Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
DHW heating issue on Kaisai heat pump
I have an issue with my heat pump, specifically the DHW heating. Now that it is winter and cold time of year, the pump does not have enough power to heat DHW with compressor anymore. I would expect it to use the IBH included that it uses for space heating when it goes too cold but that does not happen. Anyone here able to help out? Maybe something wrong with my settings?
The pump I have is a 14kW Kaisai r32 heat pump which is identical to the midea 14kW pump I have seen discussed here.
Sorry to hear this.
To help with the diagnosis can you describe exactly what you are observing when you say 'it doesnt have enough power' and also tell us about the DHW tank and your DHW settings.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Welcome to the forums @tinsel8152.
To help narrow down what might be going on, could you share a bit more detail on your current setup and settings? For example, what temperature are you heating your domestic hot water to, and what are your DHW temperature setpoints?
Irrespective of the current winter temperatures, your heat pump should have no issues getting hot water to 45C without any additional assistance.
Also, do you know if the backup heater is enabled in the control settings specifically for DHW, or only for space heating? Sometimes the IBH activation logic can be configured separately for DHW and heating circuits.
It would also be useful to know if you’ve checked any error codes or system logs that might indicate why the backup heater isn’t activating.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
I have set the water to heat to 52C. I have a 300 liter tank. Depending on outside temp, the pump heats the DHW to 45C if it is below -10C and 48C if it is between -5C and -10C. 48C is fine for me but 45C is a little too low for a shower.
I did also check the DIP switch setting that I found in the manual that it is set to be valid to use IBH for DHW.
E: I also checked that there are no errors in the logs.
Can you advise if the tank is a 'heat pump' tank, ie one with a large coil (generally 3 sq m). Do you by any chance know what flow temperature the heat pump reaches and how long is it set to heat for?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The tank is specifically this one with 3,1 sq m coil: https://www.osohotwater.com/product/oso-delta-geocoil-dgc/
The pump reaches at least a 55C flow temp. Usually I have it set on a timer for a couple hours a day, but lately i have been testing with DHW set on all the time but the pump just stops heating DHW when it reaches above states temps.
Posted by: @tinsel8152Here is photo from the controller. Temp is 55C but it did go to 56C for a bit too.
With an LW of 55 you will struggle to get to 52, but you should get to 48 I would have thought. Does your heat pump allow you to increase the max lwt for dhw?
The other factor to bear in mind is that to heat 300l of water from 10 to 50 takes 2.5 hours with a 6 kW pump, are you heating for long enough?
How far is the cylinder from the heat pump and how well insulated is the route. Could the water be cooling between heat pump and cylinde
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Yesterday when I took that photo I got to precisely 48C and then the pump just stopped again even if I disable space heating and only DHW is turned on. I tried later with set temp 60C and there was no difference. As I said earlier depending on outside temp, the pump heats the DHW to 45C if it is below -10C and 48C if it is between -5C and -10C.
I don't heat from 10 degrees. I have the cold water coming to the tank going through a coil in my "buffer tank" for preheating. That way the water going to the tank is closer to the temp I use for space heating, which is 40C if it is -10 outside.
The tank is right next to the pump so distance should not be an issue here. Insulating could be better still, only the outside connection part is insulated at the moment.
OK, I’m a bit baffled. Does it switch off after a certain time or when the flow temperature reaches a certain value? Some heat pumps have a 'max DHW heating time' feature to ensure space heating isnt turned off for too long. Could be that?
When you say the tank is right next to the pump, is the 'pump' the heat pump- it is the temperature of the flow from the heat pump that I was concerned about when I asked about insulation.
Apart from the above I cant immediately think of an explanation and without further data doubt I will come up with anything. You may need to log times and flow temperature to get to the bottom of this, unless it’s some simple setting somewhere buried in the installer menu! Maybe someone else has an idea. I would say that it feels like the system is 'marginal' (rather than catastrophically faulty) so its probably that something, somewhere, isnt quite getting hot enough for long enough but what exactly is difficult to tell. If you can somehow turn up the LWT for DHW that may fix it (R32 should be capable of 60-65), but it is also possible that the capacity of the heat pump at -10 isn’t sufficient (do you have the capacity tables/specifications?)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
It switches off based on the temp in the tank. So yesterday when it was -8C outside it switched off when the tank reached 48C. Didn't matter if it was set at 52C or 60C. Flow temp reached 55-56C both times.
I found in the settings a t_DHWHP_MAX setting(the maximum continuous working period of the heat pump in DHW PRIORITY mode.) that is set at 90 minutes, but it stops much sooner than that.
Posted by: @jamespaPosted by: @tinsel8152When you say the tank is right next to the pump, is the 'pump' the heat pump- it is the temperature of the flow from the heat pump that I was concerned about when I asked about insulation.
Yeah, it is the heat pump indeed what I mean here. There is only a wall separating them.
I'm thinking it is a setting buried somewhere, that's just hard to figure out with the documentation not telling what all the settings even mean.
Here is the capacity table. Around 9kW heating capacity at -10C i think should be enough.
Posted by: @tinsel8152It switches off based on the temp in the tank. So yesterday when it was -8C outside it switched off when the tank reached 48C. Didn't matter if it was set at 52C or 60C. Flow temp reached 55-56C both times
That cant be precisely true if, as you say, the temperature the tank reaches depends on the outside temperature.
According to the table the capacity at -10/60 is only 6k.7W. That should still be enough!
Posted by: @tinsel8152I'm thinking it is a setting buried somewhere, that's just hard to figure out with the documentation not telling what all the settings even mean.
Im inclined to agree. Possibly some minimum delta between flow and return or between flow and tank temp?
Ive just looked back to your first post and you suggest that the situation has changed (you use the work anymore). If so then perhaps a sensor has moved?
Measurements and observations, plus going through the menu, is the only way to track this down I fear. Sorry I couldn't be more helpful.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 314 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago