Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan - optimal external installation?
I think this notion of an 'optimal' install is something of a chimera. Every installation is different, and the majority of forum users have experience of just the one installation. From what you have said (though images are worth a thousand words) your installation seems to be fine, the installers haven't done anything stupid.
If you are having vibration issues at the heat pump then it might be an equipment issue rather than a pipework issue. I have noise inside introduced by the circulation pumps, but only small amounts of occasional mechanical noise and the sound of the air being moved from the outside unit. The units weigh around 100kg so you wouldn't want any slight vibration to be converted into sound or transmitted to the rigid, fixed pipework, but they aren't going to move around like washing machines.
You ask a few questions:
28mm pipework should run as far as you can take it into the house - you need volume of water in the system to cover defrosts.
You protect the outside pipework and the pump either by having glycol so the water can just sit at very cold temperatures, or you circulate the warm water in the pipes to keep the outside parts from freezing – the anti-freeze valves are a fail-safe should you be unable to power the water circulation. You would not want to be dumping glycol.
Full bore valves are isolating valves...
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
I’d consider my system to be installed quite optimally… I have one anti freeze valve, no flexis, and over 20m of buried primary pipework.
I also don’t have any hydraulic separation, and I have 400mm clear to the rear of the evaporator.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @harriup28mm pipework should run as far as you can take it into the house - you need volume of water in the system to cover defrosts.
Yes. Where would the optimal position and method of stepping down? I assume nearest the unit, so at the unit's inlet/outlet - but not sure how.
You protect the outside pipework and the pump either by having glycol so the water can just sit at very cold temperatures, or you circulate the warm water in the pipes to keep the outside parts from freezing – the anti-freeze valves are a fail-safe should you be unable to power the water circulation. You would not want to be dumping glycol.
Thank you.
Full bore valves are isolating valves...
From the BES component diagram in the OP (relevant section below), it shows 'isolator valves' and 'full bore valves' - though, having just looked at it again, I've just noticed the isolator valves are inside the property:
The isolator valves I mentioned describing my install are Inta lever ball valves - I assume these should be full bore to maximise flow rate and be positioned as the primary pipework exits the brickwork outside? Is there any value in having a second set at the unit's inlet/outlet too?
Posted by: @rhh2348What's the optimal / minimum length and shape of flexihoses (and why, if not for best performance and least vibration)?
I'd appreciate anyone's thoughts on this, having read in one or two posts (I now can't find...) that longer hoses can reduce/eliminate vibrations travelling through the primary pipework elsewhere.
-
Rate the quality of your heat pump design and installation
6 hours ago
-
Mitsubishi Ecodan not good enough ?
2 months ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
3 months ago
-
Mitsubishi Ecodan circulation pump running.
3 months ago
-
Ecodan Auto Adapt Options
4 months ago
- 26 Forums
- 2,715 Topics
- 63.6 K Posts
- 271 Online
- 7,115 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Comms and power cabling to outside unit
Does anyone know if 1. The comms cable should be 50 m...
By Papahuhu , 49 minutes ago
-
RE: Rate the quality of your heat pump design and installation
I had a Heat Geek lead install by Green Heat Norfolk. T...
By Orlando , 6 hours ago
-
+1 that works well If most of the thermal mass is in ...
By bobflux , 13 hours ago
-
RE: Mitsubishi Ecodan FTC6 settings
While @F1p's dongles are great, the FTC can do this its...
By RobS , 21 hours ago
-
RE: Samsung heat pump - data cable issue
If it's a data cable, current will be minuscule, voltag...
By bobflux , 22 hours ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
I got hit with an RHI audit in 2022. It was far from c...
By Abernyte , 1 day ago
-
RE: Electricity price predictions
@papahuhu Groucho Marx had something to say about no...
By Toodles , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa haha very true, although the engineer yesterda...
By swwils , 1 day ago
-
RE: Vaillant Arotherm Pro vs new Plus
One of the test modes in the installer menu forces it t...
By JamesPa , 2 days ago
-
RE: What a difference a few degrees make.
Wow. Having accepted the challenge, I ran the cold tap ...
By Old_Scientist , 2 days ago
-
RE: HeatPump maintenance in Swindon area?
@vince31 have you tried using our finder:/p>
By Mars , 2 days ago
-
Looking for beta testers for a new homeowner heat pump tool
Over the past few months I've been building a brand new...
By Mars , 2 days ago
-
-
RE: Indevolt Batteries UK Support & Info Thread
It depends on how you configure it via the app. The ma...
By JamesPa , 2 days ago