Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @webcmgDoes anyone happen to know the current month energy consumption update interval for the 700/6 controller? It certainly isn't realtime (no idea why not!) and I have a significant variation in usage at the meter vs usage at the controller. If I can figure out when the controller updates I can rule out something else using so much energy.
Thanks,
Chris
Hi,
Check to see if you have a booster heater (immersion) or backup heater that may be operating.
@Derek-m @kev-m @alec-morrow @mike-patrick @mattengineer
General update. Vaillant attended and resetup the controller and checked the glycol levels. They set the programmer to 0.7 heat curve and 21 deg desired heat temperature. Room stats in hall and landing set to 18 deg c, others set to 21 (kitchen/snug area), lounge and dining room currently set to frost protection. At night the thermostats are set to three degrees below day time temperature as advise by the engineer. Hot water set to 50 deg c and recharges if it drops by 5 deg between 05:00 and 21:00.
I've been monitoring temps and, sadly, it's the same story. Warm downstairs, cold upstairs with room temps (now measured by my array of disconnected tado wireless trvs repurposed from my old house) between 14 and 18 deg c (see image). The landing stat does not turn off unless sun is shining directly through the window for an hour or so in the middle of the day and the temp, on the landing only, reaches 20 deg, other rooms remain at or, below 18 deg c. Rooms with vaulted ceilings and lots of windows (Bed 1 and 4) tend to be the coldest, ensuites are also very cold - not ideal at all.
24 hour Kwh at the meter is as follows, I think the latest is still reletively high:
16/01/2022 - 56.2 kwh
17/01/2022 - 48.7 kwh
18/01/2022 - 67.1 kwh
The installation plumber attended and measured the flow and return temperatures on each of the radiators. They were all within 2-3 deg c with flow ranging between 35-37 and return 32-35 deg c. He is happy that the plumbing is working as intended. Flow rates on UFH pumps have been decreased. Flow rate of radiator pump set to its highest setting. Flow rate indicators typically @ 2.5 litres per minute.
To experiment and optimise, what steps would you take now to try to increase heat whilst maintaining some level of economy? Should I:
- Leave on 24/7 at 18-20 deg across the whole house?
- Increase the night time temperature?
- Increase the desired temperature from 21 deg c on the VRC700?
- Increase the heat curve?
~£12 per day seems expesive given upstairs isn't warm 🙁
Thanks in advance for any further advice.
Posted by: @derek-mPosted by: @webcmgDoes anyone happen to know the current month energy consumption update interval for the 700/6 controller? It certainly isn't realtime (no idea why not!) and I have a significant variation in usage at the meter vs usage at the controller. If I can figure out when the controller updates I can rule out something else using so much energy.
Thanks,
ChrisHi,
Check to see if you have a booster heater (immersion) or backup heater that may be operating.
Immersion is off at the switch - how might I identify a backup heater? I think the difference in values is probably just a timing issue.
Just for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week. Our flow temps vary between 30-35 depending on how cold it is outside.
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
@webcmg is you need a higher curve for radiators than the floor…but more heat means more energy consumed.
and the floor temps need to be mixed down by a mixer controlled by the vr71 which works with the vrc700
You can’t get any manageable out come with out installing as vaillant design engineers (in Germany) intend
Professional installer
Posted by: @colinJust for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week .
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
Wow, this sounds incredible. When you say max assume you mean any TRVs and thermostats at say 25 deg c or something? What is your desired temp set at on the vrc700?
Posted by: @alec-morrow@webcmg is you need a higher curve for radiators than the floor…but more heat means more energy consumed.
and the floor temps need to be mixed down by a mixer controlled by the vr71 which works with the vrc700
You can’t get any manageable out come with out installing as vaillant design engineers (in Germany) intend
And I found out that it was Vaillant themselves who 'outsourced' the system design... sigh.
@colin assume your setup has a controlled mixer?
Are you using vaillant mixers for the floor? Or is there a pump for each floor zone?
raise heat curve and shut down all the floor and see how the rads respond?
Professional installer
Posted by: @webcmgPosted by: @colinJust for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week .
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
Wow, this sounds incredible. When you say max assume you mean any TRVs and thermostats at say 25 deg c or something? What is your desired temp set at on the vrc700?
Pretty much. I have the radiator TRVs mostly up to max, and the UFH zones mostly set to 25 deg, then let the heat curve adjust the flow temp. I use the TRV to limit the temp in the kids rooms. The key is to get the flow temp as low as possible while keeping the house at a comfortable temp. Our indoor temps are around 22-24 degrees, based in a relatively cold/exposed part of Scotland, but it's a well insulated new build.
Posted by: @webcmg@colin assume your setup has a controlled mixer?
That, I'm not sure I can answer. We have a Snug Underfloor Heating solution, which has manifold, actuators etc and it looks like it mixes but still trying to figure that part out. The heating engineer is due back soon to install the Internet Gateway and cooling resistor option so hopefully I'll get a better hand-over than I've had.
Posted by: @colinPosted by: @webcmgPosted by: @colinJust for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week .
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
Wow, this sounds incredible. When you say max assume you mean any TRVs and thermostats at say 25 deg c or something? What is your desired temp set at on the vrc700?
Pretty much. I have the radiator TRVs mostly up to max, and the UFH zones mostly set to 25 deg, then let the heat curve adjust the flow temp. I use the TRV to limit the temp in the kids rooms. The key is to get the flow temp as low as possible while keeping the house at a comfortable temp. Our indoor temps are around 22-24 degrees, based in a relatively cold/exposed part of Scotland, but it's a well insulated new build.
Thanks going to give this a try...
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
1 week ago
-
Surface mount or bury primaries for heat pump installation?
3 weeks ago
-
Design Of Cascade System Replacing Undersized ASHP
3 weeks ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
4 months ago
-
Rodents! A word of warning for heat pump owners
6 months ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,724 Topics
- 63.8 K Posts
- 1,083 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Microgeneration Certification Scheme (MCS)
I’ve just spotted that Ian Rippin is leaving MCS as CEO...
By Mars , 1 hour ago
-
RE: Who's your electricity provider and what's your tariff?
Hi. I have 16 panel solar panels producing about 20k...
By peterackstraw , 5 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 6 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 20 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago