Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New and confused ASHP owner
We moved into our house in December. It is roughly 5 years old, A rated wit a Mechanical Heat Recovery System and an 11Kw Ecodan with UFH upstairs and down.
The control system, is really odd. We have Uponor manifolds for the UFH. They are fitted with Uponor 24V actuators and T148 thermostats in the various rooms. Some odd things with the Uponor system is that it seems like a bus wired system for the thermostats so they are all wired together and back to the control unit. They have a night time set back which was at 4 degrees, we changed this to 2 degrees because the house was taking too long to get back to comfort levels in the morning and it seemed to be unnecessary cycling. Another weirdo with the Uponor is that the manifolds have a timer control, this manages things like the set back, but there is no battery backup so both timers need to be reset after a power cut. If I could I would junk the Uponor system and replace it with Heatmiser, but the thermostats are bus wired.
I have been trying to optimise the system in various ways as the COP seems to be about 2.2. The system design seems to be fairly poor as well. There are towel rails in the upstairs bathroom and these are T'd off the heating flow and return with no control valves and therefore rely on TRV's. Even odder is that when the UFH manifolds are off, the towel rails still run suggesting the heating is permanently on and not wired to the UFH manifold controllers. I suppose this could be so that the heating runs all the time and the room stats shut off the various rooms when they reach the thermostats settings. Then I guess we rely on flow vs return temps? There also seems to be two zones, but no idea if this is upstairs or down or just a config error.
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Any advice welcomed!
Thanks
Bob
Posted by: @spudthe COP seems to be about 2.2.
Bob
Where are you getting the numbers from? I have about the same, based on the "Energy Delivered" reported by the FTC6 controller.
However the total energy consumed in 12 months by the heat pump according to the separate meter is about 3850kWh. The 'contract of performance' states 2623kWh input for space heating and 1586kWh input for hot water, total 4209 kWh so we are coming in under that. This suggests that the FTC6 isn't a reliable source for the energy delivered. (the FTC6 reports about 10% more kWh consumed than the actual heat pump meter).
We probably save a bit on hot water as there are only 2 of us in a 5 bedroom house, but most of the house is heated to c. 21C. The running cost of the MVHR and the pumps do not go through the heat pump meter so I suppose total heating cost should include that.
Quite early on, I tackled the supplier about the poor COP. TBH I got a bit of a brush off - they said the FTC6 implied COP is just an "estimate" and should be ignored. Apparently I would need a heat meter to get a proper measurement of COP (I do not have one fitted).
In a nutshell, the COP as measured by the FTC6 is pathetically low, but the actual electricity consumption is more or less what it should be.
Is this the case for you?
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Incidentally, it seems odd to have the towel rails tee'd off the heating flow. Our flow temp (UFH) is never higher than 40C and often not even at blood temperature. It would make more sense to be on the DHW flow (except insofar as it isn't heating water most of the time).
Maybe it's taking heat from the hot water tank? That would seem a bit silly especially if it were 24/7.
I put electric towel rails in our bathrooms. I have some controllers fitted whereby a push of a button puts them on for 2 hours.
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Posted by: @spudWe moved into our house in December. It is roughly 5 years old, A rated wit a Mechanical Heat Recovery System and an 11Kw Ecodan with UFH upstairs and down.
The control system, is really odd. We have Uponor manifolds for the UFH. They are fitted with Uponor 24V actuators and T148 thermostats in the various rooms. Some odd things with the Uponor system is that it seems like a bus wired system for the thermostats so they are all wired together and back to the control unit. They have a night time set back which was at 4 degrees, we changed this to 2 degrees because the house was taking too long to get back to comfort levels in the morning and it seemed to be unnecessary cycling. Another weirdo with the Uponor is that the manifolds have a timer control, this manages things like the set back, but there is no battery backup so both timers need to be reset after a power cut. If I could I would junk the Uponor system and replace it with Heatmiser, but the thermostats are bus wired.
I have been trying to optimise the system in various ways as the COP seems to be about 2.2. The system design seems to be fairly poor as well. There are towel rails in the upstairs bathroom and these are T'd off the heating flow and return with no control valves and therefore rely on TRV's. Even odder is that when the UFH manifolds are off, the towel rails still run suggesting the heating is permanently on and not wired to the UFH manifold controllers. I suppose this could be so that the heating runs all the time and the room stats shut off the various rooms when they reach the thermostats settings. Then I guess we rely on flow vs return temps? There also seems to be two zones, but no idea if this is upstairs or down or just a config error.
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Any advice welcomed!
Thanks
Bob
Please provide more details of your system.
How are operating the system, fixed LWT or weather compensation mode?
What value is the LWT and RWT?
Posted by: @spud
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Bob
I'm guessing that is the temp at the location of the FTC controller. Mine is in an "airing cupboard" with the pre-plumbed tank etc and when the door is shut the temperature in there can reach mid-30s, which Melcloud gives as Room Temp. I'm going to insulate all the warm pipes I can find in there.
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Thanks, yes I am using the data from the FTC. I'll see what I can get monitoring the actual power consumed.
Hadn't realised that the Ecodan measured the temp in the airing cupboard, but yes that is where it is located and it does get warm in there. Again, when I get to it I will check if that is where the temp is being measured.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 454 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago