Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

[Solved] Vaillant aroTherm not heating with many faults

16 Posts
5 Users
14 Reactions
5,622 Views
(@anon67)
Active Member Member
Joined: 11 months ago
Posts: 6
Your energy: 0 kWh
Topic starter  

Thank you all for your help with trying to get this sorted. Just a quick update to close this thread off incase anyone has similar in the future. 

I phoned Vaillant on Monday, spoke to the tech support line, he said going off the fault codes he suspected it to be low on refrigerant so he booked me an engineer visit. 

Tuesday morning the DHW started faulting displaying similar messages compressor blocked etc

Guy came out late yesterday afternoon, zero pressure in the refrigerant circuit, pressured it up with his test gas, could watch pressure dropping off immediately and could physically hear a leak. Traced to the evaporator, which isn't replaceable or repairable so they are replacing the full unit. 

Hopefully it'll be all sorted by next week. 

 


This post was modified 10 months ago by Anon67

   
Like
2
ReplyQuote
(@ashp-bobba)
Prominent Member Member Professional+
Joined: 2 years ago
Posts: 505
Your energy: 2 kWh
 

@anon67 Pleased they are replacing it for you and I am pleased when I said they are quite good with their warranty they actioned it.

Good luck with the replacement 


AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.


   
Like
2
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5047
Your energy: 82 kWh
 

@anon67, glad to hear they’ve found the issue and that it’ll be replaced. Hopefully that goes smoothly. Will Vaillant be doing the replacing themselves?


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Mitsubishi Electric
Famed Member Moderator
Joined: 5 years ago
Posts: 2264
Your energy: 45 kWh
 

The mark of a good company to deal with is less to do with them not having issues as much as how they deal with them when they arise. Glad you’re on the way to a quick resolution and props to Vaillant so far for playing fair.


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Home Assistant to make it all play nicely together
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
Like
2
ReplyQuote

Page 2 / 2

Share:
Click to access the login or register cheese
Protected By
Shield Security PRO