Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Minimum Run Time, Flow & COP
We have an 11.2KW Ecodan with an FTC6, installed 2022 with a 300l HW tank and 10 circuits of Wundasmart underfloor heating in around 120 sqm, installer (who was generally great) left every circuit thermostatically controlled.
We spent a lot of time learning about the system over the last year, and one quirk of the Ecodan is a minimum run time which it imposes on itself and the impact on flow temperatures. After conversations with Mitsubishi, this is called the Compressor On Guard Strategy, which enforces a 20 minute minimum runtime, unless the Superheat has been >10C for 10 minutes. It took us a long time to find out from Mitsubishi that this existed.
It doesn't matter a lot what the above means, but the effect - a minimum run time - is interesting. Normally if the pump's minimum heat delivery is higher than the demand, then during low flow conditions (e.g. only a few thermostats calling for heat) the flow temp rises and the pump will turn itself off when flow exceeds 5C above the compensation curve set temperature. In our case, with flow around 27C that might be when flow hits 32C, cunsuming around 1KW of energy.
However the Ecodan will prioritise the importance of keeping on running over halting when exceeding the flow temperature, and will keep trying to heat the water while it keeps running. The compressor runs harder and harder as the temp spirals and we were recording 55C flows at which point it turned off. This incurred very high energy consumption (3KW or more).
This had a huge impact on the COP, dropped below 3 during mild weather. During cold weather it's never a problem, there's always enough flow because so many circuits are calling for heat and minimum runtimes are over 20mins anyway.
We contemplated adding a buffer (cost around £1K installed) but instead trialled removing all thermostatic control in all rooms except the coldest one and using full system volume all the time with the compensation curve driving the system. The result in mild weather is dramatic: we can keep flow temps at 23C above 13C outside, the pump cycles twice an hour with max flow never exceeding 5C above set flow temp, Melcloud-reported COP is regularly over 5 and often over 6, it appears to be phenomenally efficient, borne out by much lower daily energy usage in mild weather.
We do have some small challenges with some warmer rooms getting a couple of degrees C above what we'd prefer but it is cheaper to just live with the extra heat, cost goes up if we re-introduce any thermostatically control rooms, because the volume reduced and pump works harder as above. Our Wundasmart manifolds use automatic balancing valves which set the circuit flow dependant on flow/return temps and can't be manually adjusted down, which is an unfortunate side-effect of an automated system.
The lesson learned is that Ecodans and lots of thermostats really don't work well in mild weather and it's much cheaper (and generally nicer) to go to the effort of working out the right compensation curve and running low flow temps against your full system volume.
Might be useful to anyone with an Ecodan, lots of thermostats and seeing big spikes in flow temps and energy consumption several times an hour during mild weather.
Rod
Posted by: @rodMight be useful to anyone with an Ecodan, lots of thermostats and seeing big spikes in flow temps and energy consumption several times an hour during mild weather.
Rod
Welcome to the forum and thank you for the detailed report. I must admit that I was not aware of the Compressor On Guard Strategy, which I don't believe is mentioned in the manual.
Your findings about thermostats is not only relevant to Ecodan owners, but probably all heat pump owners.
Very interesting. My (14kW) ASHP can definitely run the compressor in bursts of less than 20 minutes when in heating mode. It doesn't do it very often and only when in WC mode and mild conditions. It never heats to more than one or two degrees above WC set point though, although I have only two zones, which means the ASHP is heating at least half my house at any one time. Interestingly, although the compressor stops after less than 20 minutes, I don't think it is ever in heating mode for less than 20 minutes. That is, it spends some time in heating mode while delivering no energy.
This is heating you're talking about btw - the label on the graph on your attachment mentions DHW?
I've never heard of Compressor on guard or Superheat; it's not mentioned on the manuals afaik.
@derek-m if you skim through this Samsung doc, you will see details how a double compressor "heat pump"/AC works, some of this data is pointless to anyone but the engineers that need to look(improve/make a new model) at the machine beyond checking the refrigerant charge.
@kev-m Yes, it's in heating mode. For reasons I still don't understand the HP can spin up to do a DHW cycle when the tank temp is very close to setpoint and cut out immediately the set point is reached without entering the On Guard strategy, even if it's only a couple of mins long. Mitsubishi could not explain why the strategy is used for heating but not for water.
This stuff definitely isn't in the manual and isn't generally known to the support teams, it was only when I pressed them that this appeared.
Thanks fazel, much appreciated.
I suspect that the training manual is for industrial type units, since the smallest compressor of a twin compressor unit is rated at roughly 19kW, and each compressor in the main unit is rated at 25kW. I don't think that it would get planning permission. 😋
Nevertheless the manual appears to give a good description of the inner workings of a heat pump, which is very similar, if not exactly the same, as a domestic sized unit.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 291 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 29 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 37 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 13 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 14 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 14 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 17 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 24 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 24 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago