-GR1P5K inverter to it. This is rated at a max input of 7.5KW DC but a max output of only 5KW AC even though efficiency is stated at 97%. Does this make sense? Shouldn't they fit an inverter with an output of 6KW?
Rapid response appreciated because the electrician is due this afternoon to fit it!
Many thanks Tom
TBF you won't get 6 kW from your solar array for very long. You'll only get 6 kW if the sun and roof are at the right angle (South facing roof, around midday, during the height of summer). Any deviation from that and you won't be getting as much. For example, I have a South-East facing solar array that's 5 kWp (p = peak). But I only get 5 kW for a few hours a day, and only during the Summer months. If your solar array is, say, an East-West array, I doubt you'd get 6 kW at any time of the day/year, as it won't be facing the right way to produce that. There are websites I think where you can put your location, roof pitch, and panel orientation, and it will estimate how much power you'd produce.
The other thing to consider: is the inverter also connected to a battery, and is that connection a DC connection? In this case it's even less likely that you'll need the full 6 kW AC output, as some of the PV power will be remaining as DC and going into the battery before it's converted to AC and dumped into your house / grid.
Having said all that, I still insisted on an inverter that was capable of producing my 5 kW peak power, even though it won't make a difference 95% of the time. The difference in cost was some hundreds of pounds, which is a fraction of the total cost, and I just wanted the best setup. I got another quote from a different company for a 3.6 kW inverter, and their logic was as above (i.e. it won't make a difference most of the time), but I just wanted the best stuff. 5 kW is better than 3.6 kW so give me the 5 kW one please.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
@scrchngwsl My setup is 8.1 kWp (with panels on various orientations) my installer applied on a G99 form to my DNO and was granted a 5 kW connection. Without DNO approval a rig would be limited to 3.68 kW. My grid connection allows the 5 kW to flow via my Tesla Gateway and powerwall (I have actually seen 5.1 kW of power flow to the grid but this could be measurement errors I suppose). My system has only been in use since Aug.13th. and the best day’s production was that very first day: 41 kW/h. Having the battery and an immersion heater plus an all electric kitchen (and soon to be all electric house when the ASHP is installed next month) I don’t have a need to export much power at present but, come the summer Octopus Agile Outgoing will pay me quite decently for anything I don’t consume myself. This exporting will be ‘banked’ for the increased consumption when I am all electric and am powering the ASHP. So you can export up to 5 kW of power but should your rig produce above this figure, you may care to employ a Myenergi Eddi power diverter to your immersion heater or any other resistive load. Regards, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @scrchngwslPosted by: @tommclHi All My installer has just put up a 6 KW Solar PV array and is about to connect a Solis S6-GR1P5K inverter to it. This is rated at a max input of 7.5KW DC but a max output of only 5KW AC even though efficiency is stated at 97%. Does this make sense? Shouldn't they fit an inverter with an output of 6KW?
Rapid response appreciated because the electrician is due this afternoon to fit it!
Many thanks Tom
TBF you won't get 6 kW from your solar array for very long. You'll only get 6 kW if the sun and roof are at the right angle (South facing roof, around midday, during the height of summer). Any deviation from that and you won't be getting as much. For example, I have a South-East facing solar array that's 5 kWp (p = peak). But I only get 5 kW for a few hours a day, and only during the Summer months. If your solar array is, say, an East-West array, I doubt you'd get 6 kW at any time of the day/year, as it won't be facing the right way to produce that. There are websites I think where you can put your location, roof pitch, and panel orientation, and it will estimate how much power you'd produce.
The other thing to consider: is the inverter also connected to a battery, and is that connection a DC connection? In this case it's even less likely that you'll need the full 6 kW AC output, as some of the PV power will be remaining as DC and going into the battery before it's converted to AC and dumped into your house / grid.
Having said all that, I still insisted on an inverter that was capable of producing my 5 kW peak power, even though it won't make a difference 95% of the time. The difference in cost was some hundreds of pounds, which is a fraction of the total cost, and I just wanted the best setup. I got another quote from a different company for a 3.6 kW inverter, and their logic was as above (i.e. it won't make a difference most of the time), but I just wanted the best stuff. 5 kW is better than 3.6 kW so give me the 5 kW one please.
Thanks Scrchngwsl. My roof is due south and nicely pitched so should be able to hit peak pretty well in summer. Diverter to water heater is in but the that is after the inverter. Inverter is in the loft with AC connection back into the consumer unit. Battery and/or EV is on the long term plan but not yet designed in. I thought the limit from the DNO around here (mid Cheshire) was 6KW ? Seems a shame to put that beautiful array and then clip the top 20% of performance.
