Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
External stat issue
Hi
I'm back after running the ASHP for 7 months now with a different topic.
The pump runs fine with a constant temp of 20 degrees inside. It does cycle. I think we decided it's too big at 9kw.
Anyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers. The mercury is nearer predicted temperatures by forecast.
I would consider this important but should I make a thing of this?
Thanks
Cliff
Is it reading high or low?
Measurement of the outside temperature will directly affect Weather Compensation where the target flow temps are determined by the outside temperature, but if it's out by a known margin (3-4C), you may be able to offset the WC curve by the same amount.
It may also affect functions such as anti-freezing (if your heat pump has such features), which may be set to trigger at temps below 5C, either meaning the do not trigger when intended or trigger too early depending if it's reading high or low.
Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero
Posted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
I mean OAT. I have an external stat facing north around 2m up
Posted by: @cliffhangerI mean OAT. I have an external stat facing north around 2m up
If it is measuring (and only measuring) the OAT, it is a sensor, if it measures the OAT and then does something like turn the heating on or off, then it is a (thermo)stat. It is difficult to answer your original question (how important is accuracy) if we don't know what you are talking about!
Midea 14kW (for now...) ASHP heating both building and DHW
Right. It's the outside weather sensor that's wrong compared to Mercury.
I'm running the pump on external weather compensation.
@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
As mentioned earlier it is 2m up sand facing north.
Looks like I will have to make curve changes as it is consistently inaccurate. Still under guarantee incidentally. Are they as accurate normally as Mercury?
Posted by: @cliffhangerStill under guarantee incidentally.
That's probably the most important point, maybe see if you can get a replacement fitted?
Midea 14kW (for now...) ASHP heating both building and DHW
Midea 14kW (for now...) ASHP heating both building and DHW
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 2,027 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 1 hour ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 2 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 2 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 2 hours ago
-
RE: Why don't people choose heat pumps?
With a heatpump tariff, it should be cheaper to operate...
By Batpred , 2 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 2 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 6 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 10 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 3 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 3 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago
Members Online
No online members at the moment