Mitsubishi Ecodan Fails to Heat Water despite temperature drop
This will show you how to check and adjust DHW settings. He waffles a bit to about half way through then gets to the important bit so far as you are concerned. Hope this helps.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
The settings for DHW are the defaults with the target set to 50 and drop set to 10. The issue is that even when the water temp drops well below 40 it still does not kick in and start heating the water. My daughter is now trained to hit the Heat Now button on the MELcloud app after her morning shower until we figure out why this is happening.
Posted by: @m1kegibsonThe settings for DHW are the defaults with the target set to 50 and drop set to 10. The issue is that even when the water temp drops well below 40 it still does not kick in and start heating the water. My daughter is now trained to hit the Heat Now button on the MELcloud app after her morning shower until we figure out why this is happening.
What's the 40C shown on the display?
It might be worth changing settings and changing them back, it feels like something might be out of sync between ftc and odu, or as @ashp-bobba suggests, calling mitsubishi.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@m1kegibson Apologies if I'm teaching grandma to suck eggs but have you confirmed the max temp drop in the controller is set to 10C? To do that you hold down the menu button for a few seconds till the hot water/heating menu appears then under the tap symbol press the pen/notepad symbol then there you will see the options for the max temp set that should be 50, as that is what Melcloud is reporting, rhe max temp drop value, which you should check is set to 10C. Then there is the max operation time that will stop hot water cycles if reached regardless of the set temp so check that is set to a couple of hours. Lastly, there is the time limit that prevents it restarting even if its demanding heat but that shouldn't be an issue at this time of year.
If you are happy to post screen shots of those values then at least we can confirm its all set correctly.
I don't believe its a scheduling issue as your screen shot shows a paused symbol by the hot water symbol and nothing else if it was on a schedule there would be a clock and if it was disabled completely there would be a stop sign so I do believe you are in constant hot water heating mode the unit just believes the temperature is satisified.
Hep. Max drop is 10C. Tried changing and it 5C made no difference. As you say, DHW set to Constant, target is 50C with 10C max drop. I think I will try setting a schedule and switching to timed operation when next round at her flat to see if that makes any difference. She is waiting for another engineer visit but all they do is turn it off and on and then say “there, it’s working now”!
@m1kegibson did you try calling Mitsubishi as suggested by @ashp-bobba, it may be the easiest fix!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Not yet. I am away at present so will do so when I am in front of the controller.
Posted by: @jamespaWhat's the 40C shown on the display?
Its the flow temperature for the heating circuit, it means its running a fixed flow temp and is not on weather compensation, get that changed come the heating season especially with UFH its way too high for all but the depths of winter and in a flat may not even need to get that high
If you are able to access the service menu settings and navigate to the thermistor readings, I suspect you may find the answer as to why the system re-heat is not behaving as you are expecting it to based on the information displayed to you by the FTC.
On the right of this screen, THW5A and THW5B are thermistor readings for the hot water tank (however slightly older systems, and the videos Mitsubishi have posted which are of the FTC4, only show one value). 5B is for a thermistor placed low on the tank, 5A for one placed higher up - around 2/3 up perhaps, it will depend on the tank design. 5B, the lower of them, will limit the heating cycle - i.e. when the bottom part of the tank has reached the target temperature the cycle will be ended, the upper one, 5A, is the one that will trigger the reheat cycle when the temperature at that level has dropped by the value that has been set.
The issue here is that it is the value of 5B that is displayed by the FTC as the tank temperature, and that can be many degrees below the temperature at 5A, the one that will trigger the reheat cycle. Currently on my tank 5A is at 40° and 5B is at 31°, and this can drop into the low twenties while still delivering hot water out of the top of the tank.
You don’t say what brand of tank is installed, but I am going to guess it is not a Mitsubishi pre-plumbed one. The screen shot of the daily temperatures you posted shows a gradual decline of tank temperature as cold water cools the bottom of the tank during the day when water is being used but otherwise a very stable temperature overnight. (For comparison my Mitsi tank records a steady loss of 6 or 7 degrees over 24hrs even when no water draw is introducing cold water into the tank.) So I would infer that the hot water at the top of the tank, above the placement of the thermistor 5A, may well stay close to the target temperature for a long time even as the bottom of the tank gets quite cold.
If your daughter’s hot water usage is relatively low a full tank could last for a few days before requiring a heating cycle. Switching on and off, or using a daily timed off/on will force a hot water cycle but the warmer the water remaining in the tank the less energy efficient that cycle will be. So tweaking the reheat settings to get the balance right may need some monitoring of the value of the thermistor 5A.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 329 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
This really helps. But I cannot work out the icon on th...
By Batpred , 3 minutes ago
-
RE: Fan is clipping ice build up from the front of unit.
Not sure if this helps, but the probes look like this. ...
By Mars , 9 minutes ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
So does that mean the rads are operating at the same fi...
By JamesPa , 13 minutes ago
-
RE: Running from backup generaor in powercut?
@transparent, super interesting. I had a long chat w...
By Mars , 20 minutes ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
Indeed. Present ToU tariffs are based on national sup...
By Transparent , 3 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 3 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 23 hours ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 1 day ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 1 day ago
-
RE: Setback savings - fact or fiction?
Never assume it makes an ass of u and me! You need the...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago