Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsun Gen 6 disinfection cycle fault
For a long while our Samsung gen 6 hasn’t been performing its disinfection cycle. I’ve tried to troubleshoot and gave up- thinking that it’s not essential anyway. However, have had heating engineers around recently upgrading our installation and they couldn’t solve the problem either. I think it must be an electronics fault but in case I’m missing anything. Do any other users or installers here have any insights or troubleshooting advice for us?
Disinfection cycle is set to use and we’ve experimented with short and long durations and left the max time long to allow it plenty of time to achieve the temp.
Observing the system’s behaviour when the disinfection cycle should be happening:
The status menu highlights the disinfection cycle but not the booster heater nor water tank. Comp and water pump are also highlighted.
LWT on the user display remains steady according to WL curve. It never increases. Valve stays in direction allowing flow to the central heating and doesn’t switch to water tank. Water tank remains at its usual set point of 48 degrees and never changes.
Looking at the flows and DT in the indoor and connection menus in the device menu these are the same as when normally running the CH. Flows of 24 lpm approx.
At no point does the immersion come on.
Booster heater is set to use in the FSVs with a delay time of 20 mins.
i have hunted through the service menu in case there’s another setting somewhere that needs switching on but don’t think I’m missing one.
Have tested immersion in self test mode and it works- current flows and tank gets hotter.
It seems like the ASHP and booster make no effort to raise the temp although the operation status menu would seem to say it’s doing the disinfection cycle. Then it throws the error 911 whenever it times out!
Anyone any words of wisdom?
Time to contact Samsung? And if so- anyone know the best way to do this? I get stuck in menus for phones and TVs and tumble driers!
tech.aircon@samsung.com may be able to help. My immersion heater is connected only to the solar iboost, so cannot help you much. Prior to the iboost being fitted, my memory of the disinfection cycle was that it only used the immersion heater and the outside unit was not involved.
@mike-h Thank you. I'm interested in your experience with the iboost. It's something we've considered. How do you use it? Does it work well for you? Is it controlled via the Samsung controller or separately?
@bauchie I like the iboost. It’s pretty simple and it does our hot water for 7-8 months of the year. It operates independently of the heat pump and is directly connected to the immersion. The original connection between the Samsung wiring and the immersion was removed. It uses excess solar produced electricity, but you can also use it to run straight from the grid manually or according to a schedule.
We are on the feed-in tariff so the solar boost saves us money. Those who are getting an export tariff of 15p/kWh prefer to use the heat pump to heat DHW.
@mike-h ah yes. That makes sense. If you get the FIT then I guess you might as well maximise your own usage! For us - we are on the newer export tariff so I guess exporting and suing the ASHP to heat our water all year round is probably cheaper as well as more efficient...
@mike-h Ive just happened upon this thread mike. You do know that you can still export to the grid at 15p per unit and keep your FIT generation tariff. You just need to apply to octopus to split them. Generation goes to FIT tariff and export goes to export tariff instead of the paltry FIT export rate. Ive done it myself and thats why my Eddi is sitting unused 🙂
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks very much for pointing this out as I was unaware that you could do this. The need for a hot water cylinder is the one thing I feel is a disadvantage of owning a heat pump. Mine is supposed to lose 0.3C per hour, but seems to lose twice that and a lot more when the Samsung does its 5 minute run every 24 hours to keep things from seizing up during the non heating season. I also don't get a particularly good COP, 1.5-2.0, when heating DHW. Leaving the iBoost to do its thing during the summer has kept things very simple, but I will certainly look into what you have suggested. Thanks again.
@mike-h No problem Mike. Actually I dont use my heat pump to heat my DHW. Im on Intelligent Octopus Go and have a Mixergy cylinder so just use the immersion at night for 7p a unit. That gives me a financial COP of about 3.5 even discounting that there might be some efficiency gains through the stratification of the Mixergy tank.
The 1.5-2 COP doesnt sound very good, there is a lot of discussion about how to get good DHW COPs on heatgeek. Big coils help but I think they are emphasing slow heating cycles too. might be worth a look.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 931 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 11 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 15 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 19 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 19 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago