Three pipe buffer
The club I am a member of is having a heat pump installed and the schematic shows a three pipe buffer. I have not seen this before and could find only one mention on Linkedin. I wonder what members think of this arrangement?
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
Caleffi speak in one of their tutorials about the benefits of a 3 pipe buffer. Someone else may have taken the trouble to understand it. As always I would ask the question - why do I need a buffer at all. If the answer isnt satisfactory then I would find another installer.
I note a mixture of rads and UFH both run at the same flow temperature as no mixing is shown. That means either your floor are going to be very warm or your rads are going to be very cool. Are these existing emitters or new, whats going on here?
For what its worth I did ASHP in three community centres. Because they were principally large rooms, I went for A2A and background electric heating in the 'small' areas. It worked a treat and achieved a factor of 4 reduction in carbon.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Sadly the answer to why a buffer tank was, I've been working with Heat pumps for 47 years and we know this works.
The club has 14 showers that will be used quite heavily on a couple of days every week in the summer (it is a sailing club). I hope they will have enough hot water with 2 300 litre DHW tanks. In winter it is little used. They have 8Kw of Pv and the same in batteries but with an older gas boiler fed by an LPG tank both of which need replacing. My suggestion of some solar thermal was rejected out of hand.
The club officer basically called in his favourite Installer to get a quick quote to get a council grant so it won't cost the club much to fit but we will see how much it costs to run!
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
It sounds rushed to me but also that it may not be possible to question the direction. I hope you are lucky!
Since he has been doing it this way for 47 years he should be able to provide some references and so you can speak to customers with a similar installation.
If I were the club officer I would be having a quiet word with the Council about flexibility to use another installer, then do the procurement job properly. They are unlikely to want to waste their money and the club needs certainty that the system is going to work. From what you say it hasn't got it. Id also seriously consider A2A for the clubroom (you presumably need it to heat up for a short time only - so heating the air makes more sense than heating radiators which then heat the air). 600l is 42 l per shower which sounds enough, but if each is used multiple times in a short period it wont be. This needs nailing down IMHO.
Im not getting the warm and fuzzes that due diligence has been done and just because its not the Club's money is hardly a good reason to skip that stage.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Coincidentally, I had an introductory visit from a very reputable installer the morning and after a very quick look at my present system he suggested that a 3-port buffer may be an option in my case. He attempted to explain it to me but I was more interested in covering other topics on this first visit and what he explained didn't sink in. I think it may have been something to do with the difference in water volumes or flow rates/pressures in different branches of the system. It's something I will need to understand if the requirement firms up.
Update. The system was fitted and commissioned last week, by Friday the radiator zone was still not coming to temp. On Wednesday we had a meet with the Installers and went through the system. Some adjustments were made (I am not sure what) and it started to warm up. The system relies entirely on thermostats calling for heat. I tried to question the need for the buffer and the response was quite bullish. They believe all systems need a buffer and they will always fit them and tried to tell me that it is a requirement of Part L!! They insist that open zone thinking is misguided! (@editor maybe you can get Total Renewable Solutions Axminster to explain their their reasoning on buffers in a podcast?) Next I will try to find how the Pv and Bess will be used to offset the electric useage. @jamespa since the coordinator of this project is the Vice Commodore and a building contractor I have be circumspect in my observations, after all what do I know? I haven't got a heat pump and most of my, er 'knowledge' is from this forum and they are the experts.
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
Posted by: @jancoldThey believe all systems need a buffer and they will always fit them and tried to tell me that it is a requirement of Part L!! They insist that open zone thinking is misguided! (@editor maybe you can get Total Renewable Solutions Axminster to explain their their reasoning on buffers in a podcast?)
I will make a note of Total Renewable Solutions Axminster, but I'm guessing that like all other installers that use buffers they won't come on the episode. But if they're so bullish, maybe I'll get lucky.
Buffer tanks are not a requirement under Part L. As I understand it, Part L is about the conservation of fuel and power. While it sets standards for energy efficiency and system design, it does not mandate buffer tanks in heat pump systems. In fact, considering how inefficient many buffer tanks are (especially when poorly installed) you could argue that Part L should advocate for their removal rather than their inclusion.
