Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Advice on ball park radiator sizes please
Posted by: @derek-mI'm afraid that I do not follow your logic, since heat loss is heat loss and is not dictated by the radiator size or type. Different size or type of radiators will merely require a higher or lower water temperature so that the thermal energy output matches the present heat loss.
Sorry, I obviously didn’t explain that very well, and wrong to boot. As you say, the room/house heat loss is fixed and determined by the fabric and outside temperature, etc. the radiators would then be chosen to provide that output at the desired flow temperature and flow rate, again as you state. I was speculating that the values might be for the standard 50C but without checking the actual radiator specifications and so misled myself on the figures, the Stelrad k3 700x2000 for instance looks like it outputs 5424W at delta-t 50 according to the data sheet, which is considerably higher than the values given. Please ignore my mistaken intrusion.
Thank you all - so grateful for your advice.
I went back to the company, and they forwarded my query to another branch (the original person being away for 3 weeks). The person there confirmed there was an error - apparently the original guy had read the wrong column of figures or something...
So I now have a revised set of sizes, which are much closer to what I anticipated:
|
Room |
Watts required |
Suggested radiator |
Radiator type |
|
|
|
|
|
|
|
|
Living room |
|
|
|
UFH |
|
Shower room |
|
|
|
|
|
Kitchen |
|
|
|
|
|
Dining hall |
|
|
|
|
|
Hall |
|
|
|
|
|
Landing (1st floor) |
700 |
600x600 |
K2 |
|
|
Study |
1050 |
600x600 |
K2 |
|
|
Sitting room |
1600 |
600x1000 |
K2 |
|
|
Bed 1 |
1500 |
600x1000 |
K2 |
|
|
Bed 2 |
1600 |
600x1000 |
K2 |
|
|
Bed 3 |
1550 |
600x1000 |
K2 |
|
|
Landing (2nd floor |
700 |
600x600 |
K2 |
Somewhat different to the originals!
I would suggest that you ask the company to provide a full set of heat loss calculations for your home. Also ask them to clarify what is meant by 'Watts required' in the table, and to confirm their calculated Leaving Water Temperature (LWT) coming from the heat pump.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 280 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 4 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 5 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 7 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 8 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 9 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 10 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 10 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 11 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 13 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 14 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 15 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 16 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 16 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 17 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago