Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Is it KISS or constant – weather compensation vs. set flow temperature?
Away at present. Hence the delay. Will get back asap.
Cliff
Okay. I have setup the system using just weather compensation. There is something called 'thermal blockade' on my smart controller which turns off the stat rather than turn it to maximum.
I'm going to video the heat curve but at the moment it starts at 18(20c) and runs to 45(-30). -5c = 33c. The OAT is 10c and the system is stable at 19.5c. I tried a lower curve but the pump cycled as expected, 25c is the lowest it will go.
What's struck me is how cool the rads are. They don't feel they could warm anything! But they do of course. Now we are at the end of March the system's not going to be tested at lower temperatures which to me is the breaker.
To be continued
Cliff
Posted by: @cliffhangerWhat's struck me is how cool the rads are. They don't feel they could warm anything! But they do of course. Now we are at the end of March the system's not going to be tested at lower temperatures which to me is the breaker.
Indeed. Its weird at first but you get used to it and actually it is more comfortable because the temperature gradients are less.
There is a school of thought pursued by some installers that having cool radiators leads to call outs (which is probably true). Thus some installers force a minimum FT of 37, which is roughly the point at which radiators feel warm. This of course increases the cost to the householder.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
We ran our radiations at anywhere between 30-35C over winter. At 30C I struggle to tell they are on. If I place my face over the top of the radiator, I can just about feel warm air convecting on my face. At 32C I can feel they are warm to the touch, and at 35C they are (relatively) positively hot!
I still walk around touching the radiators to see if they are on - I just need to trust the room thermostat, which doesn't lie.
Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero
I had to laugh at this as I do exactly the same thing, I read on here someone explain it well, the body is running at 36c so anything less will feel cold. As I explain to friends it is actually magic that heats my house!
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
25kWh Sigenstor battery
Hi
Just as an aside. My system is heating only.
What is the best way of turning a weather compensation setup off in the summer? I thought of turning the stat back on to its lowest temp, in this case 10c. Won't go any lower.
Or setting the heating curve to its lowest?
Cliff
@cliffhanger Mine has a 'space heating off' setting! Otherwise turn down thermostat if you have one and it's set up to call for heat
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,754 Topics
- 64.8 K Posts
- 1,499 Online
- 7,159 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
Thanks for sharing that. Your objective seems very sen...
By JamesPa , 1 hour ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Very nice. Ours was the opposite, about 10%...
By Papahuhu , 3 hours ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
A couple more points about placing solar panels at low ...
By Transparent , 3 hours ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@kilgorexv definitely a larger inverter will help and m...
By AndrewJ , 1 day ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
The installation is almost done! I've written up two ...
By tomasmcguinness , 2 days ago
-
RE: Glass lined Cylinder for private water supply
This has turned into a fascinating little rabbit hole. ...
By Mars , 2 days ago
-
RE: Switch suitable to change between two inverter CT's
Last winter my battery ,32KWh, could run the house com...
By Jancold , 2 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Agree with Major. And even if I was very happy with ...
By Batpred , 2 days ago
-
RE: Is the "divide by 2900" rule still valid?
There is another estimator that you could use, a formul...
By Rob of York , 2 days ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
@penval, really useful update. After all the discussion...
By Mars , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 5 days ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 6 days ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 6 days ago