Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Solved] Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
Posted by: @papahuhu@jamespa @toodles Finally, after 6 months, my heat pump is now working correctly.
The hard reset of the modbus has completely resolved the control system delinquency. Running permanently and gently on an adaptive weather comp now as opposed to a drag race previously. Once cold rooms are now warm as rads are permanently emitting, power consumption significantly down, even the noise of the unit has significantly changed for the better. A wholly reformed beast now.
Thanks for help in getting me there, all it took in the end was powering down and restarting the outside unit. I had previously reset the inside computing paraphernalia but never the outside unit. Thanks both.
Classic isn't it. I will remember in future to suggest this to people experiencing odd errors. Now I come to think of it a similar procedure was suggested when I had some errors with my Vaillant. It turned out that the cause was a blocked filter so reset didn't fix it, but the fact it was suggested at all does indicate that it can be a problem. Modern electronics eh!
Im glad you are now up and running.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
previously it was so noisy, it was like having a diesel tractor in the garden, rattling and thumping and hissing. I’d even had 2 disputes with the neighbour over it and to be honest I agreed with them.
Now it’s just purring, god only knows what it was doing before but it’s chalk and cheese. Bloody electronics.
- 27 Forums
- 2,738 Topics
- 64.3 K Posts
- 575 Online
- 7,143 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Electricity price predictions
Nationally-based Demand Flexibility makes little sense....
By Transparent , 40 minutes ago
-
-
RE: Has anyone seen this problem before? Huge anticycling times
Oh dear. Glad it was replaced. I have been mighty imp...
By JamesPa , 7 hours ago
-
RE: Can I start an argument about buffer tanks please? 🙂
Dont, just adjust the LSVs to get different temperature...
By JamesPa , 17 hours ago
-
RE: Heat pump running costs – what has actually worked for you?
I installed the air source heat pump in January 2026, i...
By bobflux , 20 hours ago
-
RE: Grant Aerona Air to Water R290 6.5 kW - Quiet Mark and Silent Running
Thats all interesting. DHW on my Vailant seems to respe...
By JamesPa , 1 day ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
One of the other mods has just reminded me that @ashp-b...
By Majordennisbloodnok , 1 day ago
-
RE: PV and battery long payback - sense check query
@old_scientist I have now drafted 2 replies - both have...
By DavidB , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: adrian Manufacturer: Appliandirect.co....
By Adrian , 3 days ago
-
RE: Acond heat pump failed after four years - diagnostic quote £940 plus VAT
@downfield Thank you Downfield. This sounds potenti...
By Mia , 4 days ago
-
RE: Digest of UK Energy Statistics
@jeff Yes my brother in Oz told me of that charge year...
By Jancold , 4 days ago