Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan circulation pump
Hi @sunandair , so if I’ve understood correctly, you believe the pump running 24/7 is ok/normal? I’m happy with that, but my only concern is why this would be the case when the outside temperature is ok, say +5, or in summer at +25? The bit I don’t get is why I need to circulate water then as the ashp will be off as room stats won’t call for heating?
it just feels odd that the circulation pump runs 24/7, although I guess the electrical consumption isn’t going to be that high?
on a separate note, please can you help me with setting up the energy consumption and produced data. It show blank at the moment per the photos I posted and I can’t work out how to get that working?
thanks in advance. Adam.
@adamba I don't believe the pump running 24/7 is either normal or desirable but I have not a clue how to stop it when there's no call for heat (CH) or DHW heating.
Someone will need to tell you how to set up consumption and production data I'm afraid. Mine was set up by the installer.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Hi @morgan , I find it a bit strange as this wasn’t the case for my old heat pump that broke beyond repair (apparently, although I think they just wanted to sell me one of their new range).
I’m not sure if we’ve just not installed correctly. Maybe the circulation pump needs to have the same ‘run’ signal as provided to the external ashp?
This would make sense to me as I would think something needs to tell the circulation pump to run (as the ashp needs to be told to run). If it’s not a wiring connection in the Mitsubishi control panel then maybe there is another setting on the keypad?
I’m past my knowledge level though!
Posted by: @adambaHi @sunandair , so if I’ve understood correctly, you believe the pump running 24/7 is ok/normal? I’m happy with that, but my only concern is why this would be the case when the outside temperature is ok, say +5, or in summer at +25? The bit I don’t get is why I need to circulate water then as the ashp will be off as room stats won’t call for heating?
it just feels odd that the circulation pump runs 24/7, although I guess the electrical consumption isn’t going to be that high?
on a separate note, please can you help me with setting up the energy consumption and produced data. It show blank at the moment per the photos I posted and I can’t work out how to get that working?
thanks in advance. Adam.
The wiring diagram I studied recently, shows the main and any auxiliary water pumps wired to the main Mitsubishi control panel. Is that the case with your system?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Hi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
Posted by: @adambaHi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
You are one of the lucky ones to only have the one water pump, which would indicate that you don't have the unnecessary complexity that has been built into other systems. Having just one water pump will not only slightly reduce electricity consumption, it will also mean that you don't have a buffer tank, low loss header or plate heat exchanger installed, any of which can seriously effect overall efficiency.
Obviously, your water pump should operate whenever your heat pump is supplying the central heating or DHW, but may also run - on for a period of time after the heat pump has stopped. There are also settings to periodically run the water pump for a short period of time, even when the heat pump is stopped, to ensure that the water temperature sensors are measuring the average temperature. I will have to look at the manual, but I believe that the water pump can also be set to run continuously.
Posted by: @adambaHi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
The main water pump should be wired to OUT1 on terminal block TBO.1 connections 1 & 2 as shown on page B-46 of the attached manual. I would suggest that you also check the water pump economy setting as shown on page B-70 and the freeze stat setting as mentioned on page B-72.
Posted by: @adambaHi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
You obviously have failed your observancy test, since you failed to notice that I had not attached the referenced manual.
Posted by: @adambaHi @sunandair , so if I’ve understood correctly, you believe the pump running 24/7 is ok/normal?
No, that’s a slightly different slant on what I said. My point was that when you’ve resolved any problems you may have with your system you may find the most energy efficient way to operate your under floor heating is at low temperature with a continuous flow.
Posted by: @sunandairthe most energy efficient way to operate your under floor heating is at low temperature with a continuous flow
I agree that without evidence suggesting otherwise, this is probably the way to go. But this could be a moot point ...
... and likely depends on other factors If you are on economy 7 and have good thermal mass in your UFH you should get 7 hours electricity at 16p and 17 hours at 47p. The CoP needs to be 3 times better during the 17 hours (on average) to justify running it through the 17 hours as well.
Things to consider though
- the heat pump is working much harder at night and running a number of defrost cycles (right now - that should stop at some point in spring)
- there is the cost of wear and tear (which is probably higher at night - due to low outside temp and the higher flow temperatures)
- a yoyo of temperatures (maybe not good for the floor - expand/contract a lot)
- upstairs UFH does not have the same thermal mass as downstairs (can be fixed by zoning)
- option of using solar in the day, if you have it, or battery may offset the costs allowing you to be on a cheaper all day tarrif
I am still trying to work out the best option, since there are some [potential] "costs" that are not that easy to quantify.
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
1 week ago
-
Mitsubishi Ecodan circulation pump running.
2 weeks ago
-
Ecodan Auto Adapt Options
2 weeks ago
-
Ecodan heat pump leak
3 weeks ago
-
Interpreting MelPump data / cycling?
1 month ago
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 456 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago