Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Solar to power Heat Pump for DHW
I have a solar PV inverter rated at 4kW and the Mitsu heat pump is timed to heat DHW at 3:00pm (at least iin the summer months). The power increases to say 6kW as the temperature in the tank approaches the 50C setting, even though I am on the lower Mitsu setting for DHW.
At that time my storage batteries are fully charged and I would have expected they would be able to contribute to the load, see screenshot
i.e Load 6.62 : Ppv 3.69: Batteries SOC 100% Discharging Power 0.85
However, my supplier tells me that the Inverter rating dictates the amount that the batteries can provide.
Is he correct that I can get no more out of the batteries under conditions like this?
If so heating DHW during daytime doesn't seem a good option
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @davidalgarveHowever, my supplier tells me that the Inverter rating dictates the amount that the batteries can provide.
This is correct. Inverter limits protect grid and internal wiring.
Posted by: @davidalgarveIf so heating DHW during daytime doesn't seem a good option
Depends on your tarrif. For me it makes sense to heat dhw at night at 6.7p/kWh and export excess solar during the day at 16.5p/kWh. I don't have a battery.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I was going to ask what model of Growatt inverter you had, @davidalgarve, but I did a quick scan of one of your previous threads and found out. In doing so, I also found @robs provided this answer to a very similar question you posted in that thread.
https://renewableheatinghub.co.uk/forums/postid/41612/
That appears to answer your question here too. Your inverter is running in Load First mode, so any household load will be met by what your panels are generating first and the battery will be used to supplement up to the inverter's limits. The previous thread I mentioned showed your inverter is an MOD4000-TL XH and can only convert a maximum of about 4kW of DC current to AC with any load above that having to come from the grid. That being the case, it seems to me there's never going to be a time of day when your house can place a load of 6.6kW without some power being drawn from the grid.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @davidalgarveI have a solar PV inverter rated at 4kW and the Mitsu heat pump is timed to heat DHW at 3:00pm (at least iin the summer months). The power increases to say 6kW as the temperature in the tank approaches the 50C setting, even though I am on the lower Mitsu setting for DHW.
Wow, how big is your heat pump that it is pulling 6kW during a DHW cycle? I suppose if it's a 16kW model, and it is requiring a LWT of 60C to achieve a tank set temp of 50C, then it may pull that much towards the very end of the cycle, but it won't be for long.
As others have said, you are limited by your 4kW inverter, so the combined solar and battery output is 4kW max. Whenever the house load exceeds 4kW, the excess will always be pulled from the grid.
There are two factors to consider when determining the optimal time to run your DHW cycle. The first is outside ambient temp (OAT), as the heat pump will always be more efficient when the OAT is warmer, which normally means the early afternoon. Secondly, there is the price of electricity, so if you are on a very cheap overnight tariff, half price (or lower) electricity will always offset any efficiency gains by running at a warmer time of day. With a battery, you can smooth out electricity pricing, but not fully in your case as you see from above you will still be pulling some power from the grid. Also for you, trying to minimise other household load whilst the DHW cycle is running will minimise the amount of excess above 4kW you pull from the grid.
Is there not a lower power mode you can select for your heat pump (on Samsung, it's called quiet mode which basically limits the input/output to ~70%). I use this in summer for my DHW cycles so I can keep my usage totally within my solar generation rather than drawing from the grid. This way you can minimise the amount of power you draw from the grid by running lower and slower for as long as possible during the DHW cycle.
Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 1,858 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 4 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 5 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 5 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 5 hours ago
-
RE: Why don't people choose heat pumps?
With a heatpump tariff, it should be cheaper to operate...
By Batpred , 5 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 5 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 9 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 12 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 3 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago