Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Who has a V2G EV installation
Posted by: @agentgeorgeWhat is foxing me with doing this is getting the type B rcd for CU I have, so I cant move the ASHP from its Cinch CU which has the type B in it :-/
Would that be a Chint RCD perhaps?
Have a look at this topic on high current trips, where I mention a number of potential manufacturers and suppliers for the trip being sought by BatPred.
For the benefit of others wanting to follow this discussion,
this chart shows the features found in the four types of earth leakage trip:
The majority of EV chargers are installed using a Type-A trip.
But the OVO Trial of V2G chargers five years ago showed that there was a significant DC component in the fault leakage current.
So they installed Type-B trips from then on.
Type-B RCD trips used to be very rare, and cost more than £200 each.
For a V2G charger, it would also need to be bi-directional of course.
It was usually the case that the installer needed a separate RCD and MCB.
However, we are now starting to see manufacturers responding to the market, and designing an RCBO Type-B.
This one from Proteus is also C-curve.
That means the trip-time is slower than the usual B-curve we find in domestic installations.
A C-curve is less prone to spurious tripping from switch-on surge currents
Save energy... recycle electrons!
Posted by: @scalextrixId also add to this thread that V2G (Vehicle to Grid) is not necessarily the same as V2H (Vehicle to Home). Allowing an energy provider to offtake your car charge to support the grid, wont necessarily allow you to use the car battery to run your ASHP or other home appliances.
I am wondering if in any V2X, would the car battery ever send DC to the EV plug or always AC?
And what happens when a V2X car is plugged into a recent EV charger not designed for it, does it just not work or can it cause any issues if the car attempts to export?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
@majordennisbloodnok. I have been considering a Volkswagen ID 3/4/5, or Skoda Elroque, as the back up to my Tesla Powerwall 3 which ran out of juice during the recent cold snap.
As I understand it, all these cars are ready for V2H. Is that correct and are you using V2H?
I know that a special bi-directional charger is needed, but also that the Zaptec Go2 is available. None of this makes any sense financially for me, but I just like the idea of getting all my electricity at 7p pKwh. I wonder how long it will be before the 7p is increased substantially.
@broadsman, yes-ish and no.
We bought our ID3 secondhand because it ticked too many boxes at the right time. We were interested in the V2X concept and I looked seriously at it when I saw VW were releasing an over-the-air upgrade to make all models after a certain date V2X-compatible. However, for the ID3 that was only on the 77kWh models and ours is a 58kWh, so no we're not using it. However, I have little doubt that our next purchase will be another VW stable car and that'll need to have a longer range so we can visit family, so V2X is already in our future upgrade plans.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,327 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 1 hour ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 15 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago