Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
To zone or not to zone?
There are a lot of posts on this forum suggesting heat pumps should be run with a single open loop. I struggle with this concept in our house due to temperature variations. It's about 240 m2 but L shaped and the main rooms face SSW. It has quite large windows. Four bedrooms, two living rooms, main one facing south, the other facing N and E. Kitchen/Dining facing S and W but shielded from most of the S sun due to a loggia which is great in the summer! Also an office. The hall is double height but does not get much sun (limited windows and loggia) and is effectively between the living rooms and kitchen/dining.
On a sunny winter day we get lots of solar gain. Last week when it was minus 1 outside and lots of sun the main living room stayed over 21 degrees for about four hours with no heat. However on a dull day, same outside temperature, it will struggle to get to 19 degrees with heat. Also other parts of the house don't benefit from the sun and are much colder. On the same sunny day without heat they would drop to say 14 degrees or below. Due to the layout of the house it is far removed from an open plan arrangement and some rooms, such as the office (cold side) are really quite separate.
It's impossible to set a flow temperature that will work in all rooms with no zoning or local TRV control. Also, it is running with weather compensation but of course not sun compensation. I know systems like Homely will look at sun levels but that only has one temperature sensor and if that was in the main living room it would turn the flow temperature down so low we'd freeze in other rooms.
I have an opportunity at the moment to re do our heat pump set up completely - it's a three year long story that I'm not going to delve into - and I really want to get it right this time.
The heat loss is about 14kW and one option I'm considering is basically two systems - one for the sunnier bits and one for the cold area. This would be reasonably easy to achieve, but still not convinced about the sun factor unless I go for something like Homely. Would the living room be representative of temperatures in the other living areas - I'm doubtful. Also the sun makes virtually no difference on the cold side and I'd struggle to think where I could put a single temperature monitor that would be representative.
Anyone any thoughts?!
My initial reactions are this.
I don't know where you are in the country but 14kW is quite high for 240sq m suggesting some insulation might help.
You might want to run it open loop for the cold side and have trvs on the warm side to adjust for solar gain when necessary, but have the warm side lockshields adjusted so when there isn't solar gain both sides remain about right (basically running open loop throughout on WC on dull days, on bright days open loop on WC cold side, modulated by the trvs warm side
If you post a plan it might be easier to comment.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Solar gain would result in an increase in return temperature, and the heat pump will throttle back or turn off, reducing heat input - provided you're running open loop without a buffer.
It's self regulating.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @chrislayThere are a lot of posts on this forum suggesting heat pumps should be run with a single open loop. I struggle with this concept in our house due to temperature variations. It's about 240 m2 but L shaped and the main rooms face SSW. It has quite large windows. Four bedrooms, two living rooms, main one facing south, the other facing N and E. Kitchen/Dining facing S and W but shielded from most of the S sun due to a loggia which is great in the summer! Also an office. The hall is double height but does not get much sun (limited windows and loggia) and is effectively between the living rooms and kitchen/dining.
On a sunny winter day we get lots of solar gain. Last week when it was minus 1 outside and lots of sun the main living room stayed over 21 degrees for about four hours with no heat. However on a dull day, same outside temperature, it will struggle to get to 19 degrees with heat. Also other parts of the house don't benefit from the sun and are much colder. On the same sunny day without heat they would drop to say 14 degrees or below. Due to the layout of the house it is far removed from an open plan arrangement and some rooms, such as the office (cold side) are really quite separate.
It's impossible to set a flow temperature that will work in all rooms with no zoning or local TRV control. Also, it is running with weather compensation but of course not sun compensation. I know systems like Homely will look at sun levels but that only has one temperature sensor and if that was in the main living room it would turn the flow temperature down so low we'd freeze in other rooms.
I have an opportunity at the moment to re do our heat pump set up completely - it's a three year long story that I'm not going to delve into - and I really want to get it right this time.
The heat loss is about 14kW and one option I'm considering is basically two systems - one for the sunnier bits and one for the cold area. This would be reasonably easy to achieve, but still not convinced about the sun factor unless I go for something like Homely. Would the living room be representative of temperatures in the other living areas - I'm doubtful. Also the sun makes virtually no difference on the cold side and I'd struggle to think where I could put a single temperature monitor that would be representative.
Anyone any thoughts?!
The idea that James proposed of using TRV's in the solar gain rooms should work, and is probably the easiest and simplest solution.
An alternative would be a mixer tank for the solar gain area, which could be used to lower the LWT going to those heat emitters. If you look through the Ecodan manual they suggest such a system.
Posted by: @hughfSolar gain would result in an increase in return temperature, and the heat pump will throttle back or turn off, reducing heat input - provided you're running open loop without a buffer.
It's self regulating.
I think the problem OP has is that some rooms get too hot while others remain cold.
Posted by: @derek-mThe idea that James proposed of using TRV's in the solar gain rooms should work, and is probably the easiest and simplest solution.
An alternative would be a mixer tank for the solar gain area, which could be used to lower the LWT going to those heat emitters. If you look through the Ecodan manual they suggest such a system.
