Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hitachi Yutaki M efficient operation
So i think i have narrowed it down without however knowing the solution. Buffer creates a loop. Hp provides the required water temp to the buffer but somehow the energy is not diverted to the ufh but returns to the hp, hence the low dt and the reduced temp at the manifolds compared to the outlet reading of the hp. Does this means that there is unbalanced flow between the primary circuit (hp and buffer) and secondary circuit (buffer and manifolds)? The circulating pump in the first circuit is adjustable but the second is not
Posted by: @iraknicDoes this means that there is unbalanced flow between the primary circuit (hp and buffer) and secondary circuit (buffer and manifolds)? The circulating pump in the first circuit is adjustable but the second is not
Yes, almost certainly.
I dont know if the HP can control the buffer, some can. If the buffer has two temperature sensors at different heights then its possible in principle to use this information modulate the speed of one or other pump so that on average the rates are the same (which is ideally what you want). It would be worth looking at the HP manual and the buffer in case it can do this.
Otherwise you are down to adjusting the pump rates. The HP might adjust the primary pump to suit its needs. If it does so and unless the HP does feature buffer management, Id be loathe to touch this. That said there is generally no harm in turning the primary up, HPs complain about low flow (because its not enough to take the heat away) more than about high flow.
Im surprised that there is no adjustment on the secondary pump, many have three settings.
Having the primary a bit faster than the secondary will tend to force the thermocline (barrier between 'hot' and cold' water, assuming its stratified) down the tank, which means that the feed to the emitters should be at the same temperature as the feed from the heat pump, thus minimising the sacrifice in efficiency which would occur if the feet to emitters is lower temp than the feed from the heat pump. Obviously this will cause a little bit of recycling through the heat pump, but its better so far as I understand these matters than pushing the thermocline to the top which is what happens if the primary is slower than the secondary.
Do you know why the buffer is fitted? Generally they are a bad idea in heat pump systems, albeit that many installers put them in because its pretty much guaranteed to reduce callouts (by masking problems).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@iraknic how are you monitoring your UFH delta T?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@jamespa the buffer was fitted to increase water in the system due to the existence of zones. @editor
I am measuring the temps at the manifold using an IR thermometer. In my case it seems that the primary water pump is slower than the secondary (after the buffer) one? Can the secondary flow be reduced by manually decreasing ufh flow at the manifolds?
Posted by: @iraknicCan the secondary flow be reduced by manually decreasing ufh flow at the manifolds?
Yes. Its the same as turning down the lockshield on a radiator
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
i attach the setup of the buffer, highlighting the return lines and the specs of the water pump that is placed after the buffer. I thought of closing a bit of the outlet and return valves of the left side of the buffer (to and from) the manifolds and increase the flow of the primary pump (from hp to the buffer) to see what happens
@iraknic Please note, I don’t have any experience at all (diddly squat) of UFH plumbing but if a circuit has both send and return valves, it is probably only necessary and better to just constrict the flow to the circuit and leave the return without any restriction. I may be talking through the wrong orifice of course! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @iraknicA reason i believe is causing a low delta-t is the waterflow that is too high
I also tried lowering the internal waterpump speed but have not found yet how to do that. The setting in the installer section of the controller did have a deltaT setting and a HP ON deltaT setting I changed both to the same increase but the waterpump speed still is 100%
How did you try changing the deltaT?
I have a modbus gateway from which I can extract most relevant information. No real cycle information to be found though. Once can monitor and deduce it sure.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 1,011 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 5 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 10 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 11 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 11 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 14 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 20 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 20 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago