We moved into our house in December. It is roughly 5 years old, A rated wit a Mechanical Heat Recovery System and an 11Kw Ecodan with UFH upstairs and down.
The control system, is really odd. We have Uponor manifolds for the UFH. They are fitted with Uponor 24V actuators and T148 thermostats in the various rooms. Some odd things with the Uponor system is that it seems like a bus wired system for the thermostats so they are all wired together and back to the control unit. They have a night time set back which was at 4 degrees, we changed this to 2 degrees because the house was taking too long to get back to comfort levels in the morning and it seemed to be unnecessary cycling. Another weirdo with the Uponor is that the manifolds have a timer control, this manages things like the set back, but there is no battery backup so both timers need to be reset after a power cut. If I could I would junk the Uponor system and replace it with Heatmiser, but the thermostats are bus wired.
I have been trying to optimise the system in various ways as the COP seems to be about 2.2. The system design seems to be fairly poor as well. There are towel rails in the upstairs bathroom and these are T'd off the heating flow and return with no control valves and therefore rely on TRV's. Even odder is that when the UFH manifolds are off, the towel rails still run suggesting the heating is permanently on and not wired to the UFH manifold controllers. I suppose this could be so that the heating runs all the time and the room stats shut off the various rooms when they reach the thermostats settings. Then I guess we rely on flow vs return temps? There also seems to be two zones, but no idea if this is upstairs or down or just a config error.
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Any advice welcomed!
Thanks
Bob
Posted by: @spudthe COP seems to be about 2.2.
Bob
Where are you getting the numbers from? I have about the same, based on the "Energy Delivered" reported by the FTC6 controller.
However the total energy consumed in 12 months by the heat pump according to the separate meter is about 3850kWh. The 'contract of performance' states 2623kWh input for space heating and 1586kWh input for hot water, total 4209 kWh so we are coming in under that. This suggests that the FTC6 isn't a reliable source for the energy delivered. (the FTC6 reports about 10% more kWh consumed than the actual heat pump meter).
We probably save a bit on hot water as there are only 2 of us in a 5 bedroom house, but most of the house is heated to c. 21C. The running cost of the MVHR and the pumps do not go through the heat pump meter so I suppose total heating cost should include that.
Quite early on, I tackled the supplier about the poor COP. TBH I got a bit of a brush off - they said the FTC6 implied COP is just an "estimate" and should be ignored. Apparently I would need a heat meter to get a proper measurement of COP (I do not have one fitted).
In a nutshell, the COP as measured by the FTC6 is pathetically low, but the actual electricity consumption is more or less what it should be.
Is this the case for you?
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Incidentally, it seems odd to have the towel rails tee'd off the heating flow. Our flow temp (UFH) is never higher than 40C and often not even at blood temperature. It would make more sense to be on the DHW flow (except insofar as it isn't heating water most of the time).
Maybe it's taking heat from the hot water tank? That would seem a bit silly especially if it were 24/7.
I put electric towel rails in our bathrooms. I have some controllers fitted whereby a push of a button puts them on for 2 hours.
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Posted by: @spudWe moved into our house in December. It is roughly 5 years old, A rated wit a Mechanical Heat Recovery System and an 11Kw Ecodan with UFH upstairs and down.
The control system, is really odd. We have Uponor manifolds for the UFH. They are fitted with Uponor 24V actuators and T148 thermostats in the various rooms. Some odd things with the Uponor system is that it seems like a bus wired system for the thermostats so they are all wired together and back to the control unit. They have a night time set back which was at 4 degrees, we changed this to 2 degrees because the house was taking too long to get back to comfort levels in the morning and it seemed to be unnecessary cycling. Another weirdo with the Uponor is that the manifolds have a timer control, this manages things like the set back, but there is no battery backup so both timers need to be reset after a power cut. If I could I would junk the Uponor system and replace it with Heatmiser, but the thermostats are bus wired.
I have been trying to optimise the system in various ways as the COP seems to be about 2.2. The system design seems to be fairly poor as well. There are towel rails in the upstairs bathroom and these are T'd off the heating flow and return with no control valves and therefore rely on TRV's. Even odder is that when the UFH manifolds are off, the towel rails still run suggesting the heating is permanently on and not wired to the UFH manifold controllers. I suppose this could be so that the heating runs all the time and the room stats shut off the various rooms when they reach the thermostats settings. Then I guess we rely on flow vs return temps? There also seems to be two zones, but no idea if this is upstairs or down or just a config error.
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Any advice welcomed!
Thanks
Bob
Please provide more details of your system.
How are operating the system, fixed LWT or weather compensation mode?
What value is the LWT and RWT?
Posted by: @spud
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Bob
I'm guessing that is the temp at the location of the FTC controller. Mine is in an "airing cupboard" with the pre-plumbed tank etc and when the door is shut the temperature in there can reach mid-30s, which Melcloud gives as Room Temp. I'm going to insulate all the warm pipes I can find in there.
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Thanks, yes I am using the data from the FTC. I'll see what I can get monitoring the actual power consumed.
Hadn't realised that the Ecodan measured the temp in the airing cupboard, but yes that is where it is located and it does get warm in there. Again, when I get to it I will check if that is where the temp is being measured.
- 27 Forums
- 2,433 Topics
- 55.3 K Posts
- 398 Online
- 6,118 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help needed with Grant Aerona 3 issues
Just to update the thread, I now have a new heat pump!!...
By fleurcules , 29 minutes ago
-
RE: Is it normal to use power from the grid when running off the battery?
Well, the Huawei CT clamps I have are 100amp and 230V. ...
By Batpred , 3 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor condensate drain worries me, Ive wondered why t...
By Papahuhu , 4 hours ago
-
RE: A Smarter Smart Controller from Homely?
@johnnyb I think so. It’s a UPM4xL that takes its sp...
By Papahuhu , 5 hours ago
-
RE: A Single Voice for Heat Pumps, But Will It Finally Raise Industry Standards?
Great question - I don't know for sure, but I would ass...
By Mars , 6 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Actually, I came across the list of batteries that this...
By Batpred , 6 hours ago
-
RE: Say hello and introduce yourself
Hi all, my name is Julian, and I’m new to the forum. We...
By JLeyland , 7 hours ago
-
RE: Heat pump not reaching flow temperature
@davec that's good news! Thanks for sharing Dave.
By johnd , 8 hours ago
-
RE: Renewables & Heat Pumps in the News
@toodles this industry lacks accountability. That's one...
By Mars , 10 hours ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@prunusk I guess I was being generic with PV The pipe...
By HeyMikey , 15 hours ago
-
RE: Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
@jamespa previously it was so noisy, it was like hav...
By Papahuhu , 15 hours ago
-
RE: Running from backup generaor in powercut?
Fortuitously, I've just posted here on another topic ab...
By Transparent , 16 hours ago
-
The Myth of the MCS Performance Guarantee
As the editor of Renewable Heating Hub, I dedicate a si...
By Mars , 16 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Yes, I agree that the dearth of public knowledge of ene...
By Transparent , 17 hours ago
-
RE: UK Heat Pump Problems: A Complaint Process That's Irreparably Broken
Why do they not get replaced by NICEIC, assuming they w...
By Batpred , 1 day ago
-
RE: Volumiser required on Grant R290?
Bold move, and welcome to the forums @Patrick. I’ve h...
By Mars , 1 day ago
-
RE: R290 Heat Pump and Foundation Air Bricks
@l8again I agree fully, so what we would do is offer yo...
By ASHP-BOBBA , 1 day ago
-
RE: Setback savings - fact or fiction?
I agree, I have even been known to call some of the 'op...
By cathodeRay , 1 day ago