Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature

82 Posts
10 Users
17 Reactions
24.8 K Views
(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

@majordennisbloodnok our swap out install finished around 1pm


Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   
ReplyQuote
(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

@jamespa pics showing status pages, level 1 parameters and level 2 parameters

Software version seems to be dated 2023-03-24

Status page 5
Status page 4
Level 2 Parameters page 5
Level 2 Parameters page 4
Level 2 Parameters page 3
Level 2 Parameters page 2
Level 2 Parameters page 1
Level 1 Parameters page 3
Level 1 Parameters page 2
Status page 3
Level 1 Parameters page 1
Home screen
Status page 2
Status page 1
Initial menu

 


This post was modified 11 months ago by DaveC

Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   
ReplyQuote
(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

@jamespa factory menus;

Factory menu page 8
Factory menu page 7
Factory menu page 6
Factory menu page 5
Factory menu page 3
Factory menu page 1
Factory menu page 2
Factory menu page 4

Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5756
Your energy: 114 kWh
 

Peak Energy Products most recent accounts (to June 2024) make interesting reading.  Im not an expert by any means, but their assets are almost entirely 'inventory' and their liabilities include a debt for £300K to their only director which is 'repayable on demand'.  Net assets are just £9K.  The debt 'repayable on demand' (ie at the convenience of the director) worries me given that if payment is demanded it could easily be enough to bankrupt the company.  Unfortunately there is no I&E so we have no idea what the turnover is, but 400K inventory is quite a lot of kit.

On a more practical note there are some parameters in those menus that look interesting, but its a bit difficult to be precisely sure what they do.  An 11kW heat pimp should be big enough for most properties if it really is 11kW; consumption suggests it may not be.

I will take a mpore detailed look at menus and numbers over the next couple of days and see if anything leaps out, meanwhile we now have two owners on this thread so hopefully a bit of self-help will resolve.

 


This post was modified 11 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

Thanks @jamespa and thanks @johnd (hope I haven’t hijacked your thread too much).

I’ll hopefully hear back from our installer or the manufacturer early next week and will post if there’s anything useful.

Just wondering now if we are undersized or have a faulty unit causing the issues for us, the symptoms for us do appear to point to an undersized unit.

However with 11kw + 3kw heat coming into the house it should be more than enough to keep us warm, when the initial heat loss calculation by the installer came out at 7kw and the HeatGeek website guesstimate shows 8.5kw heat loss.

Unless the 11kw unit as mentioned above isn’t actually producing 11kw of heat. Or we somehow need more than 14kw of heat input into the house.

Should we consider getting a second opinion from another company to recheck the heat loss calcs, potentially with a HeatGeek certified installer?


Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5756
Your energy: 114 kWh
 

Posted by: @davec
↑

Should we consider getting a second opinion from another company to recheck the heat loss calcs, potentially with a HeatGeek certified installer?

At this stage I would say no as gross underestimation of the loss is not the most likely cause of the problem.

More likely causes are

(a) the heat pump, though badged 11kW, doesnt actually do 11kW at the design temperature/flow temp - I reproduce the only published capacity table below but Im not sure if its for the relevant model and there doesnt seem to be anything else.

(b) the heat pump is faulty

(c) something in the system is preventing the heat getting to the building.  There is a long running thread on this forum where the householder (one of our moderators) was not getting sufficient heat - turned out eventually to be due to throttling at the PHE.

 

If you could provide a bit more info it might be possible to infer which

The following questions will give an independent handle on house loss:

  • What is the floor area, construction and insulation of your house
  • How much fuel did you previously burn annually 
  • Where are you roughly

The following question will give a handle on faults/system problems

  • How much energy did you use for your heat pump on the recent cold days?

 

image

This post was modified 11 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5756
Your energy: 114 kWh
 

@davec

Ive had a look at the screenshots.  Lots of the parameters are things you wouldn't want to touch but:

Im guessing H43 and H44 are the two FTs for the WC curve and P18 and P19 the corresponding OATs.  What P20 is, or even what the units are, is anyone's guess.  I imagine some kind of 'strength of room influence' parameter, but it could be anything!  And what is F74 - is it some overall? limit (65 would make sense for an R32 unit which I believe this is).

 

With P18 set at 0 FT will likely (but not definitely) flatline at lower OATs which isnt what you want.  However you would expect it to flatline at 52C if my guess about H43 and H44 is correct.

P15 is interesting.  Its turned on.  Is it just 'Weather compensation on' or some sort of 'auto adapt'.  At first I though the second, but maybe Im over-thinking and its just fixed temp[ operation vs weather compensated operation.  It would be interesting to know what the heat pump does if its turned off.

 

This is also interesting    

image

Im presuming you have set the target to 40C to 'disable' and room influence, but why does it think that the house is at 32C?  or is this set FT and actual FT, in which case why is the set FT 40 when the OAT is 0?

Maybe you have some insight from observation which might help reverse-engineer the UI!


This post was modified 11 months ago 5 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

@jamespa after a bit of homework today I have responses for you;

Floor area of 122 m2

Construction, late 1930s, semi detached, brick and cavity wall.

Insulation, all double glazed, all bedroom windows replaced in June. New front door installed at the same time, kitchen external door being replaced next week. Loft insulation topped up to 300mm. Living room and hallway suspended floors insulated, dining room to do.

Kitchen and sun room solid concrete floors, unknown if insulated under.

No cavity wall insulation.

We only moved into this property in July so don’t know previous gas usage. The combi boiler when we moved in was on its last legs and fell over the day after we got the keys! Managed to use it for DHW only until the ASHP was installed in September.

