And we are now back down to 7.2lpm but heating is still going
If removing that strainer made a difference, then it's possible that something has become dislodged within the pipework.
We can't tell if that 'something' was an object within the body of the strainer,
or possibly elsewhere, and that the sudden loss of flow has moved it.
Equally, you will definitely have introduced fresh air by opening the strainer,
and that will require purging from the various release-valves over an hour or two.
Save energy... recycle electrons!
So, looks like it might be an incorrect sizing of primary pump. The installer (who was the subcontractor to who I used) came out and advise he was never given the heating design by the company who contracted him despite asking multiple times. When installing he pointed out that there was no primary pump ordered so the main contractor went and purchased one (the Evosta 3 60/130). What the installer and I think has happened is the main contractor has seen the price difference between the 60/130 and the 80/130 and went for the cheaper 60/130 (without actually understanding what those values mean).
I am in the process of requesting the full heating design (they did come out and survey everything) which brought them to the conclusion of not needing any new radiators and an 8kW system. Will let you all know how I get on.
P.S We also notice that even when the heating wasnt on, the secondary Grundfos pump was still running which seems to make the radiators cool down super quick if it's still pumping the water around and the ASHP isnt heating it. When we set DHW to on, the secondary pump goes off. Is this normal or has some mis-wiring occured?
Thanks
@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
To add, the primary pump also can run for a while before the system fires up to confirm flow.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobba@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
So the primary pump ( EVOSTA 3) does this, only comes on when required. The secondary pump which is at the bottom right of my setup picture which is attached the the flow towards the radiators is on all the time.
Going to trace where it goes on the MIM
@netdonkey OK, so this Grundfoss pump should only turn on an off when required in heating mode as your system runs through a buffer, there will be some form of stat that controls this, its should ideally through the ASHP controls if you are using their smart controls linked to a main stat, or through the ASHP control when engaging heating mode which can also be via a 3rd party stat or controls. So it depends how they have set up your system.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Save energy... recycle electrons!
@netdonkey Primary pump should run as follows:
Heating demand on
DHW demand on
Defrost demand on
Secondary pump should run as follows:
Heating demand on
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Do all ASHPs have that Primary Pump inside the building?
Or is it sometimes within the external heat-pump / heat-exchanger unit itself?
Save energy... recycle electrons!
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Sudden drop in COP
1 month ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
10 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
2 years ago
-
Issue with Samsung A2W Heat Pump - Water Outlet Temperature
3 years ago
- 26 Forums
- 2,152 Topics
- 47.2 K Posts
- 14 Online
- 5,671 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Boiling Mad: Exposing Radiatorgate
Actually they do. My case is a prime example. Catalo...
By DREI , 37 minutes ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
Blunt answer? The 20-year-old gas system was f...
By DREI , 54 minutes ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
You can even go as low as 40c flow temp, if you want a ...
By DREI , 58 minutes ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 3 hours ago
-
RE: Midea ASHP – how to set weather compensation
I'm guessing these are the mcs defaults which are likel...
By JamesPa , 3 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 4 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 6 hours ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 7 hours ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 13 hours ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 13 hours ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 1 day ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 1 day ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 1 day ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 1 day ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 2 days ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 days ago