Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Is My Midea Heat Pump Inherently Defective?
Posted by: @bobtskutterSwapping the radiator for a fan coil might not give you additional heat output because it's not the radiator that's causing the "restriction".
Absolutely, I am very aware of that! Moving to a fan coil is an (major) aesthetic improvement, but only once I know it will have adequate flow.
I am still trying to think of a way of making a diagnosis ie where is the obstruction, and what is it. I know how to drain the system and so also know it is not a trivial undertaking, and I would prefer to know if possible what I need to fix while it is drained down. I am also not inclined to do it during one of the coldest month's of the year, in case something goes wrong!
Midea 14kW (for now...) ASHP heating both building and DHW
Naturally I was concerned that increasing the energy out (delivered to the house) by opening up the lock shield valves might increase the energy in (used). I now have enough data to be able to plot hourly energy in and mean room temp for hours at a particular OAT for before and after I opened up the valves. I have done this for year to date (note date time axis is categorical, they are just the hours that match the OAT criteria), for mean OATs of 5 (5.0-5.9, normal running) and 2 (2.0-2.9, defrost territory) , and marked when the valves were opened with a down pointing arrow:
Interestingly, no obvious penalty, in fact very possibly (need more data, and there are things I haven't controlled for...) an improvement! In both charts the mean room temp improves a bit (as expected) and in both charts the energy in appears to fall. It's more marked at 5 degrees than 2 degrees OAT, but still present on both charts. Truly heat pumps are a miracle, that surpasseth all understanding...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayTruly heat pumps are a miracle, that surpasseth all understanding...
I've just remembered...two days after I opened the LSVs I dropped the weather compensation curve 2 degrees, and then 2 days later I dropped it by another 2 degreees.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayI dropped the weather compensation curve
That'll do it 😉
Can you go lower?
Bob
Posted by: @bobtskutterCan you go lower?
Very possibly. The IAT is at the warm end of my preferred range, and it looks like we'll have fairly settled though cool weather here over the next few days so a good time to experiment. Watch this space...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayTruly heat pumps are a miracle, that surpasseth all understanding...
Somehow that feels like the basis of a motto/strapline.
Without a doubt the combination of the nonlinear response to the main variables, the inherent complexity of the thermal dynamics of houses, contrasted with the extremely simplicity of the thermodynamics on which it is all based, really does make them fascinating beasts.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cathoderay any updates in this mild spell are you boiling indoors yet?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
Posted by: @judithany updates in this mild spell are you boiling indoors yet?
Thanks for asking. Yes, the indoor air temperature has certainly been more consistent, a bit higher by a degree or two despite the fact I have lowered the leaving water temperature by a few degrees. The Mark 1 Human Sensor (me) also reports good comfort levels. All in all a success, and I don't think my costs have increased greatly, if at all, the lower LWT appears, as expected, to mean better performance, with COPs at times in the 4-5 range. Sometimes I think we forget how much difference a change in COP can make. For example, a seemingly not very large change, at least in absolute terms, from a COP of 3 to 4.5 means, all other things being equal, including having the same heating load, the unit costs part of my electricity bill falls by one third - where I would have paid £100, I now only pay £66.66, not a trivial saving.
Here's my chart for the last week. On Monday, I restarted the overnight setback (using room stat down to 16 degrees between 2100 and 0300), as I am interested to see how the now all valves open system copes with the recovery period after the setback. Previously it struggled, sometimes taking 12 hours or so to get back to temperature. On Tuesday morning, after a mild night, it recovered well, back to where it should be by 0700. Last night was significantly colder, and the recovery has been a bit slower, but by no means a disaster, despite being in defrost territory. Bear in mind this is partly managed by my auto-adapt script, which adjusts the LWT depending on how far the actual IAT deviates from the desired IAT. At the moment the script is set up to do one degree of LWT change for every degree of actual vs desired IAT deviation, up to a max of 3 degrees eg if desired IAT is 19, actual IAT is 17, deviation is 2 degrees and LWT increases by 2 degrees. These parameters are easily changed, by editing the script and restarting it. I am going to run the system as is for a week, and then see if it needs any tweaking.
Note: subsequent comments here about setback running have now been moved to another thread here.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 373 Online
- 7,028 Members
Join Us!
Latest Posts
-
RE: Anyone concerned about GivEnergy?
@editor Thank you for your reply. We do have an active ...
By SUNNYSKIES , 12 minutes ago
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a — a measured heat loss always trumps a calculat...
By cathodeRay , 54 minutes ago
-
RE: Setback savings - fact or fiction?
@cathoderay Thanks for your detailed response.Just two ...
By PeterWurmsdobler , 1 hour ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
The hot water heating looks normal. The heat transfer ...
By GrahamF , 3 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 5 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 16 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 21 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 23 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 1 day ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 1 day ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 1 day ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 2 days ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 2 days ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 2 days ago