Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New and confused ASHP owner
We moved into our house in December. It is roughly 5 years old, A rated wit a Mechanical Heat Recovery System and an 11Kw Ecodan with UFH upstairs and down.
The control system, is really odd. We have Uponor manifolds for the UFH. They are fitted with Uponor 24V actuators and T148 thermostats in the various rooms. Some odd things with the Uponor system is that it seems like a bus wired system for the thermostats so they are all wired together and back to the control unit. They have a night time set back which was at 4 degrees, we changed this to 2 degrees because the house was taking too long to get back to comfort levels in the morning and it seemed to be unnecessary cycling. Another weirdo with the Uponor is that the manifolds have a timer control, this manages things like the set back, but there is no battery backup so both timers need to be reset after a power cut. If I could I would junk the Uponor system and replace it with Heatmiser, but the thermostats are bus wired.
I have been trying to optimise the system in various ways as the COP seems to be about 2.2. The system design seems to be fairly poor as well. There are towel rails in the upstairs bathroom and these are T'd off the heating flow and return with no control valves and therefore rely on TRV's. Even odder is that when the UFH manifolds are off, the towel rails still run suggesting the heating is permanently on and not wired to the UFH manifold controllers. I suppose this could be so that the heating runs all the time and the room stats shut off the various rooms when they reach the thermostats settings. Then I guess we rely on flow vs return temps? There also seems to be two zones, but no idea if this is upstairs or down or just a config error.
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Any advice welcomed!
Thanks
Bob
Posted by: @spudthe COP seems to be about 2.2.
Bob
Where are you getting the numbers from? I have about the same, based on the "Energy Delivered" reported by the FTC6 controller.
However the total energy consumed in 12 months by the heat pump according to the separate meter is about 3850kWh. The 'contract of performance' states 2623kWh input for space heating and 1586kWh input for hot water, total 4209 kWh so we are coming in under that. This suggests that the FTC6 isn't a reliable source for the energy delivered. (the FTC6 reports about 10% more kWh consumed than the actual heat pump meter).
We probably save a bit on hot water as there are only 2 of us in a 5 bedroom house, but most of the house is heated to c. 21C. The running cost of the MVHR and the pumps do not go through the heat pump meter so I suppose total heating cost should include that.
Quite early on, I tackled the supplier about the poor COP. TBH I got a bit of a brush off - they said the FTC6 implied COP is just an "estimate" and should be ignored. Apparently I would need a heat meter to get a proper measurement of COP (I do not have one fitted).
In a nutshell, the COP as measured by the FTC6 is pathetically low, but the actual electricity consumption is more or less what it should be.
Is this the case for you?
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Incidentally, it seems odd to have the towel rails tee'd off the heating flow. Our flow temp (UFH) is never higher than 40C and often not even at blood temperature. It would make more sense to be on the DHW flow (except insofar as it isn't heating water most of the time).
Maybe it's taking heat from the hot water tank? That would seem a bit silly especially if it were 24/7.
I put electric towel rails in our bathrooms. I have some controllers fitted whereby a push of a button puts them on for 2 hours.
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Posted by: @spudWe moved into our house in December. It is roughly 5 years old, A rated wit a Mechanical Heat Recovery System and an 11Kw Ecodan with UFH upstairs and down.
The control system, is really odd. We have Uponor manifolds for the UFH. They are fitted with Uponor 24V actuators and T148 thermostats in the various rooms. Some odd things with the Uponor system is that it seems like a bus wired system for the thermostats so they are all wired together and back to the control unit. They have a night time set back which was at 4 degrees, we changed this to 2 degrees because the house was taking too long to get back to comfort levels in the morning and it seemed to be unnecessary cycling. Another weirdo with the Uponor is that the manifolds have a timer control, this manages things like the set back, but there is no battery backup so both timers need to be reset after a power cut. If I could I would junk the Uponor system and replace it with Heatmiser, but the thermostats are bus wired.
I have been trying to optimise the system in various ways as the COP seems to be about 2.2. The system design seems to be fairly poor as well. There are towel rails in the upstairs bathroom and these are T'd off the heating flow and return with no control valves and therefore rely on TRV's. Even odder is that when the UFH manifolds are off, the towel rails still run suggesting the heating is permanently on and not wired to the UFH manifold controllers. I suppose this could be so that the heating runs all the time and the room stats shut off the various rooms when they reach the thermostats settings. Then I guess we rely on flow vs return temps? There also seems to be two zones, but no idea if this is upstairs or down or just a config error.
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Any advice welcomed!
Thanks
Bob
Please provide more details of your system.
How are operating the system, fixed LWT or weather compensation mode?
What value is the LWT and RWT?
Posted by: @spud
When I look at the melcloud App, both zones typically show a room temperature of 26 with a set temperature of 21.
Bob
I'm guessing that is the temp at the location of the FTC controller. Mine is in an "airing cupboard" with the pre-plumbed tank etc and when the door is shut the temperature in there can reach mid-30s, which Melcloud gives as Room Temp. I'm going to insulate all the warm pipes I can find in there.
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
Thanks, yes I am using the data from the FTC. I'll see what I can get monitoring the actual power consumed.
Hadn't realised that the Ecodan measured the temp in the airing cupboard, but yes that is where it is located and it does get warm in there. Again, when I get to it I will check if that is where the temp is being measured.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 517 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 2 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 3 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 6 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 7 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 8 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 9 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 11 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 11 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 17 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 18 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 1 day ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 4 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 5 days ago