Seeking Help for In-Principle Quote to fix a botched heat pump installation by Heat Geek Installer

68 Posts
12 Users
27 Reactions
1,528 Views
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2241
 

Posted by: @drei

I am using Home Assistant's utility meters, so they add up the relevant data based on live readings, to make up the daily, weekly, monthly and yearly data. These will eventually get better, as right now it doesn't have a whole month worth of data, or a year.

The handicap is that it is still using the Heat Pump sensors, as it is connected to it via WiFi, and every now and then, Samsung wants HA to re-authenticate, which will cause a gap in the data, unless I can pick it up straight away.

In effect you are relying on the manufacturer marking their own homework. Is there any way you can validate these readings? For example, I have an independent kWh meter that supplies only the heat pump, that I use to validate my modbus collected kWh in data, and yes, there is a discrepancy, the modbus/Midea data is an under-estimate, possibly because that data is just for the compressor, excluding ancillaries like the circulating pump. The discrepancy is reasonably stable over long periods of time, and I deal with it by using a 'discrepancy correction factor' in my calculations to bring the calculated kWh figures into line with the independent kWh meter figures.

I do think you need to get to the bottom of the discrepancies in the earlier image you posted where the daily and weekly totals are significantly less than the sum of the parts. I presume these are energy inputs, can you also do the same checks on energy out data (which I believe you have access to, based on your earlier posts)? It may throw some light on why your COPs are low. GIGO and all that...


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2241
 

Posted by: @benson

No. 12kW is obviously the maximum heating capacity (at certain conditions, dependent on manufacturer) but the actual maximum consumption will be much lower than that. I think our 12kW max power input is around 5kW. You can get the figures for yours from the technical bulletin, data sheet etc.

This is all part of the smoke and mirrors around heat pump marketing. My unit is badged as a 14kW unit, but the maximum it has ever put out is 11.52kW. The problem is that while it may be able to put out 14kW on a sunny spring day, in practice it never does, because I don't need 14kW to heat the house in those conditions. When it is much colder outside, and I could do with a few more kW, the heat pump performance is compromised by the lower outside temperatures, and cannot reach it's badged output. As it happens, 11.52kW is pretty close to the tabulated output in the Midea Engineering Data manual at around zero degrees outside, but that is cold comfort so to speak for the disappointed owner who thought he or she might have had a 14kW heat pump.

It's the same as selling a car as an 100mph car and not mentioning that only happens going downhill with a following wind. Going uphill with a head wind is a rather different story...


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@benson)
Reputable Member Member
Joined: 1 year ago
Posts: 188
 

@cathoderay I think this was a different point unless I've misunderstood. DREI was asking about the actual power input to the unit itself and whether this meant, for example, a 12kW unit actually consumes 12kW (which it doesn't). Midea do indeed use some slightly misleading test conditions, some might say, to give their power output rating. Personally speaking I wasn't overly bothered as it is what it is and we just consulted the data sheets.



   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3058
 

Posted by: @cathoderay

This is all part of the smoke and mirrors around heat pump marketing

Posted by: @cathoderay

. As it happens, 11.52kW is pretty close to the tabulated output in the Midea Engineering Data manual at around zero degrees outside

I think the first comment is a little unfair.  The thermodynamics mean that heat pump output inevitably varies with OAT and FT.  The only way to circumvent this is artificially restrict the output in firmware, which some manufacturers do, but honestly what's the point as it simply restricts the use unnecessarily? 

The manufacturer has to give the model a name and ideally one which are least tells the designer something about the output to point her in the right direction.  What are they supposed to do in this circumstance?

So long as the name is in the right ballpark and the engineering data is published and correct, it seems to me that what they do is fair enough.

 


This post was modified 4 hours ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2241
 

Posted by: @benson

for example, a 12kW unit actually consumes 12kW (which it doesn't).

I agree, the badge rating is about output, and I think @drei's recent posts showed inputs, which is why I asked about outputs, and thereby COPs. Recall, if I am not mistaken, one of @drei's chief concerns is low COP values. But if the energy in or out are out of whack, then the COP will also be out of whack.


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
cathodeRay
(@cathoderay)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2241
 

Posted by: @jamespa

The thermodynamics mean that heat pump output inevitably varies with OAT and FT.

The thing is most people aren't physicists. If they buy an 100mph car, they expect it to go 100mph. I've suggested many times that the standard conditions used to describe heat pump outputs should be close to the conditions when real output really matters. Various flow temps at zero degrees OAT for the UK for example. My heat pump might then be badged as a far more realistic 11.5kW heat pump. The fact it can do 14kW on a day when I don't need 14kW is neither here nor there.

I agree the data is usually there for the designer who knows where to look for it, and cares to do so, but I think we know not all of them do that. But this is really about managing expectations for the buyer, not the designer.  


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote



 DREI
(@drei)
Trusted Member Contributor
Joined: 2 months ago
Posts: 41
Topic starter  

Posted by: @benson

Posted by: @drei

Not 100% accurate, but it is better than we I had, and I made the power level to a maximum of 8kW and red over 6kW, no idea if the HP would even reach that but, if it is a 12kW Heat Pump, does it mean that it can draw 12kW electricity at maximum usage?

No. 12kW is obviously the maximum heating capacity (at certain conditions, dependent on manufacturer) but the actual maximum consumption will be much lower than that. I think our 12kW max power input is around 5kW. You can get the figures for yours from the technical bulletin, data sheet etc.

 

Good to know, if you have a look at that screenshot you might be able to see, hot water hit a maximum of 4.68kW and heating it reached 5.5kW.

 



   
ReplyQuote
 DREI
(@drei)
Trusted Member Contributor
Joined: 2 months ago
Posts: 41
Topic starter  

Posted by: @cathoderay

Posted by: @drei

I am using Home Assistant's utility meters, so they add up the relevant data based on live readings, to make up the daily, weekly, monthly and yearly data. These will eventually get better, as right now it doesn't have a whole month worth of data, or a year.

The handicap is that it is still using the Heat Pump sensors, as it is connected to it via WiFi, and every now and then, Samsung wants HA to re-authenticate, which will cause a gap in the data, unless I can pick it up straight away.

In effect you are relying on the manufacturer marking their own homework. Is there any way you can validate these readings? For example, I have an independent kWh meter that supplies only the heat pump, that I use to validate my modbus collected kWh in data, and yes, there is a discrepancy, the modbus/Midea data is an under-estimate, possibly because that data is just for the compressor, excluding ancillaries like the circulating pump. The discrepancy is reasonably stable over long periods of time, and I deal with it by using a 'discrepancy correction factor' in my calculations to bring the calculated kWh figures into line with the independent kWh meter figures.

I do think you need to get to the bottom of the discrepancies in the earlier image you posted where the daily and weekly totals are significantly less than the sum of the parts. I presume these are energy inputs, can you also do the same checks on energy out data (which I believe you have access to, based on your earlier posts)? It may throw some light on why your COPs are low. GIGO and all that...

 

Part of the remedial work, whenever I get the green light and it commences, I will ask the installers to replace the fuses on the heat pump with the same ones I have on my solar, micro meters. Hopefully that will help.

I can see what you mean, somehow the Heating comes up a lot more, and when added together they are way above what the heat pump usage is.

 



   
ReplyQuote