Posted by: @ringi

Does the quality of sine wave from the generator then become an none issue?

Interesting question.

The usual assumption is that generation sources based on mechanical rotation will naturally provide genuine sine-wave output.

Do you have experience suggesting that this is not the case?


Save energy... recycle electrons!


   
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 739
 

Posted by: @ringi

Posted by: @abernyte

then the plumbing was left with manual change over valves to isolate the heat pump and run the old LPG boiler to provide heating,

Does that setup heat the water inside of the heatpump?

What abernyte proposes here is just using a generator to run a backup fossil fuel boiler.

A heatpump will always need more electricity..

Your backup solution could use a generator to power a heatpump that then trebles the generator output and keeps your home warm. But many heatpumps use a lot more power on startup than after they get going. Adding an inverter that is powerful enough with even a small battery may make the difference. 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
(@pipcart)
Eminent Member Member
Joined: 3 years ago
Posts: 23
Topic starter  

@transparent Thanks. Good point about startup surge current. I guess an appropriate battery could absorb that, so that the generator would only need to be sized for normal running. Would need to keep in mind that it could be running in cold weather. I was also thinking of turning off DHW, to limit demand.

Any thoughts about how to determine startup current?



   
ReplyQuote



Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 739
 

Posted by: @pipcart

@transparent Thanks. Good point about startup surge current. I guess an appropriate battery could absorb that, so that the generator would only need to be sized for normal running. Would need to keep in mind that it could be running in cold weather. I was also thinking of turning off DHW, to limit demand.

Any thoughts about how to determine startup current?

If the heatpump manufacturers app does not show it, you could use a ct clamp or a smart switch. Most provide that information via their app.

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
(@pipcart)
Eminent Member Member
Joined: 3 years ago
Posts: 23
Topic starter  

Thanks. Well need a professional in I think. I struggle with Ohms law!



   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
Joined: 4 years ago
Posts: 3075
 

Us Moderators have had a (private) discussion in 2025 about peak current demand from heat-pumps.

It certainly used to be the case that there was high demand for the first minute or so after start-up whilst the motors for fans and compressors reached operational levels.

However, that is no longer the case.

Heat pumps now use soft-start motors and there is no noticeable surge as the HP starts up.
That comment applies both to electrical surge currents, and also the possibility of lower efficiency as the HP water-circuit reaches the required flow-level.

Those issues are now substantially resolved.

If you're reading topics here on the forum which refer to large current draw, particularly when a HP is cycling on/off,
then check the date when that discussion occurred...
... and whether the post refers to a HP system which was of an older design.

 


Save energy... recycle electrons!


   
ReplyQuote



Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 739
 

Posted by: @transparent

However, that is no longer the case.

Heat pumps now use soft-start motors and there is no noticeable surge as the HP starts up.

That´s useful to know. 

Given that the peak power has to be determined in order to size the generator or inverter (and the number of queries I read here, where the users cannot find it like from the manufacturers app), a CT clamp or a smart circuit relay still seems to be a cheap and effective way to assess it.

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
Joined: 4 years ago
Posts: 3075
 

Fortuitously, I've just posted here on another topic about buying a (cheap) clamp multimeter.

image

Save energy... recycle electrons!


   