Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Advice on ball park radiator sizes please
Posted by: @derek-mI'm afraid that I do not follow your logic, since heat loss is heat loss and is not dictated by the radiator size or type. Different size or type of radiators will merely require a higher or lower water temperature so that the thermal energy output matches the present heat loss.
Sorry, I obviously didn’t explain that very well, and wrong to boot. As you say, the room/house heat loss is fixed and determined by the fabric and outside temperature, etc. the radiators would then be chosen to provide that output at the desired flow temperature and flow rate, again as you state. I was speculating that the values might be for the standard 50C but without checking the actual radiator specifications and so misled myself on the figures, the Stelrad k3 700x2000 for instance looks like it outputs 5424W at delta-t 50 according to the data sheet, which is considerably higher than the values given. Please ignore my mistaken intrusion.
Thank you all - so grateful for your advice.
I went back to the company, and they forwarded my query to another branch (the original person being away for 3 weeks). The person there confirmed there was an error - apparently the original guy had read the wrong column of figures or something...
So I now have a revised set of sizes, which are much closer to what I anticipated:
|
Room |
Watts required |
Suggested radiator |
Radiator type |
|
|
|
|
|
|
|
|
Living room |
|
|
|
UFH |
|
Shower room |
|
|
|
|
|
Kitchen |
|
|
|
|
|
Dining hall |
|
|
|
|
|
Hall |
|
|
|
|
|
Landing (1st floor) |
700 |
600x600 |
K2 |
|
|
Study |
1050 |
600x600 |
K2 |
|
|
Sitting room |
1600 |
600x1000 |
K2 |
|
|
Bed 1 |
1500 |
600x1000 |
K2 |
|
|
Bed 2 |
1600 |
600x1000 |
K2 |
|
|
Bed 3 |
1550 |
600x1000 |
K2 |
|
|
Landing (2nd floor |
700 |
600x600 |
K2 |
Somewhat different to the originals!
I would suggest that you ask the company to provide a full set of heat loss calculations for your home. Also ask them to clarify what is meant by 'Watts required' in the table, and to confirm their calculated Leaving Water Temperature (LWT) coming from the heat pump.
- 26 Forums
- 2,689 Topics
- 63.1 K Posts
- 643 Online
- 7,099 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
You guys have it easy It's engineering: calories in...
By bobflux , 5 hours ago
-
RE: Moving growatt axe batteries
@etchedpixels just been informed that you can’t have ba...
By David999 , 6 hours ago
-
RE: Anyone have experience with Daikin Multi+ for air to air & hot water?
Maybe, just maybe, if you are prepared to leave the doo...
By JamesPa , 6 hours ago
-
RE: How to heat a bathroom when using an air to air heat pump?
You can air/air a bathroom with a suitable ceiling or o...
By EtchedPixels , 6 hours ago
-
RE: Plug and play solar. Thoughts?
They've been extensively tested by folks like the Germa...
By EtchedPixels , 6 hours ago
-
RE: How do I set up Tesla Powerwall export for saving sessions since AI Takeover?
@papahuhu The decision as I say, was influenced very he...
By Toodles , 10 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
A summary of this history and discussion for those sear...
By Tim441 , 15 hours ago
-
RE: Electricity price predictions
@majordennisbloodnok Similar, although no heat pump h...
By IanMK13 , 18 hours ago
-
RE: vaillant arotherm plus - Failure - DHW
As expected it failed to run late yesterday with the sa...
By trebor12345 , 19 hours ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
Personally, I don't always rate the "payback on install...
By HeatNoob , 1 day ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thanks. Will be sure to keep a record of s...
By bontwoody , 1 day ago
-
@jamespa Well, something along the lines of "three buse...
By ian33a , 1 day ago