Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@ngillam No way to control defrost cycle, but that isn't your issue it only increased 5C in 30 mins before the defrost started that isn't normal, its as if you were emptying the tank as it was trying to heat it back up.
@gary That's a good observation on emptying the tank!! I wasn't at home but will check with the other half if she was up earlier than planned. Once again, you're a fountain of knowledge.
Does my flow and return seem nominal to you?
Thanks,
Neil
Flow and return are fine, what isn't is the rate at which it is changing.
If I look at my HW run last night to get from 37C to 42C flow mine took 5 mins yours took 30 mins, hence my comment on was the HW being used at that time, if you have never had an issue before with HW heating up in that time period there is some other factor here. See what happens tomorrow morning I guess
Is this a pump issue? What jumps out at me on the chart at the the time of the defrost cycle is that the return drops dramatically first, and pulls the flow temp down slightly with it. Two minutes later the flow drops right down and only then looks like a normal defrost cycle, but rather than the flow temperature bouncing straight back up at the bottom of the cycle it takes few minutes and in addition the tank cools slightly as the return temp goes up several degrees before the flow temp goes back up. None of that looks normal, but I can't think of an obvious cause. The latter bit looks like the HW pump might be running while the defrost is taking heat out.
I would expect a HW cycle to stop when a defrost is needed (I don't HW at night though) and then just restart. There is meant to be enough volume in the primary circuit to enable defrosts.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
@harriup @gary I really do need some help with this one. It seems my HW never gets up to 47 target now due to defrost cycle running every hour. It gets to 41 or 42 before defrost cycle (the controller shows inverted colour heat pump symbol) which seems to draw down the tank temp to 38ish before defrost cycle ends.
Gary, your comment on slow warm up, yours seems a lot quicker than mine, I have a 5kw but even allowing for your step up in power it still seems very slow. Thinking about it a historical comment of yours mentions enough heat throughout the day. My tank once up to temp seems to dwindle back down quite quickly, it's a pre-plumbed cylinder 210L, I have timers set to 24hrs on pumps and can only think all this is related.
Can I ask what other ECODAN owners have there settings on for defrost and settings for HW duration etc.
My partner went out last night so I had to put the HW on constant to ensure she had hot water for shower, checked in the early hours when she came in and immersion heater had stepped in, disappointing!
Suggestions welcome, it's only 2 degs outside but defrost seems to be really hampering our comfort at present.
Thanks,
Neil.
check what the HW pump is set to on the cylinder it should have 3 positions it should be on 3 which is the highest setting
@gary Yep, it's on 3. Here are the last two hours of info:
Every hour it does this, this is the first winter we've gone through since heat pump installation so first time it's seen these temps.
Thanks,
Neil.
I have two of these in the control room, one looks to be UFH manifold side and the other DHW. I have it set 24hr because if it isn't then outside of times it won't send hot water to taps/showers or bath.
My DHW settings:
Max temp - 47
Drop temp - 7
Max op time - 90mins
Mode Restrict - 55mins
Similar to yours?
Thanks,
Neil.
So it will only run for 90 mins before shutting off and that currently isn’t long enough to reach your set temp
In the HW schedule on the FTC when is that set for? .
Is a pump running constantly if you have that Heatmiser thermostat set to on 24hrs a day?
If so I’m wondering if you are circulating HW round a pipe which would explain why your hot water is losing temp quickly and won’t be helping with the hot water heating up
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 1,956 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Why don't people choose heat pumps?
It's swings and roundabouts - during off-peak periods t...
By Temperature_Gradient , 10 minutes ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 7 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 7 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 7 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 8 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 8 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 11 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 15 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 3 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago