Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @adamkAlso I’m not entirely convinced the heat loss the last company did is that accurate
I apologise if this has been covered already but have you got any way to sense check loss calculations eg from past usage. The two, three hour full professional surveys I had done on my house both said 16kW, the actual loss is 7kW. This may be extreme but illustrates how far out surveys can be
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I’ve had a few done most come out around 7kw so that’s probably about right, but the loss per room I’ve only got one and it’s been corrected a few times but one bedroom is still listed 2m2 smaller than it is.
@jamespa to be that far out the assessor has got the insulation thickness of the floor, walls and ceiling too thin.
i have 150mm thickness but its celotex not rockwool, took ages to explain that to the assessor who could only input thickness and not the true R rating.
@adamk Sounds encouraging, what about any independent measure of total loss eg from current gas/oil consumption.
Rooms share heat to a fair extent so it's debatable how much precise room by room losses matter, so long as they are roughly right. If in doubt oversize emitters and turn down the lsv (or flow temp if they are all oversized). Much more important to get the total right so your heat pump is right-sized.
Posted by: @agentgeorgeto be that far out (16 kW Vs 7kW actual) the assessor has got the insulation thickness of the floor, walls and ceiling too thin.
I got the calculation details for one of the two surveys, they ignored any fabric upgrades they couldn't see (principally insulation for the solid walls) even though I made a big point of telling the surveyor about them, double counted room to room losses and overestimated ventilation loss. I presume the other surveyor must have done similar. GIGO
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa what I didn’t want to do was oversize too much then end up having the HP cycling. What I have noticed is most companies I’ve contacted want to fit a 45L Vaillant buffer/volumizer? Yet after watching this weeks QA vid a guy on there said no buffers.
Posted by: @adamk@jamespa what I didn’t want to do was oversize too much then end up having the HP cycling. What I have noticed is most companies I’ve contacted want to fit a 45L Vaillant buffer/volumizer? Yet after watching this weeks QA vid a guy on there said no buffers.
The guy was right as regards buffer tanks, avoid. However a 2 port volumiser is ok. Unfortunately terminology isn't quite consistent.
Check that it's got 2 ports only. 2 ports good, 3 or 4 ports bad.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
just trying to roughly get an idea what price an install should be if the following has already been done.
1) upgraded some 15mm copper runs to 22mm. 15mm for the last 3m worst case.
2) the above mentioned 22mm and about half the rads (15mm feeds) fed from 28mm flow and return.
3) 28mm primaries run from plant room and lagged and core drilled through back wall.
4) plant room 1300w x 900d x 2300h
5) new meter box on same side of house as plant room and heat pump, so easy run along wall for cabling.
6) no rad changes as part of the quote.
i would think the only work needed is heat pump base, heat pump mount, 28mm primaries up back wall in primary pro lagging, pipe work for HW tank and rad circuits in plant room, electrical work for plant room and heat pump, smart controls, commissioning.
@adamk, in terms of ballpark pricing, if we assume a straightforward install of a mid-size unit (say 8–12kW), with a standard heat pump ready HW cylinder and proper controls/commissioning, you’d expect to be in the region of £9,000–£12,000 (pre-BUS grant).
That assumes you’re going with a reputable installer using quality kit and doing things by the book: no cut corners, proper lagging, flow setting and performance commissioning. Some might come in a bit lower, but I’d be cautious if it drops below £9,000, because at that point they’re likely clawing it back somewhere else (labour, electrical spec, shortcuts, etc.). The caveat there will be the size and brand of ASHP.
Estimated time of completion is another benchmark. If they say it’ll be installed and commissioned in a couple of days, run.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @adamkjust trying to roughly get an idea what price an install should be if the following has already been done.
1) upgraded some 15mm copper runs to 22mm. 15mm for the last 3m worst case.
2) the above mentioned 22mm and about half the rads (15mm feeds) fed from 28mm flow and return.
3) 28mm primaries run from plant room and lagged and core drilled through back wall.
4) plant room 1300w x 900d x 2300h
5) new meter box on same side of house as plant room and heat pump, so easy run along wall for cabling.
6) no rad changes as part of the quote.
i would think the only work needed is heat pump base, heat pump mount, 28mm primaries up back wall in primary pro lagging, pipe work for HW tank and rad circuits in plant room, electrical work for plant room and heat pump, smart controls, commissioning.
I agree with @mars.
My install was not dissimilar. I got a 7kW Vaillant, 200l cylinder and 4 rads (including one fancoil) for 12.5K les grant. Im in the south east of england, prices may differ elsewhere. In my case the 16A feed for the ASHP was already in place (my friendly electrician did that for £180 - I ran the cable he connected it up), but the pipework run from the ASHP to the point where all the existing pipework converged was a bit of a nasty and took a whole day, even though I had done most of the 'building' work to expose the voids where I wanted it hidden and then made good afterwards.
The whole install was six long days with one person doing the whole thing roughly split as follows
- Receive & check deliveries, site ashp, base on top of existing paving, run primaries to location of existing boiler - 2 days total
- Fit DHW tank & vent pipe - 1 day (8am-9pm without a break!)
- Radiators - 1 day
- Wiring, flush, connect up, debug, commission - 1 day
- Remove old cold water tank, insulate, tidy up generally, commission internet gateway - 1 day
I watched the guy more or less throughout and he worked very hard, so I dont think it could reasonably have been done in fewer man-days.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@editor guess the reason im asking is cause ive looked at the break down on heat geeks quote system and then stripped out what ive already done and im getting around £2800 after BUS for 7KW Vaillant with 250L HW tank and me doing the base. but so far cheapest is £3800, maybe there doing the base like the HG quote suggests?
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 293 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 1 hour ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 15 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 15 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 18 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago