Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Additional ASHP kW for DHW cylinder?
Hi everyone.
My heat loss calculation comes in at 8.1kW. I’ll need a minimum 250 litre cylinder (would take a 300 but not enough headroom) and was wondering what are the guidelines for additional ASHP capacity? Is there a rule of thumb for extra kW?
Are all ASHP systems DHW priority or can they manage a bit of both space heating and DHW?
Thanks.
Welcome to the forums @project_electrify.
While there's no fixed rule, I’ve heard some installers say that adding 1.5kW to your heat loss is a common practice to ensure sufficient heating capacity during peak periods, but I’m pretty sure that this figure will vary from heat pump to pump.
On the subject of DHW and space heating, the ASHP does both. Ours prioritises DHW. So if it’s cold outside, and the heating is on, and someone has a shower, the heating temporarily goes off while the hot water is reheated. As soon as it is, the system returns to central heating.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Thanks for your reply.
Perhaps the forum could help me with another question!
My current system has 10mm copper microbore tapped from a 22mm main run.
One installer wants all the microbore gone and replaced with 15mm from the main pipes. In general I don’t have an issue with this but the new pipe runs for 3 of the 16 radiators will require significant redecoration and I’d prefer it if they used the existing 10mm copper in the wall.
One of the radiators has a heat demand of 820w. The other two are only 170w each. In theory, would it be possible to run a system with mixed diameter pipes? There would be 13 other rads on the larger pipe size.
@project_electrify
Yes you can have different pipe sizes. The 10mm copper can move over 1100 Watts at a flow of 0.9 m/s and DT5 (the usual parameters).
I assume they are replacing part of the 22mm copper main run? As that can only move about 6kW
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks for your reply. Looking at your table they must be replacing all or part of the main run too.
So for a heat loss of 8.1kW with the main backbone in say 28mm copper and radiators on 10mm requiring no more than 1.1kW that would be acceptable?
@project_electrify
Im not an installer but I would imagine they could just replace the first section of the 22mm with 28mm so that say 3kW of radiators come off that leaving the other 5kW on the 22mm.
My bathroom radiator is fine on 10mm copper and my other bigger radiators are on 15mm plastic as it was easier to replace the existing 10mm copper with it.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @thebinmanMy current system has 10mm copper microbore tapped from a 22mm main run.
We're in a similar boat to you with a hodgepodge of different pipe sizes, which was briefly covered in this recent video:
On the back of this, like you, we have no intention of ripping up our house to repipe. As a follow up to the video above, the plan is to increase the heating pipework in the cupboard to 28mm going up to the tees and to install balancing valves on each 22mm circuit. In addition to this, we are going to repipe the heating circuits as open loop, using the existing buffer as a volumiser instead. An additional pump may then be required to run the heating to the index circuit (our TV room). This, according to Ultimate Renewables, should give us sufficient flow through microbore.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 2,562 Online
- 7,222 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: DIY powerflushing tutorial
What came out of the UFH loops is rust from oxygen seep...
By bobflux , 9 hours ago
-
RE: Renewables & Heat Pumps in the News
@temperature_gradient I don't doubt the veracity of ...
By Rob of York , 9 hours ago
-
I think that CCGT plant in Lingen is more likely to suc...
By Transparent , 14 hours ago
-
RE: Heat Geek installations: share your experiences
@l8again fwiw my experience (Valiant but not with heat ...
By JamesPa , 16 hours ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
@etchedpixels thank you for the advice paid cash all...
By Chilli304 , 2 days ago
-
RE: Why don't people choose heat pumps?
Savings you need to consider versus the investment valu...
By EtchedPixels , 2 days ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@susannasaunders An interesting conversation to have ...
By Rob of York , 2 days ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Yes, in my case, the ISP hub is permanently there, they...
By Batpred , 3 days ago
-
RE: Electricity price predictions
@rob-of-york sounds like a term that Heidegger would...
By Papahuhu , 3 days ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 3 days ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 3 days ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 3 days ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 5 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 6 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 6 days ago
Members Online
No online members at the moment