Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
Posted by: @luciaMy question - brain knot - is am I better going 4KW with more /bigger rads or 6kw with more/bigger rads
We have a heat demand of 3.5kW at -9 and are using a 6kW heat pump, which outputs nearly at 7kW at 12 degs and just under 6kW at -10. It cycles, but importantly doesn't short cycle. It will run for 10 to 15 mins and then circulate water for the next hour or so, then run for another 10 to 15 mins. It is a normal capacity control.
I would go for a 6kW, remember you need to heat your hot water cylinder also. My 6kW heat our 210L twice a day and it takes around 40 mins at a time. The 4kW will take 50% longer. So if you choose 4kW your heating will be off for 2 hrs minimum a day.
The colder it is outside and the longer the heating spends off the more the heat pump has to play catch-up, so running full load instead of part load. On the coldest day the 4kW may never catch up, so runs at full load all day.
I would choose the 6kW every time
@johnmo
Thank you soooo much for this reply - it was exactly the kind of informed response I was hoping for.
Efficiency/running costs are fundamental for me.
Also, I feel the cold via humidity too and not just temperature. In the winter, even if it's say 8-10º outside, if it then rains I have to turn the heating up or I get cold.
I'm not sure how they'll respond to the rad upgrades but my fingers are crossed because it will give me more leeway with lower flow temps. 🤞🏻
@lucia My octopus survey has just been completed and he has put a note on my survey that I requested a 45C design temp so they are listening? Out of interest his heat loss calc was 5.25 kW as BG was 3.46 kW! and Heatpunk gave me 4.9 Kw.
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
OK Houston we have lift off 🚀 🥳
So 🐙 just phoned here's the deal:
6kw Daikin
My two extra rad upgrades (K2s in hall and bedroom) accepted. ✊🏻
One year's free service plan.
Big NO to 45º design temp (with the implication that was pushing it re changes to original design) but I think it's no worries because I got the rads so I have more room for manoeuvre anyway.
Contract on its way.
I think that's the best I can do? Feedback gratefully accepted. 🙂
Posted by: @luciaPosted by: @toodles@lucia Sounds to me as though you have made great progress (and I suspect, Octopus staff have learnt a few things about customer’s want and needs and heeding them!). Did you manage to get them to design out a LLH or buffer tank? Though I could not employ Octopus to install my system (as relayed ad nauseam elsewhere), I still think they will install a good system at a good price - and at least they are a company that listen and have the resources behind them to rectify any problems. Regards, Toodles.
I agree @toodles that for me with limited resources they are the best deal - plus I really liked the lead installer (who may not be my installer -dunno yet).
But I don't know if I have made great progress ... that's the problem. 6kw is the result BG came up with if designing for no cavity wall insulation.
4kw was borderline for Octopus.
My question - brain knot - is am I better going 4KW with more /bigger rads or 6kw with more/bigger rads (hall/bedroom as identified by me above)?
I need to keep running costs as low as possible without getting cold. 🤔
It hasn't got a buffer it has a volumiser and I'm not pushing back on that.
I don't want the short cycling probs of a too big heat pump but I don't want a too small one working flat out when it's cold or wet.
From your information you need 6kW. Bigger radiators DON’T give you the heat output you need, all you would have is lower temperature flow and a too cold house.
You seem to have won a lot from Octopus and you can always change the radiators in the study and hall in the future if leaving the doors open doesn’t get the rooms warm enough.
Obviously if you get 2 bigger radiators then that’s a big win for you but you have won enough with the 6kW.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
From your information you need 6kW. Bigger radiators DON’T give you the heat output you need, all you would have is lower temperature flow and a too cold house.
You seem to have won a lot from Octopus and you can always change the radiators in the study and hall in the future if leaving the doors open doesn’t get the rooms warm enough.
Obviously if you get 2 bigger radiators then that’s a big win for you but you have won enough with the 6kW.
Er?
Sure, I know what bigger radiators do - obviously they permit me to run at a lower flow temp which is precisely why I lobbied for them. Running costs matter to me. I'm shoe string productions here.
Thus the two radiators in the living/ dining room were already being upgraded to K2s and now I have two more in the next two most used areas - the bedroom/office and hallway.
I'm miffed about the 50º design temp but hopefully the bigger rads facilitate dropping that.
My aim is to run an open loop system at a flow temp of 40º - I think this gets me as close as possible to that for the cost and certainly leaves me much more room for manoeuvre.
I have to supply the bathroom rad because I want a 'designer radiator' but otherwise I think/hope this will be ok.
I'll try post the specs and floor plan eventually.
Now I know the volumiser is not the greatest but Octopus will not fit a system without one. And at least it's not a buffer tank.
It's a bit beggars can't be choosers but I can't afford those heat geek levels of money.
@lucia My system was set out on the MCS forms indicating that the calculations had been based on a 50 degree C. flow temperature and that is where the installers aimed all the settings upon commissioning the system. It was a mild day in mid-February 2023 and not a lot of heat was required. The engineers did their bit and as fast as they tried to set up the LWT and then the radiators, I instructed them to ‘now leave that as you initially set it and I’ll do the tweaking’. Before they left, they knew I was lowering the LWT and within a day or two, I had the system down to 35 degrees C. Of course, I couldn’t be sure that this would suffice as it was still very mild. Come the autumn, I found a balance of LWT at 35 and WC set up, things were very stable and only needed a little tweaking when very cold or very mild. When last winter arrived I had the Homely smart controller in place and noted that 35 degrees C was rarely exceeded and we were very comfortable. When the OAT dropped to -7 or -8, Homely would adjust the LWT to about 43 - 45 but I have never seen it exceed this and we like a room temperature of 22.5 degrees C. 24/7. Regards, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles Thank you that's really helpful.
I reckon I have the basis for a good set-up but installation is not likely to happen until October.
I don't know why 🐙 are so obsessed with 50º (my installer said cheaper installations) when everyone else, including British Gas, design for 45º.
When I've got some time I'll play with the very useful radiator output spreadsheet that @derek-m gave me.
@lucia if your house needs 6kW then that is what you need. There’s nothing you can do with bigger radiators to make a 4kW heat pump give you enough heat power.
Yes you are completely right to consider operating costs and try to get a design and installation which will give you lower flow temperatures by using larger radiators. Good luck with it all. October isn’t too bad as a waiting period and it’s rarely that cold by then.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
-
Heat pump done right first time? Installation in Kent.
3 weeks ago
-
Daikin 6kw setup with Dixell controller
2 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
6 months ago
-
Are Octopuses Slowing Consumer Adoption of Heat Pumps?
7 months ago
-
Vaillant arotherm plus heat pump frost protection
1 year ago
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 292 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago