Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Our Daikin ASHP
Hi Derek, thanks so much again for sharing your expertise.
You are quite correct I was confusing the terminology. I have put equilibrium temp back to the default of -4°C.
That makes complete sense, so we should expect to the ASHP running more given the higher pricing for gas and electricity. I will leave the curve at 45°C at -10°C and 25°C @ 18°C and with the lot max modulation now set at 10°C and monitor the cycling and overall COP.
Thanks,
Adam
Hi @adaml
When time allows, monitor how long the heat pump runs and then how long it is stopped before restarting. Also record the water flow and return temperatures, which may highlight any possible problems with your system. If your heat pump is running for short time periods then stopping for short time periods then it may be necessary to adjust some of the operating parameters.
Hi Derek,
I've been watching it run tonight and it is sometimes running for about 20 minutes and then stops and other times it is starting, running for only a couple of minutes and then stops. The required flow temp for tonight is showing as 31°C. The required was showing as 26°C and the lwt modulation seems to have increased this. The house is sitting at 21.7°C at the moment.
I think one potential problem could be that the Daikin thermostat/controller is situated in our downstairs hallway, with the kitchen door relatively close to it. This means that when we're cooking the temperature raises in the hall and trips the thermostat off, despite other parts of the house being cooler. I wonder if increasing the thermostat temp in the hall to say 22°C could be worth a shot?
Jan shows the compressor has been running for 4 hours with 42 starts at the moment. Other snapshots were 27 at 2 hours and 36 at 3 hours.
Stats from the controller tonight, couple of snapshots;
Outdoor temp. 9.0°C
Leaving water 26.8°C
Leaving water (PHE) 26.8°C
Inlet water temp. 25.3°C
Refrigerant temp. 26.0C
Flow rate 12.9l/min
Outdoor temp. 9.0°C
Leaving water 30.4°C
Leaving water (PHE) 30.0°C
Inlet water temp. 30.2°C
Refrigerant temp. 29.7C
Flow rate 12.6l/min
Hi @adaml
First of all let's clarify what is meant by running, do you mean that the compressor is actually running, or that it is just the water pump that is running?
The water pump is often started before the compressor is started, and continuous to run for a short period after the compressor has stopped. The water pump is also run for short periods of time to check the water temperature, so that the controller knows when to start the compressor to provide more heat energy.
Looking at your snapshots, I would say that the upper one has the water pump running but the compressor is stopped, and in the lower one both compressor and water pump appear to be running.
I think that you may find that the data relating to running and starts should be interpreted in the following manner.
'Jan shows the compressor has been running for 4 hours with 42 starts at the moment'.
I think that this actually means that since the start of January, the compressor has run for a total of 4 hours, and since the start of January the compressor has started 42 times. So it would appear that what has actually happened is that the compressor has started 42 times in approximately 42 hours, so has started on average once per hour, and has run for an average 5.77 minutes each time.
- 26 Forums
- 2,645 Topics
- 61.8 K Posts
- 381 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
No, I agree entirely. There shouldn't be a need for an ...
By Majordennisbloodnok , 58 minutes ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 2 hours ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 2 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 2 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 15 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 23 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 4 days ago