Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Who has a V2G EV installation
Posted by: @agentgeorgeWhat is foxing me with doing this is getting the type B rcd for CU I have, so I cant move the ASHP from its Cinch CU which has the type B in it :-/
Would that be a Chint RCD perhaps?
Have a look at this topic on high current trips, where I mention a number of potential manufacturers and suppliers for the trip being sought by BatPred.
For the benefit of others wanting to follow this discussion,
this chart shows the features found in the four types of earth leakage trip:
The majority of EV chargers are installed using a Type-A trip.
But the OVO Trial of V2G chargers five years ago showed that there was a significant DC component in the fault leakage current.
So they installed Type-B trips from then on.
Type-B RCD trips used to be very rare, and cost more than £200 each.
For a V2G charger, it would also need to be bi-directional of course.
It was usually the case that the installer needed a separate RCD and MCB.
However, we are now starting to see manufacturers responding to the market, and designing an RCBO Type-B.
This one from Proteus is also C-curve.
That means the trip-time is slower than the usual B-curve we find in domestic installations.
A C-curve is less prone to spurious tripping from switch-on surge currents
Save energy... recycle electrons!
Posted by: @scalextrixId also add to this thread that V2G (Vehicle to Grid) is not necessarily the same as V2H (Vehicle to Home). Allowing an energy provider to offtake your car charge to support the grid, wont necessarily allow you to use the car battery to run your ASHP or other home appliances.
I am wondering if in any V2X, would the car battery ever send DC to the EV plug or always AC?
And what happens when a V2X car is plugged into a recent EV charger not designed for it, does it just not work or can it cause any issues if the car attempts to export?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@majordennisbloodnok. I have been considering a Volkswagen ID 3/4/5, or Skoda Elroque, as the back up to my Tesla Powerwall 3 which ran out of juice during the recent cold snap.
As I understand it, all these cars are ready for V2H. Is that correct and are you using V2H?
I know that a special bi-directional charger is needed, but also that the Zaptec Go2 is available. None of this makes any sense financially for me, but I just like the idea of getting all my electricity at 7p pKwh. I wonder how long it will be before the 7p is increased substantially.
@broadsman, yes-ish and no.
We bought our ID3 secondhand because it ticked too many boxes at the right time. We were interested in the V2X concept and I looked seriously at it when I saw VW were releasing an over-the-air upgrade to make all models after a certain date V2X-compatible. However, for the ID3 that was only on the 77kWh models and ours is a 58kWh, so no we're not using it. However, I have little doubt that our next purchase will be another VW stable car and that'll need to have a longer range so we can visit family, so V2X is already in our future upgrade plans.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 1,014 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 6 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 10 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 11 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 11 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 14 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 20 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 20 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago