Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Who has a V2G EV installation
Posted by: @agentgeorgeWhat is foxing me with doing this is getting the type B rcd for CU I have, so I cant move the ASHP from its Cinch CU which has the type B in it :-/
Would that be a Chint RCD perhaps?
Have a look at this topic on high current trips, where I mention a number of potential manufacturers and suppliers for the trip being sought by BatPred.
For the benefit of others wanting to follow this discussion,
this chart shows the features found in the four types of earth leakage trip:
The majority of EV chargers are installed using a Type-A trip.
But the OVO Trial of V2G chargers five years ago showed that there was a significant DC component in the fault leakage current.
So they installed Type-B trips from then on.
Type-B RCD trips used to be very rare, and cost more than £200 each.
For a V2G charger, it would also need to be bi-directional of course.
It was usually the case that the installer needed a separate RCD and MCB.
However, we are now starting to see manufacturers responding to the market, and designing an RCBO Type-B.
This one from Proteus is also C-curve.
That means the trip-time is slower than the usual B-curve we find in domestic installations.
A C-curve is less prone to spurious tripping from switch-on surge currents
Save energy... recycle electrons!
Posted by: @scalextrixId also add to this thread that V2G (Vehicle to Grid) is not necessarily the same as V2H (Vehicle to Home). Allowing an energy provider to offtake your car charge to support the grid, wont necessarily allow you to use the car battery to run your ASHP or other home appliances.
I am wondering if in any V2X, would the car battery ever send DC to the EV plug or always AC?
And what happens when a V2X car is plugged into a recent EV charger not designed for it, does it just not work or can it cause any issues if the car attempts to export?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@majordennisbloodnok. I have been considering a Volkswagen ID 3/4/5, or Skoda Elroque, as the back up to my Tesla Powerwall 3 which ran out of juice during the recent cold snap.
As I understand it, all these cars are ready for V2H. Is that correct and are you using V2H?
I know that a special bi-directional charger is needed, but also that the Zaptec Go2 is available. None of this makes any sense financially for me, but I just like the idea of getting all my electricity at 7p pKwh. I wonder how long it will be before the 7p is increased substantially.
@broadsman, yes-ish and no.
We bought our ID3 secondhand because it ticked too many boxes at the right time. We were interested in the V2X concept and I looked seriously at it when I saw VW were releasing an over-the-air upgrade to make all models after a certain date V2X-compatible. However, for the ID3 that was only on the 77kWh models and ours is a 58kWh, so no we're not using it. However, I have little doubt that our next purchase will be another VW stable car and that'll need to have a longer range so we can visit family, so V2X is already in our future upgrade plans.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 927 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Heat pump Surge protection
@transparent potentially ignorant question alert, but d...
By Mars , 1 hour ago
-
Here's an excellent explanation. If you have non b...
By bobflux , 2 hours ago
-
RE: Aerotherm 12+12kw cascade huge power utilisation
@editor This is really crazy. I can sort of understan...
By JamesPa , 6 hours ago
-
Or just add any further discussion to the other thread....
By cathodeRay , 7 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
@hughmark, great to hear. Fingers crossed that it’s sor...
By Mars , 18 hours ago
-
RE: Daikin high temperature heat pump
I’ll check in with Daikin to see if they can help answe...
By Mars , 18 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
@johnnyb HI,I have an integrated unit with all componen...
By antonical , 20 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Ironical isn’t it? The last few days, the ‘Ag...
By Toodles , 21 hours ago
-
RE: Setback savings - fact or fiction?
I answered that days back, I even provided a summary of...
By RobS , 22 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
I must say that this install is sounding more and more ...
By Mars , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 2 days ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 3 days ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 3 days ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 3 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 3 days ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 3 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 3 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 4 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 4 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 4 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 4 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 4 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 4 days ago