Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Adventures in heat loss calculations

25 Posts
5 Users
5 Reactions
173 Views
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3036
 

Posted by: @jamespa

The multiplication correctly calculates the loss, but the energy that the heat pump must supply is that minus the heat supplied by other sources.  This comment would apply whether the HTC (ie the gradient of the power vs temperature line) is calculated from degree days or DT.

I'm still not sure! Consider this chart with an added line which represent to total heat loss:

 

image

 

My reasoning: the added upper dotted line Y intercept is the 'everything in balance' point: OAT = IAT so IAT - OAT = 0, no energy is needed to keep something in balance that is already in balance. But the real point of interest is where the solid line crosses the X axis: this is the point at which the primary heat source no longer has to supply any heat, because the other heat sources provide enough. How much extra heat that other heat provides is shown by the vertical distance between the two lines, which as it happens is conveniently measured by the Y axis intercept, even if a that point we have the non-real imaginary concept of a heat source that puts out negative energy. So to get the total heat loss (represented by the added upper dotted line) you have to add the other heat sources energy to the heat pump energy, to get the total needed to keep the house in balance.

Or am I just being very thick?

 


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote