Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency

245 Posts
29 Users
111 Reactions
18.4 K Views
(@tim441)
Prominent Member Contributor
Joined: 2 years ago
Posts: 281
 

@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2313
 

Posted by: @tim441

@jamespa measuring with clamp-on heating pipe thermometer? I see ebay/amazon has them around £6 or £7 .. Good enough?

I believe so, we are looking for difference so as long as you can clamp consistently then it doesn't matter if the figure isn't perfect.

I stress there is absolutely no need to do this unless you want to.

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
2
ReplyQuote
(@tim441)
Prominent Member Contributor
Joined: 2 years ago
Posts: 281
 

Borrowed a clamp on thermometer. 

Buffer tank:  PAW-BTANK50L-2 buffer tank
Only 48l
According to ashp controls
leaving temp 33deg
Return 31 deg

Arr from ashp BT 34.4flow
Leave BT 34.1 flow

Arr from house BT 33.2 return
Leave 33.8 BT return

I suspect not great test right now... as mild... so not working hard
Will be better to check on cold morning.. perhaps.

Will report again once more results

This post was modified 2 months ago by Tim441

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 4 years ago
Posts: 3111
Topic starter  

@tim441 the other thing to “check” is where the respective flow and returns are to see if your buffer has minimal distortion. Ideally, it’s plumbed like this:

buffer

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
👍
1
ReplyQuote
(@tim441)
Prominent Member Contributor
Joined: 2 years ago
Posts: 281
 

@editor 

Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?

With the pump on right on flow from BT?

Tap at bottom right ... return to BT?

So same as your diagram. but I'll try the thermometer a few times in different scenarios

20250220 135539

 

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2313
 

Posted by: @tim441

Logically the electronic motorised valve.. I think... stops buffer being used when heating DHW/hot water tank. So will be on flow to BT?

Is it a 2 way valve or a 3 way diverter valve.  Normally the (3 way) diverter valve is the only motorised valve needed.

As you say taking some temperature measurements when its working harder would be good, but your initial ones are encouraging.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote



(@tim441)
Prominent Member Contributor
Joined: 2 years ago
Posts: 281
 

@jamespa it's 3 way

Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2313
 

Posted by: @tim441

@jamespa it's 3 way

I presume the diverter valve then, which would make sense.  As you say you would expect this to be on the inlet to the BT

 

This post was modified 2 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@potatoman)
Estimable Member Member
Joined: 1 year ago
Posts: 53
 

Hi, so if I wanted to make my system more efficient, It's open loop 28/22/15mm ,all rads,run via a Homely is it possible to remove the buffer tank but still comply with 7-year LG warranty requiring hydraulic separation. Thanks


   
👍
1
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 4 years ago
Posts: 3111
Topic starter  

@potatoman can you share LG's official documentation that explicitly requires hydraulic separation to maintain the 7-year warranty?

If you've got that document, it would be extremely valuable to see it.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@potatoman)
Estimable Member Member
Joined: 1 year ago
Posts: 53
 

@editor

487221638 10163211903663552 6665514382284125271 n

Regards


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2313
 

To me that reads as 'Hydraulic separation optional but if present covered for 7 years if you take out the extended warranty', as opposed to 'Hydraulic separation mandatory'.  The very last line in the table (mag filter) would seem to confirm this.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote



Page 19 / 21



Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security