Significance of delta betweeen flow and return temperature
Hi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Hi,
The simple answer is yes, the delta T of the flow and return water does impact the efficiency and energy use of a heat pump.
It takes a defined amount of energy to heat a specified amount of water by 1C. So if the water is entering the heat pump at 20C and exiting at 40C, then it will have required 4 times more energy to heat the water than if it was entering at 35C and exiting at 40C.
Picking up this significance of deltaT topic again but from the opposite side.
My system is an Daikin Altherma 11kw Monobloc, described in other threads. I have it working with weather comp, with the internal controller modulating the leaving water temperature. It's working alright, COP about 3.2, but I notice after the overnight setback, the pump runs nicely with a deltaT around 5C, and if I record the meters (fitted as part of a trial) the COP for this period is up above 3.6, but as the house reaches temperature a bit of modulation happens reducing the leaving water temperature gradually, but then leaving and return water temperatures end up being very similar, often the same for several hours, so no deltaT. The house is warm enough, so there is no heat demand in the property but the pump keeps running in this tick over state, and this drops the COP drastically because the ASHP is using electricity but not putting heat in to the property. So that's the scenario. Should I be trying to achieve a greater deltaT through the radiators? I could wind in the locksheilds on my rads, whilst keeping the system balanced, to reduce flow and allow a greater temperature drop across them? This is counter intuitive though as I've read that high flow rates are better for heat pumps.
Thoughts appreciated about whether I'm over thinking this one.
@adaml I don’t have the option to set a maximum modulation value, for some reason that menu option doesn’t show. It’s the 11kw Altherma monobloc, the last gen, not the latest one.
The curve is 44C/-5 and 23C/15
@adaml I worked it, I scrolled through the overview settings, I’d left this lot alone until now.
8-06 looks to be 3. Have I read that correctly? Is that a sensible number? I’m guessing it’s not enough. Today with the solar gain the house is up at nearly 23C, with the LWT at around 30C.
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 24 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 9 hours ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 15 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I think that QR code is to download the app SmartHome o...
By cathodeRay , 21 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 24 hours ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 2 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 2 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 2 days ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 4 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 4 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 5 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 5 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 5 days ago