Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ideal Logic ASHP - change from 55°C to 35°C Heating?
Ok on second thoughts scrub the questions. Id be tempted to optimise the rads as previously described. If you find that this results in a rad curve lower than 0.8 (IE the rads can run at a lower temp than the ufh), assess what to do with the ufh. If there is scope to run it at lower ft do so otherwise this will be the limiting factor. It would be quite unusual however for rads to be sized so they need a lower ft than ufh.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Agree - I will finish optimising the rads before I think about the UFH
UFH temperature is adjusted with the mixing valve located on the manifold. It's currently set at 50°C which is the max setting but can be dialled down if needed. The speed of the pump can also be tweaked to increase or decrease the flow rate. The flow meters can also be adjusted for each loop if needed but fully open up when the UFH is on.
I've now opened the rad TRV's to max and will monitor the heating performance over the coming days.
UFH should never be at 50C since small feet can get burned. I think the regs say 39(?). But your floor covering could be damaged too unless it’s tile or concrete. Nobody want pipe shaped marks on their wood or blown adhesive on LVT.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
Good point. I’ll keep my eye on the manifold temperature gauge which is currently showing 30C with the room temperature currently at 19C. After changing the heat curve yesterday from 1.5 to 1.3 the heating flow temperature has reduced from 50C to 45C. I’m not sure the UFH would ever reach the same temperature as the flow but best to keep my eye on it to prevent the issues you have mentioned. Thanks for your help. It’s great to learn from others, especially through forums like this one
- 27 Forums
- 2,799 Topics
- 66.2 K Posts
- 3,980 Online
- 7,206 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
@dansus yeah, that definitely needs fixing. Good spot. ...
By Mars , 5 hours ago
-
RE: How will removing the standing charge on gas bills benefit heat pumps?
@toodles GIGO always stands! My Cosy 6, as you can...
By Watcher , 9 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Interestingly we had an internet outage about a month a...
By Rob of York , 15 hours ago
-
RE: Double or Triple Glazed Windows?
Posted by: @singlespeed With 9 years repairing windo...
By Rob of York , 15 hours ago
-
@transparent we’re still running a secure version of PH...
By Mars , 19 hours ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
Much longer than that here. The heating isn't even on. ...
By bobflux , 1 day ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Obviously the weather is changeable but there's a defin...
By Singlespeed , 1 day ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@rob-of-york I must admit that when we had a Daikin hea...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
Get the Renewable Heating Hub heads-up on WhatsApp. I...
By Mars , 2 days ago
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
@editor I pointed out to the one of the Fuse execs that...
By dansus , 2 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews As well as loft insulation, there are othe...
By Rob of York , 2 days ago
-
RE: BT cuts you off, Plusnet blames Openreach... welcome to “seamless” broadband switching
Both of which (in most cases) use Openreach for the las...
By JamesPa , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Yes, this is a swiss and german standard I believe, Vai...
By Batpred , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@editor FWIW my problem was resolved, eventually, after...
By BigFish , 3 days ago
Members Online
No online members at the moment