I'm scheduled to record a video on our buffer tank tomorrow which I hope will go live this weekend to show the short fallings of the system in our property.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@jancold thanks for the update!
Posted by: @jancold@jamespa since the coordinator of this project is the Vice Commodore and a building contractor I have be circumspect in my observations, after all what do I know? I haven't got a heat pump and most of my, er 'knowledge' is from this forum and they are the experts.
Fully understood. Since I'm just some bod on the internet in no way connected to the project Im not bound by these constraints.
Posted by: @jancoldI tried to question the need for the buffer and the response was quite bullish. They believe all systems need a buffer and they will always fit them and tried to tell me that it is a requirement of Part L!! They insist that open zone thinking is misguided!
There are (I understand) still people who believe that the world is flat. I wouldn't rely on them for navigation. There are (i have heard) people who believe that injecting chlorine might be a good way to treat disease. I wouldn't rely on them for health advice.
Seriously though I hope my concerns are misplaced and that it all works at a reasonable running cost.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@editor Looking at some of the changes to Part L this at the end of 5.20 this had me perplexed.
NOTE: There is no need to install thermostatic room controls in rooms/zones without heating in new or existing dwellings. 🤔 🤔
So I don't need a thermostat in my unheated conservatory,who would have thought!!
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
@toodles Sound advice sir! (At present having a consumer unit changed so running his coffee machine from his EV, so smug 🤣 )
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
- 27 Forums
- 2,484 Topics
- 57.3 K Posts
- 498 Online
- 6,196 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Warranty Repairs- An Un Eddi fying experience!
@editor Did you have one of the really old ones with th...
By swwils , 2 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna I’ve just DM’d you a potential company that’s ...
By Mars , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
Actually not that far, however, the cost of my...
By upnorthandpersonal , 2 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@petch I’ve not come across anyone yet that’s used thes...
By Mars , 2 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
Steady green means that the pump is running full speed....
By smsm1 , 3 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
@jamespa I meant to say I attached the report from the ...
By Fiona , 3 hours ago
-
RE: Rate the quality of your heat pump design and installation
I don’t have the strength to post this tonight, but I’v...
By Mars , 3 hours ago
-
Vaillant app under reporting flow temperature
Our Vailllant 5kW heat pump is working well and the hou...
By Bengeo , 4 hours ago
-
@boycey, in your scenario if you use Melpump to change ...
By Majordennisbloodnok , 8 hours ago
-
RE: A Smarter Smart Controller from Homely?
Yep- already done that....nothing novel as such but som...
By benson , 8 hours ago
-
RE: Help needed to adjust weather compensation on Vaillant air source heat pump
I am in the fortunate position of having independent mo...
By MartinRobinson , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils Similar here, though it has been very mild. I...
By KevH , 11 hours ago
-
RE: Home energy storage & battery register
@toodles thankfully we have a range of tariffs to meet ...
By TechnoGeek , 13 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor thanks Mars! I'll contact them.
By kevinmc1970 , 14 hours ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@heymikey thanks for the update and sorry to hear that ...
By Mars , 1 day ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
@jamiejones85mespa your comments are spot on with my th...
By AgentGeorge , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
Must of knocked a load of crud through when they added ...
By Burtis , 1 day ago
-
@mkz, yes I have other installers... can you please sen...
By Mars , 2 days ago
-
I should add that our survey came up with a heat loss o...
By MartinRobinson , 2 days ago
-
RE: Optimising LG Therma V R32 using AI
@bontwoody oh dear! ... but as you say.. I suppose th...
By Tim441 , 2 days ago
-
RE: Volumiser required on Grant R290 air source heat pump?
@judith Indeed it's similar to the UK. It has to be an ...
By Patrick , 2 days ago
-
RE: Say hello and introduce yourself
Underfloor hydronic, powered by both the heat pump and ...
By upnorthandpersonal , 2 days ago
-
RE: PV export revenue and HMRC
That makes sense. They are companies that are on market...
By Batpred , 2 days ago
-
RE: R290 Heat Pump and Foundation Air Bricks
I have been having fun and games whilst getting surveys...
By petch , 2 days ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@ashp-bobba brill thanks again!
By cmartinbwmba , 3 days ago