Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Cascade System Problem: DHW Heating Stops UFH & Pool Output
The issue seems to be solved: I found that the plumbers had routed the flow return from ASHP1 into the flow return of ASHP2, hence the whole system was behaving very badly.
I had to get the cascade removed to work it out, as there was only 1 set of thermistors - once the flow and returns of each ASHP could be monitored independently, it was pretty clear that there was a plumbing issue. Now the DHW ASHP is getting its proper flow return, the tank heating time has changed from not always being able to heat to target in 2hrs, to getting to 50 degrees in about 45 minutes!
I think the hardware supplier got the hump when asked to remove the cascade wiring (they took the master controller away...) so don't think I'll be asking for it to be put back in - with matching settings, the two ASHPs seem to be playing nicely, but the pool and pool room rads are not yet connected.
@f1p Indeed - I am just waiting to see if I get sent a bill for removing the cascade, but intend to either ask for a refund, or a return of my property and have it as a cold standby!
The next challenge will be getting 60mCu of water warmed up! - I assume for the initial heating, take the weather compensation off, fix both flow temps to perhaps 40 degrees and run it during the day to maximise efficiency.
Any thoughts on how long that volume of water would take to around 25 degrees?
- 26 Forums
- 2,726 Topics
- 63.9 K Posts
- 683 Online
- 7,131 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Be interesting to see if they quietly allow Lidl's DC c...
By dansus , 7 minutes ago
-
@trebor12345 If you select the Change Rate Plan button,...
By Toodles , 38 minutes ago
-
@grahamh-energy-donkey — thanks for the clarifications....
By cathodeRay , 6 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
A good analysis with which I agree
By JamesPa , 21 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@majordennisbloodnok Well, I can use such terms as HMRC...
By Toodles , 22 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
I'd picked up that there was a leak coming from around ...
By Sheriff Fatman , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Great info. Thank you. Regards Pete
By peterackstraw , 1 day ago
-
-
RE: Microgeneration Certification Scheme (MCS)
@jamespa A cynical view but, I fear that it is a fair ...
By Toodles , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 4 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 5 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 5 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 5 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 5 days ago