Hi. I'm new to forums so please forgive me if I've got this wrong but I'm hoping to put a thermal ground loop in our concrete foundations. As part of our building project we're hoping to use the Zehnder ComfoFond heat pump to cool/heat the incoming air from the mvhr. Wondering if anyone has knowledge of using concrete foundations for this purpose please. Regards, She's
Posted by: @scrchngwslI still insisted on an inverter that was capable of producing my 5 kW peak power, even though it won't make a difference 95% of the time. The difference in cost was some hundreds of pounds, which is a fraction of the total cost, and I just wanted the best setup. I got another quote from a different company for a 3.6 kW inverter, and their logic was as above...
The installer should not have used a 5kW grid-tied inverter under these circumstances.
It's not their decision - because they are required to operate within the permission granted by the Distribution Network Operator for your region.
Were they installing without having obtained the relevant G98 or G99 approval?
Have a look at the diagrams I've just posted over here for the benefit of @tommcl
If you'd like assistance to ensure that your installation is legal, then please ask for help over on that other topic, rather than here in the Welcome area.
I do have solutions to offer if you'd like.
Save energy... recycle electrons!
No worries, they got G99 approval from the DNO for the 5kW system.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
Posted by: @alexmHi. I'm new to forums so please forgive me if I've got this wrong but I'm hoping to put a thermal ground loop in our concrete foundations. As part of our building project we're hoping to use the Zehnder ComfoFond heat pump to cool/heat the incoming air from the mvhr. Wondering if anyone has knowledge of using concrete foundations for this purpose please. Regards, She's
According to the manual the 'brine' (Water and Anti-freeze mixture) pipework should be installed 1.2 to 1.6 metres below ground, because the temperature at that depth is a fairly constant 8C to 10C.
Unless I am looking at the wrong manual, the unit mentioned is a heat exchanger rather than a heat pump, and can be used to pre-heat or pre-cool the outside air being supplied to the MVHR unit. I assume that you have an additional form of heating for the Winter months.
Thanks Derek. Yes, in open ground the pipework should be 1.2m+ below the surface. We unfortunately can't get a long enough trench at those depths but do currently have more shallow trenches dug for our foundations. An insulated floor slab is going to be built off the foundations which might prevent the foundations from getting heated by the sun etc and so they might maintain a constant temperature even though they're not that deep in the ground.
Thanks for clarifying @alexm but I don't think that would work.
Firstly I would expect any GSHP installer to provide a desk-study/survey based on the characteristics of your local geology. From that you would get an idea of the lengths of 'slinky'-style collector coils which you'd require. But I would expect the required trenching to be many times greater than that which you would create for a strip-foundation on a domestic property.
Secondly, the body of ground from which you will be drawing heat needs to be sufficiently large that there isn't going to be the risk of the water/glycol mix in the pipes from simply freezing the ground which surrounds them!
If you wanted to try limiting the amount of ground in which the pipe coils are laid, then you'd need to be on a site which constantly replenishes that space with fresh 'heat'. In that situation you'd be looking to use a sloping site with a high water table and water slowly percolating across the layer holding the pipes.
Sloping sites, high water tables and moving ground-water are features which tend to be avoided if you're using strip foundations! 😲
If a site without sufficient horizontal space for pipe loops is to have a GSHP installed, then there are two ways forward:
- drill a borehole at least 200m deep (150mm diameter)
- find an adjacent abandoned mine-shaft and throw the heat collector coil into the flooded workings
Kensa heat pumps in Cornwall do precisely that to provide heat for their own offices and manufacturing site.
Talk to them. These guys know what they're doing!
Save energy... recycle electrons!
Posted by: @transparentThanks for clarifying @alexm but I don't think that would work.
Firstly I would expect any GSHP installer to provide a desk-study/survey based on the characteristics of your local geology. From that you would get an idea of the lengths of 'slinky'-style collector coils which you'd require. But I would expect the required trenching to be many times greater than that which you would create for a strip-foundation on a domestic property.
Secondly, the body of ground from which you will be drawing heat needs to be sufficiently large that there isn't going to be the risk of the water/glycol mix in the pipes from simply freezing the ground which surrounds them!
If you wanted to try limiting the amount of ground in which the pipe coils are laid, then you'd need to be on a site which constantly replenishes that space with fresh 'heat'. In that situation you'd be looking to use a sloping site with a high water table and water slowly percolating across the layer holding the pipes.Sloping sites, high water tables and moving ground-water are features which tend to be avoided if you're using strip foundations! 😲
If a site without sufficient horizontal space for pipe loops is to have a GSHP installed, then there are two ways forward:
- drill a borehole at least 200m deep (150mm diameter)
- find an adjacent abandoned mine-shaft and throw the heat collector coil into the flooded workings
Kensa heat pumps in Cornwall do precisely that to provide heat for their own offices and manufacturing site.
Talk to them. These guys know what they're doing!
It is not a GSHP, so there is very little chance of the pipework freezing underground. It is actually a heat exchanger to heat or cool the intake air to a MVHR system.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 917 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 7 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 8 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 11 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 12 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 13 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 14 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 16 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 16 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 22 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 23 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 6 days ago