DHW heating issue o...
 
Notifications
Clear all

Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

DHW heating issue on Kaisai heat pump

12 Posts
3 Users
7 Reactions
1,267 Views
(@tinsel8152)
Active Member Member
Joined: 10 months ago
Posts: 6
Your energy: 0 kWh
Topic starter   [#2780]

I have an issue with my heat pump, specifically the DHW heating. Now that it is winter and cold time of year, the pump does not have enough power to heat DHW with compressor anymore. I would expect it to use the IBH included that it uses for space heating when it goes too cold but that does not happen. Anyone here able to help out? Maybe something wrong with my settings?

The pump I have is a 14kW Kaisai r32 heat pump which is identical to the midea 14kW pump I have seen discussed here.


This topic was modified 10 months ago by tinsel8152
This topic was modified 10 months ago by Mars

   
Like
1
Quote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5739
Your energy: 73 kWh
 

Sorry to hear this. 

To help with the diagnosis can you describe exactly what you are observing when you say 'it doesnt have enough power' and also tell us about the DHW tank and your DHW settings.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5042
Your energy: 57 kWh
 

Welcome to the forums @tinsel8152.

To help narrow down what might be going on, could you share a bit more detail on your current setup and settings? For example, what temperature are you heating your domestic hot water to, and what are your DHW temperature setpoints?

Irrespective of the current winter temperatures, your heat pump should have no issues getting hot water to 45C without any additional assistance. 

Also, do you know if the backup heater is enabled in the control settings specifically for DHW, or only for space heating? Sometimes the IBH activation logic can be configured separately for DHW and heating circuits.

It would also be useful to know if you’ve checked any error codes or system logs that might indicate why the backup heater isn’t activating.


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
(@tinsel8152)
Active Member Member
Joined: 10 months ago
Posts: 6
Your energy: 0 kWh
Topic starter  

@editor 

I have set the water to heat to 52C. I have a 300 liter tank. Depending on outside temp, the pump heats the DHW to 45C if it is below -10C and 48C if it is between -5C and -10C. 48C is fine for me but 45C is a little too low for a shower.

I did also check the DIP switch setting that I found in the manual that it is set to be valid to use IBH for DHW.

E: I also checked that there are no errors in the logs.


This post was modified 10 months ago by tinsel8152
This post was modified 10 months ago by Mars

   
Hmmm
1
ReplyQuote

JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5739
Your energy: 73 kWh
 

Can you advise if the tank is a 'heat pump' tank, ie one with a large coil (generally 3 sq m).  Do you by any chance know what flow temperature the heat pump reaches and how long is it set to heat for?


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@tinsel8152)
Active Member Member
Joined: 10 months ago
Posts: 6
Your energy: 0 kWh
Topic starter  

@jamespa 

The tank is specifically this one with 3,1 sq m coil: https://www.osohotwater.com/product/oso-delta-geocoil-dgc/

The pump reaches at least a 55C flow temp. Usually I have it set on a timer for a couple hours a day, but lately i have been testing with DHW set on all the time but the pump just stops heating DHW when it reaches above states temps.



   
Like
1
ReplyQuote
(@tinsel8152)
Active Member Member
Joined: 10 months ago
Posts: 6
Your energy: 0 kWh
Topic starter  

 

IMG20260126173054

Here is photo from the controller. Temp is 55C but it did go to 56C for a bit too.


This post was modified 10 months ago by tinsel8152

   
Like
1
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5739
Your energy: 73 kWh
 

Posted by: @tinsel8152
↑

Here is photo from the controller. Temp is 55C but it did go to 56C for a bit too.

With an LW of 55 you will struggle to get to 52, but you should get to 48 I would have thought.  Does your heat pump allow you to increase the max lwt for dhw?

The other factor to bear in mind is that to heat 300l of water from 10 to 50 takes 2.5 hours with a 6 kW pump, are you heating for long enough?

