Advice on ball park radiator sizes please
Posted by: @derek-mI'm afraid that I do not follow your logic, since heat loss is heat loss and is not dictated by the radiator size or type. Different size or type of radiators will merely require a higher or lower water temperature so that the thermal energy output matches the present heat loss.
Sorry, I obviously didn’t explain that very well, and wrong to boot. As you say, the room/house heat loss is fixed and determined by the fabric and outside temperature, etc. the radiators would then be chosen to provide that output at the desired flow temperature and flow rate, again as you state. I was speculating that the values might be for the standard 50C but without checking the actual radiator specifications and so misled myself on the figures, the Stelrad k3 700x2000 for instance looks like it outputs 5424W at delta-t 50 according to the data sheet, which is considerably higher than the values given. Please ignore my mistaken intrusion.
Thank you all - so grateful for your advice.
I went back to the company, and they forwarded my query to another branch (the original person being away for 3 weeks). The person there confirmed there was an error - apparently the original guy had read the wrong column of figures or something...
So I now have a revised set of sizes, which are much closer to what I anticipated:
|
Room |
Watts required |
Suggested radiator |
Radiator type |
|
|
|
|
|
|
|
|
Living room |
|
|
|
UFH |
|
Shower room |
|
|
|
|
|
Kitchen |
|
|
|
|
|
Dining hall |
|
|
|
|
|
Hall |
|
|
|
|
|
Landing (1st floor) |
700 |
600x600 |
K2 |
|
|
Study |
1050 |
600x600 |
K2 |
|
|
Sitting room |
1600 |
600x1000 |
K2 |
|
|
Bed 1 |
1500 |
600x1000 |
K2 |
|
|
Bed 2 |
1600 |
600x1000 |
K2 |
|
|
Bed 3 |
1550 |
600x1000 |
K2 |
|
|
Landing (2nd floor |
700 |
600x600 |
K2 |
Somewhat different to the originals!
I would suggest that you ask the company to provide a full set of heat loss calculations for your home. Also ask them to clarify what is meant by 'Watts required' in the table, and to confirm their calculated Leaving Water Temperature (LWT) coming from the heat pump.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 230 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Advice on internal circulation pump noise
Welcome and I am sorry you are having this problem. &...
By JamesPa , 5 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@harrisonc mine has level 3 MID monitoring and you can ...
By swwils , 7 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair, in short, no, increasing emitter capacity wo...
By Mars , 8 hours ago
-
RE: Setback savings - fact or fiction?
Hi @cathoderay - this is a good discussion! I feel like...
By RobS , 9 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona happy to help as much as I can if you decide t...
By bontwoody , 9 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
I'll be honest, I love that idea! I'll start working on...
By Mars , 9 hours ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 11 hours ago
-
RE: External pipework insulation
I don't think we can tell from a photo whether your exi...
By Transparent , 11 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
@majordennisbloodnok That’s correct. I can’t find anywh...
By weoleyric , 17 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 2 days ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 2 days ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 2 days ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 2 days ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 2 days ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 3 days ago