Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant - Downstairs radiators not getting warm
Had a Vaillant 5kW installed last week and upstairs is getting up to temp ok, but all the downstairs radiators are luke warm at best.
I've tried balancing but no such luck. They are column rads, but I've got columns upstairs which are getting warm.
A couple of thoughts/questions - could this be resolved by topping up the system pressure more (analogue dial says 1.5, digital says 1.2); could I modify the remaining feed head setting (currently 900); or... Something else?
Also, my DHW doesn't seem to be getting up to temp. It has a 3 hour period over night to charge and I've set the offset to 15K which I thought would be enough. Any suggestions?
Thanks all!
Posted by: @samiebon1Had a Vaillant 5kW installed last week and upstairs is getting up to temp ok, but all the downstairs radiators are luke warm at best.
I've tried balancing but no such luck. They are column rads, but I've got columns upstairs which are getting warm.
A couple of thoughts/questions - could this be resolved by topping up the system pressure more (analogue dial says 1.5, digital says 1.2); could I modify the remaining feed head setting (currently 900); or... Something else?
Also, my DHW doesn't seem to be getting up to temp. It has a 3 hour period over night to charge and I've set the offset to 15K which I thought would be enough. Any suggestions?
Thanks all!
You had it installed only last week? I would suggest that you need to do nothing and get the installer back pronto!
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@samiebon1 Isn’t it a sad situation when we feel we must be ‘armed’ with an argument and / or a prepared report to hand over to the installer on their return when they have failed to carry out a good install? Perhaps the good installer would not have carried out a botched job in the first place but, wouldn’t it refreshing if the installer returned and said “Oh I am sorry we made such a mess of this job, we will put it right immediately and I am so sorry to have caused you this inconvenience in the first place!”? —— Yes, I live in cloud cuckoo land I know! 😉 Regrets, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @samiebon1Had a Vaillant 5kW installed last week and upstairs is getting up to temp ok, but all the downstairs radiators are luke warm at best.
I've tried balancing but no such luck. They are column rads, but I've got columns upstairs which are getting warm.
A couple of thoughts/questions - could this be resolved by topping up the system pressure more (analogue dial says 1.5, digital says 1.2); could I modify the remaining feed head setting (currently 900); or... Something else?
Also, my DHW doesn't seem to be getting up to temp. It has a 3 hour period over night to charge and I've set the offset to 15K which I thought would be enough. Any suggestions?
Thanks all!
Something is wrong with the plumbing for sure. Have the downstairs rads been bled? Are they on a separate primary or do they share a primary with the upstairs?
Unless your house is very tall 1.2 bar should suffice
Re the DHW what tank do you have and how much hot water do you use. Also what do you mean by 'up to temperature' 5kW is actually quite small if you use a lot of DHW. So if, for example, you are trying to heat 300l from cold (10) to 50, its going to take 3 hours
As @toodles says, at this stage its definitely something your installer should fix but I'm like you and prefer to be a step ahead!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa As far as I can tell they have been bled (water comes out when I bleed them). Theyre on the same primary as upstairs - 22mm copper running along upstairs, then down. Could anything be done with the 'remaining feed head' setting or is that a non starter?
Its a 150L 'UK Cylinders' heat pump tank. Its got a 3 hour window to heat in from ~36 to 48 deg so shouldn't take that long.
@samiebon1 Sounds as though the output from the heatpump is being throttled back in some way. If the system was sized appropriately, then all the radiators should be supplied with sufficient heat to bring them to temperature readily. There may be a blockage / restriction in the flow before the pipework descends to the ground floor radiators. Possibly an air lock; have you information on the consumption and how long the heat pump is running and idling? It is worth checking up on these points. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @samiebon1As far as I can tell they have been bled (water comes out when I bleed them). Theyre on the same primary as upstairs - 22mm copper running along upstairs, then down. Could anything be done with the 'remaining feed head' setting or is that a non starter?
OK so downstairs is 'after' upstairs. You may have to throttle down the LSVs upstairs, increase the pump head if thats an option, and open up (if you can) the LSVs downstairs. As @toodles says there could be an air lock, Vaillant has a 'purge' function in the installer menu which my installer said was supposed to deal with this (presumably by whacking the water pump up to max).
Posted by: @samiebon1Its a 150L 'UK Cylinders' heat pump tank. Its got a 3 hour window to heat in from ~36 to 48 deg so shouldn't take that long.
No it shouldn't, nowhere near!
Here is my 200l tank reheating today from/to about the same temperature. 22mm diameter feeds teeing off the 28mm primaries from the heat pump. I have a 7kW Vaillant. Something definitely wrong with yours, can you tell what temp the pipes are to and at the DHW tank and what diameter are they? I suppose its not possible that the installer has fitted a normal 3 way valve instead of a diverter valve (you would know as your heating would be on simultaneously with your DHW)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaI suppose its not possible that the installer has fitted a normal 3 way valve instead of a diverter valve (you would know as your heating would be on simultaneously with your DHW).
That happened with my installation. Whoever had been sent to the plumbing suppliers to buy various parts got the wrong type of valve. Once the system was running I noticed that one of the upstairs radiators was getting warm when the DHW was being heated. That was convection flow as the circulating pump wasn't running.
I think the pipe work and 3 way valve is ok from what I can see/read up. I had wondered if it's the settings - I have weather adaptation on so at the moment it's ~40deg flow, and my DHW offset is 15k (was 10k). Would this 55deg flow around the cylinder be enough to get up to target 48deg water temp?
The installer has arranged to come Monday so at least it's pencilled in!
Posted by: @samiebon1I think the pipe work and 3 way valve is ok from what I can see/read up. I had wondered if it's the settings - I have weather adaptation on so at the moment it's ~40deg flow, and my DHW offset is 15k (was 10k). Would this 55deg flow around the cylinder be enough to get up to target 48deg water temp?
The installer has arranged to come Monday so at least it's pencilled in!
DHW flow temp is completely separate to space heating flow temp. The offset is added to the target DHW temp to get the FT for DHW. 15K should be ample in principle although the cylinder supplied has a relatively small area coil (1.6 sq m) compared to 3 sq m often recommended. That said so does the Vaillant 150l cylinder! Feels to me like something is wrong, suggest you check the pipe temps near the DHW cylinder if you can!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 116 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 48 minutes ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 1 hour ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 1 hour ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 1 hour ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 2 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 3 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 4 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 6 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 6 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 8 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 11 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 14 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 1 day ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 2 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago