Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Insulation of flow and return Heat Pump piping
I know mention has been made of ties on insulation runs reducing the insulation. Well, I have my installers coming on Wednesday to take remedial action on the external pipework runs. As will be seen in the photos, there is a ‘strap’ that has come undone and whilst I was taking this photo, I noticed how deep the plastic ties were compressing the insulation next to it. (I have very limited vision at present [12 months on, still waiting for a horsepiddal appointment] and as both the insulation and the ties are black, I had not noticed before). I know the strap is easily rectified and I think the control cables running in the plastic hose will need to be clipped to the wall separately and a few wall clips should be fitted but… am I right in thinking the insulation run is likely to remain compromised in terms of insulation value and will not recover anytime soon? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Hi @toodles That external insulation looks pretty poor to me, but not unlike my original insulation. Cable ties are definitely not to be recommended. I would recommend Dave Smith's products - see https://primary-pro.co.uk
He is very helpful and his insulation solutions make a lot of sense.
@toodles An interesting question so I did some research. An uninsulated 28mm pipe with a 55C difference between the water temperature and ambient will lose 76W/m. Insulating that with 1 inch foam will take that down to 10W/m i.e. 0.1 W/cm. Assume that compression doubles the losses to 0.2 W/cm and that each compromised section is 2 cm then the additional loss is 0.2 W per zip-tie. Assume 300 hrs per annum where the outside temperature is around 0 C then you get 60 Wh per zip-tie per annum, slightly under 2p. [someone might like to check my figures!]. On the other hand sections of bare pipe will be losing heat at nearly 8 times that rate and may be much longer. My external pipe runs look like the ones in Mike H's photo but I'll be been checking out the joints and exposed fittings in my garage just in case ..
There are many assumptions in this and I would imagine that the zip-ties don't destroy the insulation, merely move it around so the insulation will still be there, just moved to the adjacent bits of pipe.
@dr_dongle From your figures, this suggests the heat loss is undesirable but fairly insignificant. As to moving the insulation around, I’m not so sure as the overall diameter on either side of the tie does not increase in my experience, it is just that it is compressed where the tie applies pressure. I have now had the ties removed and the crushed sections have all been replaced with new; the replacement ties have been placed on top of adhesive ‘straps’ which spread the load and the ties are minimal tightness to perform the job. The vertical pipework no longer has any ties as the electrical ‘hose’ has been retained in a different fashion now. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles undesirable but insignificant sums it up pretty well though the cumulative effect may be another matter. I have a retro-fitted hybrid system here so I have two lots of everything with valves to separate them so I tallied 70 zip-ties (20 in the garage where temperatures can plummet), two pumps with shut-off valves, two filters ditto, three other pairs of shutoff valves, two air bleed valves, two drain points and four large compression fittings at the buffer tank. That is all in the plant room and some of that is in the return but it is all exposed brass and it all adds up. It was an interesting exercise and I'll do the calculation properly when I have a minute. 76 W/m on exposed copper is quite a thought ..
@dr_dongle Even at ‘insignificant’ levels, all those ties certainly add up! As best as I can see, no insulation has been squashed, squeezed or crimped on my system now; once those external pipe runs I photographed enter the brickwork, they are in the airing cupboard and there, the hot runs are insulated cleanly too. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles Sounds like you're sorted - these things niggle though once you spot them. I totted up the bare metal on the flow side of my system and I came up with just over a metre so on the coldest night in theory that could be 80 watts - unlikely for lots of reasons and it would provide some frost protection but it was an interesting calculation. The biggest single items were the pump with its isolating valves and a motorised valve.
@dr_dongle I saw a YouTube presentation from one of insulation makers; they showed how to create bespoke covers around pumps and various valve devices, very neat if fiddly to create! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,095 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@peterackstraw 13.5 kWh’s of battery capacity is unlike...
By Toodles , 5 minutes ago
-
@editor — it was a not very well implemented so far as ...
By cathodeRay , 22 minutes ago
-
RE: Microgeneration Certification Scheme (MCS)
@jamespa A cynical view but, I fear that it is a fair ...
By Toodles , 23 minutes ago
-
Something sounds odd there; if you have solar power cha...
By Toodles , 27 minutes ago
-
RE: Jokes and fun posts about heat pumps and renewables
... except that the legal notice (part of which was rep...
By JamesPa , 1 hour ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 21 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 3 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago