@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?
I believe so, we are looking for difference so as long as you can clamp consistently then it doesn't matter if the figure isn't perfect.
I stress there is absolutely no need to do this unless you want to.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Borrowed a clamp on thermometer.
Buffer tank: PAW-BTANK50L-2 buffer tank
Only 48l
According to ashp controls
leaving temp 33deg
Return 31 deg
Arr from ashp BT 34.4flow
Leave BT 34.1 flow
Arr from house BT 33.2 return
Leave 33.8 BT return
I suspect not great test right now... as mild... so not working hard
Will be better to check on cold morning.. perhaps.
Will report again once more results
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 the other thing to “check” is where the respective flow and returns are to see if your buffer has minimal distortion. Ideally, it’s plumbed like this:
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?
With the pump on right on flow from BT?
Tap at bottom right ... return to BT?
So same as your diagram. but I'll try the thermometer a few times in different scenarios
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?
Is it a 2 way valve or a 3 way diverter valve. Normally the (3 way) diverter valve is the only motorised valve needed.
As you say taking some temperature measurements when its working harder would be good, but your initial ones are encouraging.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa it's 3 way
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@jamespa it's 3 way
I presume the diverter valve then, which would make sense. As you say you would expect this to be on the inlet to the BT
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi, so if I wanted to make my system more efficient, It's open loop 28/22/15mm ,all rads,run via a Homely is it possible to remove the buffer tank but still comply with 7-year LG warranty requiring hydraulic separation. Thanks
@potatoman can you share LG's official documentation that explicitly requires hydraulic separation to maintain the 7-year warranty?
If you've got that document, it would be extremely valuable to see it.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
To me that reads as 'Hydraulic separation optional but if present covered for 7 years if you take out the extended warranty', as opposed to 'Hydraulic separation mandatory'. The very last line in the table (mag filter) would seem to confirm this.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
British Gas Heat Pump Installation Complaint
4 months ago
-
Heating Turned Off but Radiators Still Warm
4 months ago
-
Samsung Heat pump with Yonos Pico circulating pump running all the time
4 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
5 months ago
-
Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
1 year ago
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 259 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 12 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 23 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 2 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 18 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 23 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 24 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago