Advice needed on hybrid system - ASHP not reaching flow temperature
Hi, hope you’re all keeping well.
We had a Mitsubishi 11kw ASHP installed a month or so ago and we struggled to heat our house during the last cold snap we had. We made the decision to install a gas boiler alongside the ASHP to run on the colder days. Looking at the charts the specified flow temp of 50c for space heating has never been reached, it gets to around 45 degrees. The pipe runs are all insulated and i have even increased the compensation curve to the maximum. The flow temp for the hot water seems to reach 60 degrees but it doesn’t on the space heating side. I have attached a diagram of our setup at the moment. Please note that the gas boiler isn’t yet up and running as we are waiting on a sensor from Mitsubishi.
Thanks in advance.
Is it the radiator side of the LLH that's not reaching temperature? Or does the heat pump monitoring show it's not achieving 50degC supply temperature? It clearly can if you're getting 60degC on your hot water, so if the primary side isn't allowing 50degC in heating, I guess some setting or parameter is overriding your climatic curve setting.
But if you're getting 50degC on the primary side and not getting that on the secondary side, the finger of suspicion points at the LLH?
Have you got balanced even flow on primary and secondary sides? Higher flow on the secondary radiator side compared to the primary side will pull return water through the LLH, mix with the higher temperature flow from the ASHP, and cause a lower radiator supply temperature.
If you've not got flow valves on both sides to balance flow, you can do it thermally with some temperature sensors. These are cheap and cheerful, and when cable tied to the copper pipe under insulation will give a reasonable indication of what's what +/-0.5degC or so. https://www.amazon.co.uk/dp/B07TY6HRL4?psc=1&ref=ppx_yo2ov_dt_b_product_details
Thanks for getting back to me ally - I am not sure where the thermistors are which are giving me the readings on the melcloud app.
there doesn’t appear to be any balancing valves installed.
all I know is that the flow temps are showing around 45c on the app despite it been set to 50c on the comp curve. Does the piping layout look ok to you from my diagram?
do you think it could be a setting on the controller somewhere?
worthwhile mentioning that there is a pipe run of around 15m from the ASHP to the llh around 10m of this is outdoors
There is a setting on the Ecodan FTC to limit flow temp. I know because I lowered mine a few days ago. It's in the maintenance menu, Operation Settings, Heating Operation, Flow Temperature Range. In case you don't know, pass key is (probably) 0000 and it'll ask you to shut the system down (which is fine as it will start when you exit).
My flow thermistors are physically just above my (non-Mitsubishi) HW tank. The sensors are attached to the flow and return copper pipes like those on Ally's thermometers and the other end disappears into the FTC.
@parmstar Great, les us know how you get on. Piping on your circuit is simple enough, and with a hybrid bivalent system I can see the LLH being of benefit. I would suggest flow monitoring/setting valves on both primary circuits, one on the ASHP return, one on the boiler return, and one on the secondary flow return. They all need to be in balance. Fired boiler design flow might be lower than ASHP design flow, but I guess you've considered that and how to handle that.
- 27 Forums
- 2,433 Topics
- 55.3 K Posts
- 204 Online
- 6,118 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help needed with Grant Aerona 3 issues
Just to update the thread, I now have a new heat pump!!...
By fleurcules , 1 hour ago
-
RE: Is it normal to use power from the grid when running off the battery?
Well, the Huawei CT clamps I have are 100amp and 230V. ...
By Batpred , 4 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor condensate drain worries me, Ive wondered why t...
By Papahuhu , 5 hours ago
-
RE: A Smarter Smart Controller from Homely?
@johnnyb I think so. It’s a UPM4xL that takes its sp...
By Papahuhu , 6 hours ago
-
RE: A Single Voice for Heat Pumps, But Will It Finally Raise Industry Standards?
Great question - I don't know for sure, but I would ass...
By Mars , 7 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Actually, I came across the list of batteries that this...
By Batpred , 7 hours ago
-
RE: Say hello and introduce yourself
Hi all, my name is Julian, and I’m new to the forum. We...
By JLeyland , 8 hours ago
-
RE: Heat pump not reaching flow temperature
@davec that's good news! Thanks for sharing Dave.
By johnd , 9 hours ago
-
RE: Renewables & Heat Pumps in the News
@toodles this industry lacks accountability. That's one...
By Mars , 11 hours ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@prunusk I guess I was being generic with PV The pipe...
By HeyMikey , 15 hours ago
-
RE: Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
@jamespa previously it was so noisy, it was like hav...
By Papahuhu , 16 hours ago
-
RE: Running from backup generaor in powercut?
Fortuitously, I've just posted here on another topic ab...
By Transparent , 17 hours ago
-
The Myth of the MCS Performance Guarantee
As the editor of Renewable Heating Hub, I dedicate a si...
By Mars , 17 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Yes, I agree that the dearth of public knowledge of ene...
By Transparent , 18 hours ago
-
RE: UK Heat Pump Problems: A Complaint Process That's Irreparably Broken
Why do they not get replaced by NICEIC, assuming they w...
By Batpred , 1 day ago
-
RE: Volumiser required on Grant R290?
Bold move, and welcome to the forums @Patrick. I’ve h...
By Mars , 1 day ago
-
RE: R290 Heat Pump and Foundation Air Bricks
@l8again I agree fully, so what we would do is offer yo...
By ASHP-BOBBA , 1 day ago
-
RE: Setback savings - fact or fiction?
I agree, I have even been known to call some of the 'op...
By cathodeRay , 1 day ago