Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @lfranklin
- @derek-m yes the vessel (buffer I think new one says) was exchanged and is fully pressurised and have checked system fully for any air.
Do you have a suitable thermometer or thermometers that could be used to measure both room temperatures, and could also be taped to radiators and pipework (with suitable insulation) to measure the system temperatures.
Starting from the pipework leaving the heat pump, could you work your way through the system and provide both wide angle and close up photo's of any equipment that you locate, things like valves, pumps, cylinders etc.
Posted by: @william1066Posted by: @derek-mWe can then try to go through your system operation in a logical and systematic manner.
@lfranklin - there is definitely two (or potentially more) components to this, and as Derek said, being systematic will speed things up. From what I can determine in the thread, there are a whole bunch of things that need addressing. My summary is as follows.
- can hear expansion vessel working and its very annoying when trying to sleep
- struggling with system not heating two rads on the system
- added a second pump onto the return side of the system trying to fix problem 2 above and that seemed to help for a few hours when first installed but now not coming back on again
- if i turn the TRV off on others earlier in the system off the last two do get warm but even then not hot
- We had solar installed at the time too (16 x 405w panels) and even that isn't working right at just 1-1.8kwh per day generation at the moment
- wired remote controller showing water pump and some other bits and a very high heat water temp on main front screen even though heating has been off
- heating stopped all together today despite pump running and eating lots of electric!
- DHW not getting up to temp and so not letting the radiators have hot water
1,2,3,4 and 8 could be combined into a single group, which is likely [mostly] plumbing rather than heat pump settings related. (with the caveat that for heat pumps you should be going for warm radiators, not hot radiators)
Item 5 probably needs its own thread on this forum.
6 is likely config/understanding of the Samsung Gen6 system operation
7 probably a mixture of hive, samsung settings, plumbing
I can probably help with 6, the rest, not so much.
To save me having to forage through the Samsung manual, do you know where the control settings for booster or back up heaters are located, and if they can be disabled if necessary?
From what @lfranklin has previously stated, you have correctly identified that there could be a number of issues.
My suggestion would be to initially set the system to operate in fixed LWT mode, and then carry out temperature measurements around the system to try to identify where the heat energy is flowing. Could you therefore explain how to set the system to fixed LWT at say 40C?
@derek-m The easiest way that I found to do this was to set the weather compensation to 40 at minimum and 40 at maximum outside temperatures. That way it’s always going to be 40° C. There is another way, I presume but I haven’t found it!
Posted by: @derek-mTo save me having to forage through the Samsung manual, do you know where the control settings for booster or back up heaters are located, and if they can be disabled if necessary?
The booster heater can be disabled [#3031], but you can also disable it by making sure your hot water is on economical setting, not standard, power or forced. That you can do in the schedul
The benefit of leaving it enabled is to speed things up when needed, by just changing the mode on the remote controller (not so convenient if in the loft)
Posted by: @lfranklinI think that the booster heater is set to come on for last 10 mins of heating if not at temp.
#3032 and #3033 will tell you when and for how long
Posted by: @lfranklinI think that the booster heater is set to come on for last 10 mins of heating if not at temp.
Note: there is an element of "lost in translation" in all the heat pump manuals, but this is what they say.
In Power or Forced mode the booster heater starts without any delay (so ignores) FSV #3032
In Economic mode the DHW heating is via the heat pump only (I think this only applies if your target HW temperature is 55 degC or less. see page 34 of the manual)
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 288 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 28 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 36 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 13 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 14 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 14 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 17 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 24 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 24 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago