Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Cooling with Samsung Gen6 and Flow error

5 Posts
2 Users
0 Reactions
744 Views
(@ecobaker)
Trusted Member Member
Joined: 2 years ago
Posts: 45
Topic starter   [#2389]

HI

I've got a Samsung gen6 ASHP, which I am trying to use for cooling. I have a large Harnitek fan assisted radiator in my main living room. Whenever I put the cooling on after about an 40 mins I get the e911 flow error. 

I've checked the flow sensor its working fine, and on a cooler day a few weeks ago I put the heating on for a couple of hours and it works fine. So is this a pump problem, is it struggling due to the cold water and increase viscosity, thus can't pump it round effectively. Maybe a pump with bigger head would help?

Any thoughts would be much appreciated?


Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
Quote
(@iaack)
Trusted Member Member
Joined: 3 years ago
Posts: 59
 

I see that these fan coil radiators either come with a two-way or three-way control valve  built into them. What does the valve do? Well from a quick read of yhe operator instructions, it appears the control board can close off the valve in certain preset conditions (e.g. timer mode). 

I suggest you look into your fan coil units (radiator) operator parameters to see what the current settings are. I take it that you are selecting cooling mode on the radiator as well as the ashp?


This post was modified 9 months ago by IaAck

   
ReplyQuote
(@ecobaker)
Trusted Member Member
Joined: 2 years ago
Posts: 45
Topic starter  

@iaack I've got cooling mode on the radiator selected, and I've disabled the valve mode on it, so they are open all the time.


Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
ReplyQuote



(@iaack)
Trusted Member Member
Joined: 3 years ago
Posts: 59
 

@ecobaker I'm still thinking that something is triggering the valve to close.

In cooling mode on the rad, what are you setting as the rad target temperature? What is the typical room temperature and water flow temp. when the problem occurs?

Is the condensate outlet clear? Air cond units have float switches to monitor the condensate level and can shutdown the cooling function if they detect an unusual rise in condensate level. 



   
ReplyQuote
(@ecobaker)
Trusted Member Member
Joined: 2 years ago
Posts: 45
Topic starter  

@iaack The system isnt running long enough for any condensation buildup, also I've got the flow temp set above the current due point temp. I don't think its the radiator


Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.


   
ReplyQuote