Located in Blackburn Lancashire.

3rd Jan - 63kWh - -6 degrees overnight - max flow temp 34 degrees (without immersion)
4th Jan - 115kWh - immersion switched on
5th Jan - 134kWh
6th Jan - 118kWh
7th Jan - 65kWh - 4 degrees external - immersion switched off - house actually at 18 degrees internal
8th Jan - 85kWh
9th Jan - 69kWh
10th Jan - 108kWh - 1 to 2 degrees external - immersion switched back on

 

H43/H44 options is just for the available FT shown on the Home Screen FT settings.

P15 is just to turn WC on or off, no difference to FT either way.

P18/P19 is the OAT for the WC to apply

P20 is an amount of WC to apply to the FT between the OAT set in P18/P19.

F74 is a top level limit for FT (I think)

 

Setting the FT on the Home Screen should work as we set the maximum FT we want at 0 degrees OAT, then the WC should work from that to reduce the FT when above 0 degrees OAT to a minimum FT at 15 degrees OAT.

But no matter the OAT the ASHP will always try to achieve the set FT. Which when set at 40 it will have a send of 42 and a return of 38. (If it can actually get there of course)

 

The table of heating capacity you found from Peak is a very interesting read, and explains some of the behaviour we have had.

For our model of PEP-M09 (as the middle option I think it’s that one, not actually labelled as that on the side of the external unit) at +2 degrees OAT it only manages to produce 7.52kw and take into account the defrost cycles and it is underspecced for our needs and that’s why it needs the 3kw backup immersion turned on to cope.

I’ll add a pic of the external unit spec sheet on the next post.


Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   
ReplyQuote

(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

@jamespa external unit details

IMG 0129

 


Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   
ReplyQuote
(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

@jamespa system design was for 40 degrees FT at -2 degrees OAT.

We’ve 11x triple radiators and 2x towel rails in bathroom and downstairs W/C


Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5756
Your energy: 114 kWh
 

Posted by: @davec
↑

after a bit of homework today I have responses for you;

Floor area of 122 m2

Construction, late 1930s, semi detached, brick and cavity wall.

Insulation, all double glazed, all bedroom windows replaced in June. New front door installed at the same time, kitchen external door being replaced next week. Loft insulation topped up to 300mm. Living room and hallway suspended floors insulated, dining room to do.

Kitchen and sun room solid concrete floors, unknown if insulated under.

No cavity wall insulation.

Interesting.  Judging by my house which is different is several ways (some better, some worse) I would have guessed ~7kW as the actual loss, however your consumption is 1.5-2x mine.  That may be because of a lesser COP, or may be because of more loss of course.  At - OATs you will of course need more than this and your unit may not be capable accounting for the deficit in recent days.  

Posted by: @davec
↑

P20 is an amount of WC to apply to the FT between the OAT set in P18/P19.

Thats an interesting (and very plausible) interpretation, but what is the starting FT in this case?

Posted by: @davec
↑

Setting the FT on the Home Screen should work as we set the maximum FT we want at 0 degrees OAT, then the WC should work from that to reduce the FT when above 0 degrees OAT to a minimum FT at 15 degrees OAT.

But no matter the OAT the ASHP will always try to achieve the set FT. Which when set at 40 it will have a send of 42 and a return of 38. (If it can actually get there of course)

Sorry I dont follow this, are you saying that it doesnt vary the FT?

 

Posted by: @davec
↑

For our model of PEP-M09 (as the middle option I think it’s that one, not actually labelled as that on the side of the external unit) at +2 degrees OAT it only manages to produce 7.52kw and take into account the defrost cycles and it is underspecced for our needs and that’s why it needs the 3kw backup immersion turned on to cope.

I think thats quite possible based on what you have said.  You should be able to tell over the next days as its getting warmer.  As it does so the heat pump should reach the expected FT.

I am a little concerned by the fact you seem to be consuming so much more than me.  My COP over past days has been 3-3.5, which is unusually low (but then its been unusually cold).  Maybe you are operating right at the extreme of its operational curve and so things will get better.  If they dont then there may be some further questions to ask.

Sorry thats probably not been very helpful/tends to confirm what you already suspect.  Suggest to see what the next week brings!

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@davec)
Eminent Member Member
Joined: 11 months ago
Posts: 33
Your energy: 0 kWh
 

@jamespa the compressor does run at max operating frequency in these lower temperatures (2 degrees and below) and doesn’t seem to have any opportunity to reduce to try and achieve a better running efficiency. I would really be surprised if our current COP is even at 2.

The starting FT for the WC is the one set on the Home Screen, as far as we know.

But unless we manually reduce this is line with a higher OAT, the ASHP will just run at max operating frequency to try and achieve this FT and would then hit the thermostat temperature limit and then get switched off. Only to then do the same once it drops below the internal temperature set point.

Or it did when the OAT was warmer than it is currently. In essence running like a gas boiler. When raised with the installer they didn’t see this as an issue, it wasn’t until later when we realised that the WC wasn’t being applied to the set FT that was causing the issue and we started to manually alter the FT to allow the ASHP to back off the compressor frequency and improve the efficiency.

 

The good news is that it has warmed up throughout today, up to a modest 8 degrees OAT at the moment, and we have been able to switch off the immersion heater and reduce the FT required to achieve our desired internal temperature of 18 degrees. And we have actually achieved this temperature!

This has reduced the electricity consumption down to a mere 74kWh so far for the day.


Grant 12kW r290 ASHP - Solis 8kW Solar Inverter with 7.8kW panels and Fogstar 2x 16kWh home batteries


   