How far is the cylinder from the heat pump and how well insulated is the route.  Could the water be cooling between heat pump and cylinde


This post was modified 10 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote

(@tinsel8152)
Active Member Member
Joined: 10 months ago
Posts: 6
Your energy: 0 kWh
Topic starter  

@jamespa Yesterday when I took that photo I got to precisely 48C and then the pump just stopped again even if I disable space heating and only DHW is turned on. I tried later with set temp 60C and there was no difference. As I said earlier depending on outside temp, the pump heats the DHW to 45C if it is below -10C and 48C if it is between -5C and -10C.

I don't heat from 10 degrees. I have the cold water coming to the tank going through a coil in my "buffer tank" for preheating. That way the water going to the tank is closer to the temp I use for space heating, which is 40C if it is -10 outside. 

The tank is right next to the pump so distance should not be an issue here. Insulating could be better still, only the outside connection part is insulated at the moment.

 



   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5739
Your energy: 73 kWh
 

OK, I’m a bit baffled.  Does it switch off after a certain time or when the flow temperature reaches a certain value? Some heat pumps have a 'max DHW heating time' feature to ensure space heating isnt turned off for too long.  Could be that? 

When you say the tank is right next to the pump, is the 'pump' the heat pump- it is the temperature of the flow from the heat pump that I was concerned about when I asked about insulation.

Apart from the above I cant immediately think of an explanation and without further data doubt I will come up with anything.  You may need to log times and flow temperature to get to the bottom of this, unless it’s some simple setting somewhere buried in the installer menu!  Maybe someone else has an idea.  I would say that it feels like the system is 'marginal' (rather than catastrophically faulty) so its probably that something, somewhere, isnt quite getting hot enough for long enough but what exactly is difficult to tell.  If you can somehow turn up the LWT for DHW that may fix it (R32 should be capable of 60-65), but it is also possible that the capacity of the heat pump at -10 isn’t sufficient (do you have the capacity tables/specifications?)


This post was modified 10 months ago by Mars

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
Like
1
ReplyQuote
(@tinsel8152)
Active Member Member
Joined: 10 months ago
Posts: 6
Your energy: 0 kWh
Topic starter  

@jamespa 

It switches off based on the temp in the tank. So yesterday when it was -8C outside it switched off when the tank reached 48C. Didn't matter if it was set at 52C or 60C. Flow temp reached 55-56C both times. 

I found in the settings a t_DHWHP_MAX setting(the maximum continuous working period of the heat pump in DHW PRIORITY mode.) that is set at 90 minutes, but it stops much sooner than that.

Posted by: @jamespa
↑

Posted by: @tinsel8152
↑

When you say the tank is right next to the pump, is the 'pump' the heat pump- it is the temperature of the flow from the heat pump that I was concerned about when I asked about insulation.

Yeah, it is the heat pump indeed what I mean here. There is only a wall separating them.

I'm thinking it is a setting buried somewhere, that's just hard to figure out with the documentation not telling what all the settings even mean.

Here is the capacity table. Around 9kW heating capacity at -10C i think should be enough.

image

This post was modified 10 months ago by tinsel8152
This post was modified 10 months ago by Mars

   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5739
Your energy: 73 kWh
 

Posted by: @tinsel8152
↑

It switches off based on the temp in the tank. So yesterday when it was -8C outside it switched off when the tank reached 48C. Didn't matter if it was set at 52C or 60C. Flow temp reached 55-56C both times

That cant be precisely true if, as you say, the temperature the tank reaches depends on the outside temperature.

According to the table the capacity at -10/60 is only 6k.7W.  That should still be enough!

 

Posted by: @tinsel8152
↑

I'm thinking it is a setting buried somewhere, that's just hard to figure out with the documentation not telling what all the settings even mean.

Im inclined to agree.  Possibly some minimum delta between flow and return or between flow and tank temp?

Ive just looked back to your first post and you suggest that the situation has changed (you use the work anymore).  If so then perhaps a sensor has moved?

Measurements and observations, plus going through the menu, is the only way to track this down I fear.  Sorry I couldn't be more helpful.

 