Search with Wattson
Hoped for improveme...
 
Notifications
Clear all

Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Hoped for improvements not being realised on my Mitsubishi heat pump

64 Posts
6 Users
12 Reactions
13.6 K Views
(@davidalgarve)
Reputable Member Member
Joined: 3 years ago
Posts: 249
Topic starter  

@f1p Thanks for your interest. Yes it is set for Room RC1. I am going to move the Par 60 from the second coldest room in the house to an upstairs bedroom, currently registering 21C on a Shelly Gen 3, and see what happens.

I am ordering a connector to be brought out to me later in the month.


342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW


   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 1 year ago
Posts: 129
 

The default for an unpaired or incorrectly assigned thermostat is also 20, could you further check:

Initial settings > Room sensor settings > Room RC zone select > Room RC 1 = Zone1 (black background)


This post was modified 9 months ago by F1p

   
ReplyQuote
(@davidalgarve)
Reputable Member Member
Joined: 3 years ago
Posts: 249
Topic starter  
 

@f1p1p I have checked both and believe them to be correct, (see photos), but I would appreciate your confirmation.

IMG 2205
IMG 2204

I now think this was a false trail because moving the PAR 60 to a warmer room resulted in an "Inside Temperature" readout of 21- 21.5 C

Weather compensation is now 27C @ 18C, but at +8, in an attempt to get an increase in inside temperatures. For the first time in 3 years we are getting signs of mould in the North facing rooms.

Screen Shot 2026 02 02 at 11.21.33

I have ordered a connector but I won't get delivery for about 3 weeks.

The only thing that I can think of trying now is the dip switch for Mixing (Buffer?) tank.

Screenshot 2026 02 02 at 11.26.54

342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW


   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 1 year ago
Posts: 129
 

@davidalgarve 

The settings look correct, and i see you now have movement in the value - so it appears to be working.

I know there is some filtering, but is it accurate or is there a difference with other sensors?



   
ReplyQuote
(@davidalgarve)
Reputable Member Member
Joined: 3 years ago
Posts: 249
Topic starter  

@f1p

Right now it is sitting next to Shelly Gen3 in the living room. The PAR 60 is reading 21.5 and the Shelly is reading 21.8

The detailed report is here:

https://melpump.com/public-report/view/019c1e2a-6844-7aeb-9f9a-f0f6270fe56e

Thank you for your continuing support.

P.S. I have just received confirmation from Mitsubishi UK that my PUHZ-SW 120YHA is 12 Kw and not 16kW so will change it on the app.


This post was modified 9 months ago by DavidAlgarve

342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW


   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 1 year ago
Posts: 129
 

The DeltaT is pretty high, by the sounds of it flow rate too low for the outdoor unit size
Pump might be set on 5 - but potentially it needs replaced with a larger circ pump

It's quite impressive you are pushing 44C flow at a freq of 26Hz



   
👍
1
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5629
 

Posted by: @f1p
↑

The DeltaT is pretty high, by the sounds of it flow rate too low for the outdoor unit size
Pump might be set on 5 - but potentially it needs replaced with a larger circ pump

Or the filters cleaned ...   OP says upthread that he hasn't checked them!


This post was modified 9 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 1 year ago
Posts: 129
 

Posted by: @jamespa
↑

Posted by: @f1p
↑

The DeltaT is pretty high, by the sounds of it flow rate too low for the outdoor unit size
Pump might be set on 5 - but potentially it needs replaced with a larger circ pump

Or the filters cleaned ...   OP says upthread that he hasn't checked them!

Also worth checking for broken springs in 2 port zone valves or 3 way valves not seating/passing and restricting flow.

 


This post was modified 9 months ago 6 times by JamesPa

   
👍
1
ReplyQuote
(@davidalgarve)
Reputable Member Member
Joined: 3 years ago
Posts: 249
Topic starter  

 

@f1p 

I would appreciate some clarification on a few points:

1 At time of forwarding the Detailed Report the pump setting was 3 and the flow rate 11 l/min. Were you able to see a different flow rate on the detailed report?

(I have now increased this to setting 5 and 16 l/min, so would a further detailed report be useful once things have settled down?)

2 Is the flow rate on my display a specified figure at a setting or an actual flow rate? (Note that in an old note to myself I had said setting 5 corresponded to 25 l/min)

3 What would cause the Ecodan to "modulate it down"?

4 As reported, I can find nothing to switch off the second pump which you record, but I can see a hidden menu item for selecting reporting on multiple pumps, here.

Screenshot 2026 02 02 at 15.12.36

Is that what your system is seeing?

5 The strainer is not very accessible (see below) and may require removal of the main PCB so I need to be sure I am on the right track before tackling this.

IMG 2206

342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW


   
ReplyQuote
 F1p
(@f1p)
Estimable Member Member
Joined: 1 year ago
Posts: 129
 

Posted by: @davidalgarve
↑

1 At time of forwarding the Detailed Report the pump setting was 3 and the flow rate 11 l/min. Were you able to see a different flow rate on the detailed report?

Without the adapter installed there is no flow rate information available to plot on the graph (as MELCloud does not record it)

 

Posted by: @davidalgarve
↑

2 Is the flow rate on my display a specified figure at a setting or an actual flow rate? (Note that in an old note to myself I had said setting 5 corresponded to 25 l/min)

Service > Running Parameter > "540" reports Flow Rate in l/min

Pump speed PWM setting (1-5) is no certainty of actual flow rate, but it will be directly linked

 

Posted by: @davidalgarve
↑

3 What would cause the Ecodan to "modulate it down"?

When flow temperature is approaching overshoot of setpoint

 

Posted by: @davidalgarve
↑

4 As reported, I can find nothing to switch off the second pump which you record, but I can see a hidden menu item for selecting reporting on multiple pumps, here

 

Is this a cross post with someone elses suggestion? I'm not sure we wanted to - i haven't checked the Hydrobox schematic as to see if there is a zone pump in addition to the primary circulation pump

Shame that strainer is difficult to access


This post was modified 9 months ago by F1p

   
👍
1
ReplyQuote
(@davidalgarve)
Reputable Member Member
Joined: 3 years ago
Posts: 249
Topic starter  

Posted by: @davidalgarve
↑

4 As reported, I can find nothing to switch off the second pump which you record, but I can see a hidden menu item for selecting reporting on multiple pumps, here

 

Is this a cross post with someone elses suggestion? I'm not sure we wanted to - i haven't checked the Hydrobox schematic as to see if there is a zone pump in addition to the primary circulation pump

Shame that strainer is difficult to access

I was just wanting to eliminate any possibility that the second pump being reported (removed when buffer tank modified) could be influencing the flow rate of the remaining pump.

Further to this, would Mitsu change the flow rate of the pump depending upon whether a buffer ("mixing") tank was being used? Considerably less resistance in a buffer compared to e.g. multiple radiators. Will try dip switch 2-6 tomorrow.

 


342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5629
 

Posted by: @davidalgarve
↑

Shame that strainer is difficult to access

Madness, like putting the oil filter somewhere that necessitates removal of the engine before cleaning it.  Unfortunately, inconvenient as it is, it will need to be checked.  Mine, after just six months in a system that had been well flushed, was totally blocked.  Perhaps consider fitting an additional external strainer so that the internal one is 'protected'?


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
Page 3 / 6
Share:

SPONSORS

Join Us!

Installer Finder

Degrees of Separation

Latest Posts

SPONSORS

Members Online

Click to access the login or register cheese
Protected By
Shield Security PRO