Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Our Daikin ASHP
Hi Derek, thanks so much again for sharing your expertise.
You are quite correct I was confusing the terminology. I have put equilibrium temp back to the default of -4°C.
That makes complete sense, so we should expect to the ASHP running more given the higher pricing for gas and electricity. I will leave the curve at 45°C at -10°C and 25°C @ 18°C and with the lot max modulation now set at 10°C and monitor the cycling and overall COP.
Thanks,
Adam
Hi @adaml
When time allows, monitor how long the heat pump runs and then how long it is stopped before restarting. Also record the water flow and return temperatures, which may highlight any possible problems with your system. If your heat pump is running for short time periods then stopping for short time periods then it may be necessary to adjust some of the operating parameters.
Hi Derek,
I've been watching it run tonight and it is sometimes running for about 20 minutes and then stops and other times it is starting, running for only a couple of minutes and then stops. The required flow temp for tonight is showing as 31°C. The required was showing as 26°C and the lwt modulation seems to have increased this. The house is sitting at 21.7°C at the moment.
I think one potential problem could be that the Daikin thermostat/controller is situated in our downstairs hallway, with the kitchen door relatively close to it. This means that when we're cooking the temperature raises in the hall and trips the thermostat off, despite other parts of the house being cooler. I wonder if increasing the thermostat temp in the hall to say 22°C could be worth a shot?
Jan shows the compressor has been running for 4 hours with 42 starts at the moment. Other snapshots were 27 at 2 hours and 36 at 3 hours.
Stats from the controller tonight, couple of snapshots;
Outdoor temp. 9.0°C
Leaving water 26.8°C
Leaving water (PHE) 26.8°C
Inlet water temp. 25.3°C
Refrigerant temp. 26.0C
Flow rate 12.9l/min
Outdoor temp. 9.0°C
Leaving water 30.4°C
Leaving water (PHE) 30.0°C
Inlet water temp. 30.2°C
Refrigerant temp. 29.7C
Flow rate 12.6l/min
Hi @adaml
First of all let's clarify what is meant by running, do you mean that the compressor is actually running, or that it is just the water pump that is running?
The water pump is often started before the compressor is started, and continuous to run for a short period after the compressor has stopped. The water pump is also run for short periods of time to check the water temperature, so that the controller knows when to start the compressor to provide more heat energy.
Looking at your snapshots, I would say that the upper one has the water pump running but the compressor is stopped, and in the lower one both compressor and water pump appear to be running.
I think that you may find that the data relating to running and starts should be interpreted in the following manner.
'Jan shows the compressor has been running for 4 hours with 42 starts at the moment'.
I think that this actually means that since the start of January, the compressor has run for a total of 4 hours, and since the start of January the compressor has started 42 times. So it would appear that what has actually happened is that the compressor has started 42 times in approximately 42 hours, so has started on average once per hour, and has run for an average 5.77 minutes each time.
- 27 Forums
- 2,792 Topics
- 66 K Posts
- 2,170 Online
- 7,197 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
I think Heat Geek have done an amazing job on their bra...
By Tomtheheatingengineer , 8 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
I have just had 3 heat loss surveys, one by heat geek o...
By David , 8 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
I think that's the key question. After all inverter uni...
By Prunus , 10 hours ago
-
RE: battery storage without solar
As of October 1st they need specific qualifications to ...
By EtchedPixels , 11 hours ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
A unit which uses water to transfer the heat/chill from...
By Temperature_Gradient , 11 hours ago
-
RE: Renewables & Heat Pumps in the News
With regards to the BUS grant raid, I gave it more thou...
By ASHP-BOBBA , 11 hours ago
-
RE: Why are ASHP installs so expensive?
The whole system seems to work on the basis of...
By ian33a , 12 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Good plan. If you can get half hourly meter readings a...
By JamesPa , 17 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@editor Most certainly. The heat pump was an ideal s...
By Abernyte , 17 hours ago
-
Although regulations may well vary from country to coun...
By Majordennisbloodnok , 17 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yep I caught our slow leak from a £100 bill rise 8)
By EtchedPixels , 17 hours ago
-
RE: Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
@jamespa in some cases, failing the Turing test might b...
By GrahamF , 21 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@energystoragetech The heat capacity of some...
By JamesPa , 22 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
Sorry you are correct, I was remembering figures from t...
By JamesPa , 1 day ago