Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Advice on ball park radiator sizes please
Posted by: @derek-mI'm afraid that I do not follow your logic, since heat loss is heat loss and is not dictated by the radiator size or type. Different size or type of radiators will merely require a higher or lower water temperature so that the thermal energy output matches the present heat loss.
Sorry, I obviously didn’t explain that very well, and wrong to boot. As you say, the room/house heat loss is fixed and determined by the fabric and outside temperature, etc. the radiators would then be chosen to provide that output at the desired flow temperature and flow rate, again as you state. I was speculating that the values might be for the standard 50C but without checking the actual radiator specifications and so misled myself on the figures, the Stelrad k3 700x2000 for instance looks like it outputs 5424W at delta-t 50 according to the data sheet, which is considerably higher than the values given. Please ignore my mistaken intrusion.
Thank you all - so grateful for your advice.
I went back to the company, and they forwarded my query to another branch (the original person being away for 3 weeks). The person there confirmed there was an error - apparently the original guy had read the wrong column of figures or something...
So I now have a revised set of sizes, which are much closer to what I anticipated:
|
Room |
Watts required |
Suggested radiator |
Radiator type |
|
|
|
|
|
|
|
|
Living room |
|
|
|
UFH |
|
Shower room |
|
|
|
|
|
Kitchen |
|
|
|
|
|
Dining hall |
|
|
|
|
|
Hall |
|
|
|
|
|
Landing (1st floor) |
700 |
600x600 |
K2 |
|
|
Study |
1050 |
600x600 |
K2 |
|
|
Sitting room |
1600 |
600x1000 |
K2 |
|
|
Bed 1 |
1500 |
600x1000 |
K2 |
|
|
Bed 2 |
1600 |
600x1000 |
K2 |
|
|
Bed 3 |
1550 |
600x1000 |
K2 |
|
|
Landing (2nd floor |
700 |
600x600 |
K2 |
Somewhat different to the originals!
I would suggest that you ask the company to provide a full set of heat loss calculations for your home. Also ask them to clarify what is meant by 'Watts required' in the table, and to confirm their calculated Leaving Water Temperature (LWT) coming from the heat pump.
- 27 Forums
- 2,815 Topics
- 66.7 K Posts
- 4,762 Online
- 7,230 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
-
@batpred The Daikin temperature probe protrudes from th...
By Toodles , 1 hour ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor And as an occasional contributor, may I say wel...
By Toodles , 3 hours ago
-
RE: Should Households Who Can Afford It Pay More for Energy to Help Those Who Can't?
They don't have to try. Our entire system is d...
By EtchedPixels , 4 hours ago
-
RE: Why don't people choose heat pumps?
Fair enough. I guess I was thinking of pipes that run ...
By JamesPa , 4 hours ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
Got excepted for the grant now so thanks for the replie...
By Chilli304 , 8 hours ago
-
Daikin Altherma 3 R F+W, room thermostat control, weath...
By JanHarley , 9 hours ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
Pretty much as I had guessed in my crude scaling from m...
By JamesPa , 12 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Well you have a vibration generator running at some fre...
By bobflux , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@downfield Thats a decent rate, I’m shocked they hadn...
By Papahuhu , 2 days ago
-
RE: Adventures in heat loss calculations
@toodles thanks! So as suspected, around a doubling of ...
By SusannaSaunders , 2 days ago
-
Six books in three years and I think I’ve now covered j...
By Mars , 2 days ago
-
RE: Grant Aerona3 13kw - Buffer Tank - Heating Journey
@heymikey Well done in achieving as nearer a match acro...
By Toodles , 2 days ago
-
Grant Aerona - Weather Compensation and Schedules
Im trying to set up a friends Grant Aerona. The WC curv...
By bontwoody , 3 days ago