My assumption is that the solar gain doesn't happen every day/all of the time so it needs an time-variable adjusting solution, hence my proposal of of TRVS in the warm area only. Obviously if the warm area is permanently too warm, then a mixer to reduce FT will work, or reducing the area of the emitters in that area, or possibly turning down the lockshields a lot (but many lockshields have only a very small proportional range, they are basically on or off, so equally this may not work)
There is scope IMHO for heap pump optimised TRV heads featuring proportional control, slow response (or possibly variable response time, a sort of learning mode and an operational mode) and which never quite shut down. These could, in principle, self-balance for the correct temperature and then operate as limiters, ie just the function we need. Electronic TRV heads already have all the required hardware, they just need different firmware.
@chrislay if you would like to post a plan we might be able to do better.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Ah, if some rooms are too cold then that needs to be fixed by either increasing emitter size, or improving insulation in that room.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
We run on WC but the UFH heating was set up with separate loops to every room. Each has its own thermostat, which provides the upper temperature limit in that room.
But even with proper insulation I think it's sometimes impossible to get all rooms up to a desired temperature. Our entrance lobby/downstairs loo, is a new pitched roof (south facing) addition to the outside of the original 20" thick stone wall of the building. It has its own UFH loop and, as new build, is cavity wall insulated. On cold winter days it can be difficult to get the temperature above 12C to 14C, when beyond the internal door through the original exterior wall, it's a cosy 20C. As a small external addition it has a high surface area to volume ratio compared with the rest of the property (we have internally insulated the external walls) and I think it suffers disproportionate heat loss as a result (plus maybe more through the front door). I gave up trying to heat it properly as it seemed that the ASHP would be running constantly just to reach that level, even when the rest of the house was OK. The thermostat in that area is now set to 14C.
Mike
Grant Aerona HPID10 10kWh ASHP
Posted by: @chrislayThere are a lot of posts on this forum suggesting heat pumps should be run with a single open loop. I struggle with this concept in our house due to temperature variations. It's about 240 m2 but L shaped and the main rooms face SSW. It has quite large windows. Four bedrooms, two living rooms, main one facing south, the other facing N and E. Kitchen/Dining facing S and W but shielded from most of the S sun due to a loggia which is great in the summer! Also an office. The hall is double height but does not get much sun (limited windows and loggia) and is effectively between the living rooms and kitchen/dining.
On a sunny winter day we get lots of solar gain. Last week when it was minus 1 outside and lots of sun the main living room stayed over 21 degrees for about four hours with no heat. However on a dull day, same outside temperature, it will struggle to get to 19 degrees with heat. Also other parts of the house don't benefit from the sun and are much colder. On the same sunny day without heat they would drop to say 14 degrees or below. Due to the layout of the house it is far removed from an open plan arrangement and some rooms, such as the office (cold side) are really quite separate.
It's impossible to set a flow temperature that will work in all rooms with no zoning or local TRV control. Also, it is running with weather compensation but of course not sun compensation. I know systems like Homely will look at sun levels but that only has one temperature sensor and if that was in the main living room it would turn the flow temperature down so low we'd freeze in other rooms.
I have an opportunity at the moment to re do our heat pump set up completely - it's a three year long story that I'm not going to delve into - and I really want to get it right this time.
The heat loss is about 14kW and one option I'm considering is basically two systems - one for the sunnier bits and one for the cold area. This would be reasonably easy to achieve, but still not convinced about the sun factor unless I go for something like Homely. Would the living room be representative of temperatures in the other living areas - I'm doubtful. Also the sun makes virtually no difference on the cold side and I'd struggle to think where I could put a single temperature monitor that would be representative.
Anyone any thoughts?!
Here are some thoughts for consideration, they may depend upon the location of your heat pump and whether it also gets some solar gain.
You should indeed treat your home heating system as two separate areas as far as control is concerned.
I will deal with the colder area first, the temperature of which I would suggest should be regulated using WC control, which should be adjusted to maintain the desired temperature in the coldest room, which should also have any lockshield valves fully open and of course no TRV's. The temperature in the remaining rooms in the colder area should be set by adjusting the lockshield valves if at all possible, or TRV's as a last resort.
The accuracy of the above of course would be dependent upon the OAT sensor on the heat pump not suffering from solar gain itself. Where is your heat pump located?
There are options for the temperature control in the warmer area, which again are dependent upon actual conditions.
If all the rooms suffer from about the same temperature increase due to solar gain, then I would suggest a zone valve controlled by a suitably located thermostat, which would shut-off the water flow through the heat emitters when the room temperature reaches the desired level. This option of course would require the pipework to be arranged into a warmer zone and a cooler zone.
If room temperatures vary with solar gain or it is not possible to arrange the pipework into two zones, then individual TRV's on the radiators would be my suggestion.
A completely different solution could be some form of ducted air system, where the solar gain heated air is moved from the warmer rooms to the cooler rooms.
Thanks all for the suggestions. I'm currently taking to some installers and waiting to hear what their solution is. I'll come back later when I can hopefully report from a comfortable house with an efficient system!
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 340 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 10 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 18 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 13 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 14 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 14 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 17 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 23 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 23 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago