Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency

224 Posts
28 Users
108 Reactions
17.1 K Views
(@tim441)
Honorable Member Contributor
2233 kWhs
Joined: 2 years ago
Posts: 265
 

@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10760 kWhs
Veteran
Joined: 2 years ago
Posts: 2030
 

Posted by: @tim441

@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?

I believe so, we are looking for difference so as long as you can clamp consistently then it doesn't matter if the figure isn't perfect.

I stress there is absolutely no need to do this unless you want to.

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
2
ReplyQuote
(@tim441)
Honorable Member Contributor
2233 kWhs
Joined: 2 years ago
Posts: 265
 

Borrowed a clamp on thermometer. 

Buffer tank:  PAW-BTANK50L-2 buffer tank
Only 48l
According to ashp controls
leaving temp 33deg
Return 31 deg

Arr from ashp BT 34.4flow
Leave BT 34.1 flow

Arr from house BT 33.2 return
Leave 33.8 BT return

I suspect not great test right now... as mild... so not working hard
Will be better to check on cold morning.. perhaps.

Will report again once more results

This post was modified 3 weeks ago by Tim441

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
26270 kWhs
Veteran
Joined: 4 years ago
Posts: 2983
Topic starter  

@tim441 the other thing to “check” is where the respective flow and returns are to see if your buffer has minimal distortion. Ideally, it’s plumbed like this:

buffer

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
👍
1
ReplyQuote
(@tim441)
Honorable Member Contributor
2233 kWhs
Joined: 2 years ago
Posts: 265
 

@editor 

Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?

With the pump on right on flow from BT?

Tap at bottom right ... return to BT?

So same as your diagram. but I'll try the thermometer a few times in different scenarios

20250220 135539

 

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10760 kWhs
Veteran
Joined: 2 years ago
Posts: 2030
 

Posted by: @tim441

Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?

Is it a 2 way valve or a 3 way diverter valve.  Normally the (3 way) diverter valve is the only motorised valve needed.

As you say taking some temperature measurements when its working harder would be good, but your initial ones are encouraging.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@tim441)
Honorable Member Contributor
2233 kWhs
Joined: 2 years ago
Posts: 265
 

@jamespa it's 3 way

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10760 kWhs
Veteran
Joined: 2 years ago
Posts: 2030
 

Posted by: @tim441

@jamespa it's 3 way

I presume the diverter valve then, which would make sense.  As you say you would expect this to be on the inlet to the BT

 

This post was modified 2 weeks ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
Page 19 / 19
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security